View Full Version : W3000 pCO2 or pCO3 & Integration



strumbeat
17-04-2008, 09:59 AM
Hi from South Africa

We are looking at Integrating 4 Turbo Core Climaveneta chillers which use the W3000 Controls to our Johnson Controls BMS

We have mapping tables for the pCO2 controller but i think the W3000 is a pCO3 ??

Any advice ?

Any Johnson fundi's out there ?

regards

PETE

nike123
17-04-2008, 11:31 AM
If you think that W3000 is Carel pCO3 then here are the data for pCO3:
http://tinyurl.com/3e9m5b

penguinkiller
22-11-2008, 02:39 PM
The W3000 is only PCO3 hardware. It has bespoke climaveneta software in it so the carel manual will not work.

You can use with the folowing BMS via a serial card and the supervisor network.

MODBUS, TREND, LONWORKS, BACNET,

I have the manual but cant't upload it because it is 671.9 KB.