Will
18-01-2008, 03:24 AM
One of the features in the Daikin software is the "current operating data" screen. Thought you guys might enjoy.
This is 'real time' info and you must be plugged into the unit via laptop RS232 port. (using the same download cable as TK, Carrier and Starcool.)
Full cool.
http://i223.photobucket.com/albums/dd235/willphotoalbum/daikinfullcool.jpg
Full heat.
http://i223.photobucket.com/albums/dd235/willphotoalbum/daikinfullheat.jpg
Defrost.
http://i223.photobucket.com/albums/dd235/willphotoalbum/daikindefrost.jpg
SET
S.P.............Temp Set Point
Hum SET......Humidity Set Point
SENSORS
SS.............Supply Air Sensor
RS.............Return Air Sensor
DCHS.........Compressor Discharge Sensor
EIS............Evap Inlet Pipe Sensor
EOS...........Evap Outlet pipe Sensor
SGS...........Suction Gas Sensor
AMBS.........Ambient Air Sensor
HPT...........High Pressure Transducer
LPT............Low pressure Transducer
PT..............Potential Transformer (input voltage)
CT1............Current Transformer 1
CT2............Current Transformer 2
DSS............Data Recorder Supply Air Sensor
DRS............Data Recorder Return Air Sensor
USDA1.........Cargo Sensor 1
USDA2.........Cargo Sensor 2
USDA3.........Cargo Sensor 3
CTS............Cargo Temp Sensor
HuM............Humidity Sensor
OUTPUTS
Ry1..............(unused)
Ry2 RSV........Reheat Solenoid Valve
Ry3 BSV........Bypass Solenoid valve
Ry4 DSV........Defrost Solenoid valve
Ry5 HSV........Hot Gas Solenoid valve
Ry6 ISV.........Injection Solenoid valve
Ry7 LSV.........Liquid Solenoid valve
Ry8 ESV.........Economizer Solenoid valve
Ry9 RM COMP..Notaclue
Ry10 RM DEF...Notaclue
Ry11 RM IR.....Notaclue
Ry12.............(unused)
Ry13 COMP....Compressor Motor
Ry14 EFH.......Evap Fan High
Ry15 EFL.......Evap Fan Low
Ry16 CF........Condensor Fan
Ry17............(unused)
Ry18 PCC1.....Phase Correction Contactor
Ry19 PCC2.....Phase Correction Contactor
SMV.............Suction Modulation Valve
EV...............Electronic Expansion Valve
This is 'real time' info and you must be plugged into the unit via laptop RS232 port. (using the same download cable as TK, Carrier and Starcool.)
Full cool.
http://i223.photobucket.com/albums/dd235/willphotoalbum/daikinfullcool.jpg
Full heat.
http://i223.photobucket.com/albums/dd235/willphotoalbum/daikinfullheat.jpg
Defrost.
http://i223.photobucket.com/albums/dd235/willphotoalbum/daikindefrost.jpg
SET
S.P.............Temp Set Point
Hum SET......Humidity Set Point
SENSORS
SS.............Supply Air Sensor
RS.............Return Air Sensor
DCHS.........Compressor Discharge Sensor
EIS............Evap Inlet Pipe Sensor
EOS...........Evap Outlet pipe Sensor
SGS...........Suction Gas Sensor
AMBS.........Ambient Air Sensor
HPT...........High Pressure Transducer
LPT............Low pressure Transducer
PT..............Potential Transformer (input voltage)
CT1............Current Transformer 1
CT2............Current Transformer 2
DSS............Data Recorder Supply Air Sensor
DRS............Data Recorder Return Air Sensor
USDA1.........Cargo Sensor 1
USDA2.........Cargo Sensor 2
USDA3.........Cargo Sensor 3
CTS............Cargo Temp Sensor
HuM............Humidity Sensor
OUTPUTS
Ry1..............(unused)
Ry2 RSV........Reheat Solenoid Valve
Ry3 BSV........Bypass Solenoid valve
Ry4 DSV........Defrost Solenoid valve
Ry5 HSV........Hot Gas Solenoid valve
Ry6 ISV.........Injection Solenoid valve
Ry7 LSV.........Liquid Solenoid valve
Ry8 ESV.........Economizer Solenoid valve
Ry9 RM COMP..Notaclue
Ry10 RM DEF...Notaclue
Ry11 RM IR.....Notaclue
Ry12.............(unused)
Ry13 COMP....Compressor Motor
Ry14 EFH.......Evap Fan High
Ry15 EFL.......Evap Fan Low
Ry16 CF........Condensor Fan
Ry17............(unused)
Ry18 PCC1.....Phase Correction Contactor
Ry19 PCC2.....Phase Correction Contactor
SMV.............Suction Modulation Valve
EV...............Electronic Expansion Valve