14-04-2008, 01:18 PM
Is Anybody Works With Dixell Xc 911m? I Need Help About Connecting Probe Input. If Anybody Have Electric Shema....but Not From Dixell, I Have It. Thanks!
Brian_UK
14-04-2008, 11:21 PM
Hello and welcome to the forum.
What is the problem you are having with connecting the probes?
The wiring schematic clearly shows the connections.
wolf-zemun
15-04-2008, 10:06 AM
Yes, but when I conncet they don't show right value and occure alarm A01F. When I switch polarity then occure alarm Er0H.
nike123
15-04-2008, 12:20 PM
Yes, but when I conncet they don't show right value and occure alarm A01F. When I switch polarity then occure alarm Er0H.
Check your probe and configuration:
5.3.2 Condensing probe configuration
Pbc: Probe selection. Cur = 4 ÷ 20 mA probe; ntc = NTC probe.
PA04: Adjustment of read out corresponding to 4mA (present only if Pbc=Cur). input
signal, given by the suction probe (0 ÷30 bar or 0÷435 PSI or 0 ÷3000 KPA)
Warning: set a value correspondent to absolute pressure. If the transducer measures
relative pressure increase the range by 1 bar.
E.I. PP30 relative pressure transducer, range: 0÷30bar. PA04=1; PA20=31.
PA20: Adjustment of read out corresponding to 20mA input signal, given by the suction probe
(0 ÷ 40.0 bar or 0÷580 PSI or 0 ÷ 4000 KPA) SEE THE WARNING IN PA04.
CAL: Condensing probe calibration (-1.00÷1.00bar; -10.0÷10.0 °C or -20÷20°F/PSI or
-100÷100KPA)
Probe is NTC and polarity shouldn't be a issue.