PDA

View Full Version : pipe insulation thickness



bangoman
24-04-2008, 10:44 AM
I live and work in high humidity area abbt 85 percent as such all ref lines are insulated wat size insul;ation thickness will suit this area and hw do u arrive to that value

2007eng
24-04-2008, 12:26 PM
More than 10 mm, 20 is good from Daikin manuals

nike123
24-04-2008, 02:59 PM
Go there and you could calculate online or download software for calculation:
http://tinyurl.com/43per7

US Iceman
24-04-2008, 08:43 PM
The insulation thickness is determined by the pipe operating temperature and the ambient conditions. The goal of this is to prevent condensation of water on the insulation surface (outside surface of insulation).

As the humidity increases the insulation thickness also increases for any given pipe temperature. The logic is to keep the outside surface of the insulation above the dew point temperature of the air. If the pipe is well insulated (sufficient thickness) the outside surface temperature will be above the dew point temperature therefore no condensation can occur.

The other important aspect of this is to ensure the insulation is sealed well. Water getting into the insulation or under it contributes to corrosion (in ferrous material like carbon steel). And, if the pipe temperature is below freezing the water can freeze so that the ice damages the insulation system.

Some of the insulation manufacturers have tables with various operating conditions you can use to determine the minimum required thickness.