Rep Power: 0
|
|
a/c seer
Can anyone tell mr what A/C SEER is & how it affects the system?? would be grateful for the advice. Thanks in advance.
stuart. 
|

08-04-2002, 03:15 AM
|
 |
Moderator
|
|
Join Date: Mar 2001
Location: St. Louis, MO
Posts: 512
Rep Power: 9
|
|
SEER (Seasonal Energy Efficiency Ratio) is an efficiency rating for unitary a/c system under 65,000 Btu/hr. It is the cooling capacity of the unit in Btu/hr divided by the energy comsumption in watts. The standard can be downloaded from here.
In short, there are 4 separate tests performed to simulate normal usage of an a/c units:
'A' test is at 95°F ambient, 80°F DB/67°F WB return air temperature
'B' test is at 82°F ambient, 80°F DB/67°F WB return air temperature
'C' test is at 82°F ambient, 80°F DB/57°F WB return air temperature
'D' test is a cyclic test at the same conditions as the 'C' test.
The actual calculations necessary to determine the SEER rating are a bit involved, but specified in the above Standard.
__________________
[b]Prof Sporlan[/b]
|

11-04-2002, 07:42 PM
|
 |
regular poster
|
|
Join Date: Mar 2002
Location: Sydney Australia :D
Age: 39
Posts: 47
Rep Power: 0
|
|
|
Wow thats very involved. Is it necessary to work out the seer in all cases or is it provided by the factory.
Is seer needed on all visits to service all refrigeration systems?
__________________
:cool: [COLOR=Red]Do the job once & do it right.[/COLOR] :cool:
|

12-04-2002, 12:47 AM
|
 |
Moderator
|
|
Join Date: Mar 2001
Location: St. Louis, MO
Posts: 512
Rep Power: 9
|
|
|
SEER is determined by the equipment manufacturer and subject to independent verification. All a service technician would need to know is that it is a rating standard. 10 SEER is the current minimum mandated by the DOE, 12 or 13 SEER will be the new minimum by 2006, and for example, a 12 SEER units is approx 20 percent more efficient than a 10; 13 SEER is approx 30 percent more efficient than a 10.....
__________________
[b]Prof Sporlan[/b]
|

12-04-2002, 02:47 PM
|
 |
VIP Poster
|
|
Join Date: Jan 2002
Location: Austin, Texas
Posts: 718
Rep Power: 8
|
|
|
Unfortunately, high SEER ratings are responsible for the destruction of real property. Here in Texas, there is a growing number of mold damage claims due to humid enviroments in occupied spaces, in addition to just water leakage within a (home).
Now I profess myself NOT to be an A/C guy, but my understanding is that higher SEER ratings are acheived through different means, but in direct discussions with very knowledgeable people, I understand the net result to be a system which does not efficiently address latent load (humidity).
Most of Texas is technically a sub-tropical climate, so it has become a big issue. As a matter of fact, it is becoming difficult to obtain general liability insurance as a mechanical contractor in this state because of the mold issue.
|

12-04-2002, 04:06 PM
|
 |
VIP Poster
|
|
Join Date: Jan 2002
Location: Austin, Texas
Posts: 718
Rep Power: 8
|
|
All of the energy in the universe is constant. We know what the "energy" of heat transmission and latent (load) is.
All SEER is, is a standard which measures the amount of work which is NOT being done! 
Last edited by herefishy; 12-04-2002 at 04:08 PM..
|

12-04-2002, 06:50 PM
|
 |
Moderator
|
|
Join Date: Mar 2001
Location: St. Louis, MO
Posts: 512
Rep Power: 9
|
|
|
One means by which SEER rating can be increased is raising the evaporator temperature, which is generally not a problem for Phoenix, but could well present indoor humidity problems in Houston.
That is why having a good a/c technician select and install the unit will be more important for the average homeowner than the SEER rating of the unit.
__________________
[b]Prof Sporlan[/b]
|

12-04-2002, 11:47 PM
|
 |
VIP Poster
|
|
Join Date: Apr 2001
Location: New Port Richey, Florida - USA
Age: 64
Posts: 3,525
Rep Power: 12
|
|
I would think every tech in Texas should know to slow the blower down. 
__________________
Author of TECH Method troubleshooting books
|

