hi, new to site, just finding my way around.
the question i have is,, what are the initial findings on a water chiller that has a burst on the plate evaporator.
i.e would the water be obvious at the start of a problem?,
would i get any wierd pressure readings or would the compressor fail to start? thanks in advance..
Reply With Quote
  #2  
Old 23-05-2002, 04:08 PM
BritCit_Juve's Avatar
BritCit_Juve BritCit_Juve is offline
regular poster
 
Join Date: Dec 2001
Location: UK
Posts: 136
Rep Power: 8
BritCit_Juve is on a distinguished road
A burst heat exchanger will give two imediate effects I think. THe first is that there would be no gas in the refrigerant circuit and the sight glass should show wet. Also the compressor will have carried on running until the LP switch made or water reached the compressor so the compressor breaker will trip.
I hope that this helps

BritCit_Juve
Reply With Quote
Sponsored links
  #3  
Old 23-05-2002, 09:04 PM
Rick Harris's Avatar
Rick Harris Rick Harris is offline
rookie poster
 
Join Date: May 2002
Location: Gloucester UK
Age: 55
Posts: 12
Rep Power: 0
Rick Harris is on a distinguished road
Brian:Certainly you would have no refrigerant pressure to speak of but I would meg the compressor before starting it and see if you can get an oil sample.I have had them actually spout water when putting on my gauges.You could also pressurize the system and see if you have any positive results on the water side.Cheers Rick
Reply With Quote
  #4  
Old 23-05-2002, 09:52 PM
Andy's Avatar
Andy Andy is online now
Moderator
Site Moderator : and general nice guy
 
Join Date: Jun 2001
Location: N.Ireland
Age: 36
Posts: 1,608
Rep Power: 10
Andy is on a distinguished road
Hi, If the compressor was a open type water reaching the compressor would not throw the breaker due to an electrical short circuit. The compressor would go out on LP or possibly oil pressure. I have seen systems where you could see an oil water emulsion in the liquid lie sight glass.
Regards. Andy.
__________________
If you can't fix it leave it that no one else will
Reply With Quote
Sponsored links
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
Dunham Bush Chiller Alarm Regulator Air Conditioning 10 18-08-2009 05:00 PM
York Screw Chiller How low will it go????? bruceboldy Industrial Compressors 11 10-08-2007 10:29 PM
DIY aquarium chiller BarraCuda Technical Discussions 11 22-07-2007 07:59 AM
Chiller iceman007 Trouble Shooting 9 08-04-2006 02:48 PM
closed loop chiller bender Trouble Shooting 8 02-01-2003 02:32 PM


All times are GMT +1. The time now is 01:43 PM.

 

Powered by vBulletin® Version 3.7.4
Copyright ©2000 - 2009, Jelsoft Enterprises Ltd.
This forum and its pages must not be copied or reprinted without the written consent of Refrigeration Engineer.com.
This forum is a free and open discussion board.
Refrigeration-Engineer.com, the administrators and Moderators of this site are not responsible for content posted here.Ad Management by RedTyger