Hi,all
Who can tell me how to operate a cascade system?
High stage is R22.Low stage is R23.
charging refrigerants?
special cases to be attention during operation?
.....
Of course it is best there is a correlative manual . I'm a greener to this system.
:):):)

TXiceman
08-03-2008, 03:25 AM
First thing to do is to get the high temp stage down to temperature. Charge in a conventional manner for the R-22.

You will need to vacuum dehydrate both systems to a fairly dry state and break the vacuum with the appropriate refrigerant.

Hope fully the R23 system is design properly with an expansion tank or a fade-out drum. It should be a critical charge system.

With the high temp system operating, charge vapor into the R23 side of the cascade condenser until you can get a liquid seal on the low temp system. Now start the low temp compressor and trim the charge as you are down to temperature.

Ken

sagittarius
14-03-2008, 04:03 AM
Thanks,TXiceman.
To avoid the air in R23 system,I wanna purge R23 through the low stage,about 2~3bar,is Ok?

norseman
14-03-2008, 11:50 AM
If this is a already made system, I would have looked for the spesifications on the unit. The high stage capacity and temperature should be correct at the start. Do not look for a "normal" pressure reading on it because a high stage without load can go into wild low pressures. Earlier days I was used to R12 on the high and it went to -45c so people without knowledge always filled the high up and made a new problem to another. The low stage in most cases use a static filling pressure by ambient which give you the best charge. Some other make a static after a run and in such systems, I normally charge +10% which drop down to correct on the new test after after test warming up. If you charge a low stage just by looking for an end temperature, you have to be careful so you not overcharge the system. You can get dangerous pressure when it warm up again.