13-04-2002, 12:02 AM
|
 |
Moderator
Site Moderator : and general nice guy
|
|
Join Date: Feb 2001
Location: Tampa Florida
Posts: 1,087
Rep Power: 10
|
|
|
LOL. Same goes for techs in Florida. Big condensers: Good. Big evaporators: Bad.
|

13-04-2002, 12:20 AM
|
 |
VIP Poster
|
|
Join Date: Apr 2001
Location: New Port Richey, Florida - USA
Age: 64
Posts: 3,525
Rep Power: 12
|
|
|
Actually, big evaps can take an even lower airflow before the coil freezes, with a lower ADP, thus more humidity removal than a smaller evap.
But a big evap with high airflow is bad news in a humid area.
__________________
Author of TECH Method troubleshooting books
|

13-04-2002, 01:17 AM
|
 |
VIP Poster
|
|
Join Date: Jan 2002
Location: Austin, Texas
Posts: 718
Rep Power: 8
|
|
Quote:
Originally posted by Gary
I would think every tech in Texas should know to slow the blower down.
|
You're exactly right!!!!!!!!.... And that just BLOWS the whole SEER bullsh*t out of the water, doesn't it?
This SEER thing is just a political scam.... like cigarettes.
|

13-04-2002, 01:41 AM
|
 |
VIP Poster
|
|
Join Date: Apr 2001
Location: New Port Richey, Florida - USA
Age: 64
Posts: 3,525
Rep Power: 12
|
|
LOL
Well...not a total scam. The evap/airflow balance is a tradeoff: Efficiency versus dehumidification. You still get the increased efficiency of the larger condenser, and scrolls are more efficient.
And in dry areas, they can crank up the airflow until the compressor gets a hernia.
Don't get me started on the TobaccoNazis...Grrrrrrrrrr...
__________________
Author of TECH Method troubleshooting books
Last edited by Gary; 13-04-2002 at 02:32 AM..
|

23-05-2002, 08:57 PM
|
 |
regular poster
|
|
Join Date: May 2002
Location: TN
Posts: 127
Rep Power: 8
|
|
|
SEER is a big rip. Government says you can't build equipment with less than say 12 SEER. YOU CAN'T BUILD A 12 SEER SYSTEM UNLESS IT IS A PACKAGE SYSTEM. It is a system with several parts. A 3 ton 12 seer CU with a 2 ton evap can be installed legally, but it will not be 12 SEER. Now let's talk about leaky undersized ducts. How about never changing the filter. It is just something that some lawyer/congressman developed to solve all the world's energy problems.
|

23-05-2002, 09:40 PM
|
 |
VIP Poster
|
|
Join Date: Apr 2001
Location: New Port Richey, Florida - USA
Age: 64
Posts: 3,525
Rep Power: 12
|
|
|
People don't seem to understand that a system has four major sub-sections. Condensing unit, evaporating unit, piping, and ductwork. Any of these can make or break the system.
__________________
Author of TECH Method troubleshooting books
Last edited by Gary; 23-05-2002 at 09:42 PM..
|

24-05-2002, 02:12 AM
|
 |
Moderator
|
|
Join Date: Mar 2001
Location: St. Louis, MO
Posts: 512
Rep Power: 9
|
|
|
Time and effort spent on developing proper training and certification programs, and educating the homeowner on the benefits of having qualified personnel install and service residential hvac equipment, will prove to be better policy than some arbitrary increase in minimum SEER ratings...
__________________
[b]Prof Sporlan[/b]
|

07-01-2007, 01:58 AM
|
 |
regular poster
|
|
Join Date: Jan 2007
Location: SPAIN
Posts: 139
Rep Power: 3
|
|
|
Re: a/c seer
Trying to find out about SEER (USA) and EER (Europe) and how they compare I came across EER=SEER/3.5 approx. Correct?
Does this explain why Europe (Spain) is now plagued by low price low efficiency i.e. EER 2.6 R407 A/Cs made in P.*.C. - because the USA will not buy them, especially wall splits!
|
 |
|