Hi. Does anybody know of where I can get 415v crankcase heater tapes from.They need to be 1000mm long and 70w. I've tried RPW,Climate center and Google with no luck. :(

The Viking
29-11-2007, 08:19 PM
I had this problem years ago,

In the end I ended up fitting a transformer and using a standard 240V heater.

cooldude
29-11-2007, 08:30 PM
Might end up having to do that. Thanks Viking

Brian_UK
30-11-2007, 12:24 AM
I have to ask - why the transformer ?

If the unit is three phase 415v why not tap off one phase to get the 230v?

Or am I missing some 'correct electrical procedure'?

The Viking
30-11-2007, 01:16 AM
Well, I assumed that as the question were asked, the unit in question lacks the Neutral (and it is really bad practice to connect it to earth)....


But I might be wrong, it have happened once in the past.

cooldude
30-11-2007, 09:43 AM
yes the unit does not have a neutral. its just 3ph + earth.

PaulZ
30-11-2007, 11:21 AM
Viking is right it is not good practice to use the earth as the neutral, reason being the earth could be defective and if so you will liven up any metal part of the installation. Earth connections are either to a water pipe (old houses) or a metal stake in the ground.
A 415V transformed is the probably the best way of using a 240V heater.

BESC5240
30-11-2007, 12:09 PM
Hi,
If you're looking for a belt type crankcase heater to go around a hermetic compressor, you could try this one:

Danfoss Maneurop has a 400V 75W crankcase heater for the MTZ-4cylinder compressors. The perimeter of this compressor is about 97 cm. The code for it is 7773014.
You could check with your local Danfoss Maneurop dealer (D&W ?)
Best regards

anuraruna@gmail
30-11-2007, 04:38 PM
Viking is right it is not good practice to use the earth as the neutral, reason being the earth could be defective and if so you will liven up any metal part of the installation. Earth connections are either to a water pipe (old houses) or a metal stake in the ground.
A 415V transformed is the probably the best way of using a 240V heater.
I also face a similar problem. Finally I used 415 transformer with neutral . Problem solved.

The Viking
30-11-2007, 06:44 PM
Viking is right

There was a doubt?
:D

frank
30-11-2007, 09:08 PM
Who mentioned that the earth was going to be used as a neutral?

frank
30-11-2007, 09:09 PM
I also face a similar problem. Finally I used 415 transformer with neutral . Problem solved.
If you have a neutral available then you wouldn't need a 415v heater tape :confused:

cooldude
30-11-2007, 10:26 PM
Ordered transformers today. Thanks for the replys :)

Brian_UK
30-11-2007, 11:12 PM
Jeeez, so many answers I can't get in to say - fair comment, no neutral so no 230v - quite correct.

I'll just sit in the corner until you've all stopped beating on me ;):D

PaulZ
01-12-2007, 01:08 AM
Sorry Brian we will stop now.
Paul

Brian_UK
02-12-2007, 12:10 AM
Thanks, I'll take the hard hat off now :)