superheat with the wrong orifice
I see alot of systems with 1/2 larger evap than CU. Many times they leave the original orifice in the evap. I am quessing it is not going to make much difference. If you charge that system perfectly in the spring when it is 75 degrees outside, how much superheat would you have when it is 95 outside. I would think that your superheat would dissappear when it gets hot out.
  #2
Old 21-10-2002, 10:10 PM
frank's Avatar
frank frank is online now
Moderator
Site Moderator : and general nice guy
frank is on a distinguished road
One would assume that the more heat outside would also mean more heat inside during the summer months. More heat absorbed into the evaporator would result in higher suction pressures.
If the condensing unit (and one would assume the compressor) is undersized in relation to the evaporator then the evaporator would be starved of liquid refrigerant. This would result in higher superheats as the evaporator would not be full of liquid.
frank
Sponsored links
  #3
Old 22-10-2002, 01:40 PM
superheat's Avatar
regular poster
You charge this system in a situation where the superheat chart calls for say 21 degrees of superheat. After a while the same system is in a situation that the superheat chart calls for 5 degrees of superheat. What will the system superheat be?
  #4
Old 23-10-2002, 12:31 PM
Andy's Avatar
Andy Andy is online now
Moderator
Andy is on a distinguished road
Hi, Superheat
I think we are supposed to size the oriface to match the cond unit duty at design conditions, it is therefore likly that the superheat will be above the normal during pulldown if the unit is small compared with the evap, this will lessen when we reach the design conditions.
I am going to put my foot in it here and say that there is no such thing as an oversized evaportor, you will be just designing with a smaller TD in mind. (ofcourse you can over do it with say a 1k design TD)
Larger evaps and condensers will lead to a more effecient system and in the case of the evap a lower latent heat removal.
Regards. Andy.
  #5
Old 24-10-2002, 05:45 AM
Gary's Avatar
Gary Gary is online now
VIP Poster
Gary will become famous soon enough
Actually, higher latent heat removal at same SST or lower latent heat removal at same fan speed. Or anywhere in between.
__________________
Author of TECH Method troubleshooting books
  #6
Old 24-10-2002, 09:00 AM
reggie's Avatar
reggie reggie is offline
regular poster
reggie is on a distinguished road
Andy as regards to your quote of larger evaporators lead to increase of latent cooling you do have a point. I worked with a guy who claimed that the design on a number of Japanese heat pump splits would have larger evaps than cooling only counterparts.
Thus they ran at lower evaporating temperatures increasing the total duty but lowering the sensible heat ratio and relied on the coil thermistor for compressor shut down during long running cycles.
  #7
Old 24-10-2002, 01:44 PM
superheat's Avatar
regular poster
I have always wondered about "mismatch" heat pumps with larger indoor coils. I do not do much heat pump work. I was under the impression that not matching coils exactly messes with the balance of freon charge between the 2 seasons. ie. system will be overcharged one season and undercharged in the other as measured by compressor superheat.
I am very curious about these Japanese systems.
  #8
Old 25-10-2002, 05:09 PM
Andy's Avatar
Moderator
Large Evaps
Hi, Gary,Reggie,Superheat.
I was thinking that if you used any given condensing unit and fitted it with a larger evap, say one working on a 6 TD instead of 8 TD the amount a latent cooling would decrease.
Also when sizing splits for computer rooms you would select an evap one size bigger than that which would be normaly be used.
This is an observation made to me by a friend who works for a wholesaler suplying Mitsi units. This selection is purly to protect the computers from static which is associated with dry air.
Regards. Andy.
Sponsored links
  #9
Old 25-10-2002, 05:55 PM
superheat's Avatar
regular poster
The other variable in the equation is airflow. Larger evap will drop the TD and raise the evap temp. If you decrease the airflow, you can increase the TD.
Imagine a larger evap with less airflow that would give the same evap temp. It would dehumidify more than a small evap with the same evap temp. Clear as mud?
  #10
Old 25-10-2002, 08:54 PM
Gary's Avatar
VIP Poster
Exactly so. Given the same coil temperature, a bigger coil means having more surface area upon which to condense moisture.
__________________
Sponsored links
Reply
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
Thread Thread Starter Forum Replies Last Post
opens on rise of outlet subzero*psia Commercial 24 01-03-2008 11:46 AM
Superheat debate zolar1 Technical Discussions 5 08-02-2008 10:57 PM
TXV Superheat Gary Trouble Shooting 14 17-11-2007 03:07 PM
Carrier 23xl chiller-Low discharge superheat alarms Bradysmill Trouble Shooting 5 07-08-2007 04:27 PM
Superheat shogun7 Fundamentals 24 23-08-2004 05:54 PM
Powered by vBulletin® Version 3.7.4
Copyright ©2000 - 2009, Jelsoft Enterprises Ltd.
This forum and its pages must not be copied or reprinted without the written consent of Refrigeration Engineer.com.
This forum is a free and open discussion board.
Refrigeration-Engineer.com, the administrators and Moderators of this site are not responsible for content posted here.Ad Management by RedTyger