View Full Version : need some help



rkmoorthy
11-02-2008, 11:31 AM
hai everybody this is moorthy from qatar i need a help from you all, can i change refrigerant is r22 to 410

PaulZ
11-02-2008, 11:50 AM
Hi Moorthy No you can't replace R22 with R410. R410 is a high pressure refrigerant and you will find the pipework used on R22 will not withstand the pressure. Also all fittings for R410 are heavier and rated at a higher pressure. Regards Paul

powell
14-02-2008, 05:29 AM
hai everybody this is moorthy from qatar i need a help from you all, can i change refrigerant is r22 to 410
moorthy

Absolutely not! The compressor, components, controls etc... are not designed for the higher pressure, stay with R-22 or install a new R410 system.

rkmoorthy
14-02-2008, 11:24 AM
thanks for your reply mr paulz and powell. i have a split type a/c in my project, that is zenithair brand. this unit is using in R410A, in my location not available 410a,thats why i ask you to can i replace refrigerant 410a to r22.

nike123
14-02-2008, 01:31 PM
Before, it was
can i change refrigerant is r22 to 410
Now, it is
can i replace refrigerant 410a to r22.Could you, please, decide what is going to be.;)