I'm trying to find the chart for the correct pvc sizes to be used per ton of chilled water cooled system taken in consideration friction losses
Lowrider
03-01-2008, 10:47 PM
I'm not sure pvc is suited for pressurized chilled water systems. A suited material would be ABS. Your supplier should have flowcharts and pressure tables for the abs pipes!
monkey spanners
04-01-2008, 03:53 PM
Iv'e always used ABS for chilled water also, i think it has a better impact resistance when its cold than PVC.
Abby Normal
05-01-2008, 05:16 AM
I have no qualms using schedule 80 PVC for chilled water.
There is no chart, but try and limit yourself to flows of 4 feet per second or less.
thornie
14-11-2009, 03:23 AM
PVC is not really suitable, ABS is an improvement, HDPE pre fabricated, pre-insulated, is the way forward nowadays