Eqivelant Pipe Length

I was looking through the latest manufacturers catalogue the other day and noticed that the maximum pipework length between indoor/outdoor unit had increased from 50m for an R22 unit to 70m for an R407c unit.
Can anyone explain why this is?
Reply With Quote
  #2  
Old 02-02-2002, 11:43 PM
Brian_UK's Avatar
Brian_UK Brian_UK is online now
Moderator
Site Moderator : and general nice guy
 
Join Date: Mar 2001
Location: Dorset
Age: 61
Posts: 6,321
Rep Power: 16
Brian_UK will become famous soon enoughBrian_UK will become famous soon enough
Higher pressures, different compressors ?

No, now that I think more deeply, I do not know why...sorry.
__________________
Brian
PERCUSSIVE MAINTENANCE. The fine art of whacking the crap out of a piece of kit to get it to work again.
ʎɐqǝ uo pɹɐoqʎǝʞ ɐ ʎnq ı ǝɯıʇ ʇsɐן ǝɥʇ sı sıɥʇ.
"You know "that look" women get when they want sex? Me neither." --Steve Martin
Reply With Quote
Sponsored links
  #3  
Old 05-03-2002, 11:34 PM
BritCit_Juve's Avatar
BritCit_Juve BritCit_Juve is offline
regular poster
 
Join Date: Dec 2001
Location: UK
Posts: 136
Rep Power: 8
BritCit_Juve is on a distinguished road
Smile

Can you give us some more info? Which manufacturer / unit?

Then we may be able to repond
Reply With Quote
  #4  
Old 06-03-2002, 09:26 PM
herefishy's Avatar
herefishy herefishy is offline
VIP Poster
 
Join Date: Jan 2002
Location: Austin, Texas
Posts: 718
Rep Power: 8
herefishy is on a distinguished road
The manufacturer put more lubricant in the crankcase????maybe?
Reply With Quote
  #5  
Old 06-03-2002, 09:34 PM
frank's Avatar
frank frank is online now
Moderator
Site Moderator : and general nice guy
 
Join Date: Oct 2001
Location: Nottingham UK
Age: 57
Posts: 3,316
Rep Power: 12
frank is on a distinguished road
sorry for the lack of information but it was Daikin a/c equipment, which we install quite a lot of, and, when doing a site survey, I was always thinking along the line of maximum indoor / outdoor limits, but suddenly I read the latest info sheets and was staggered to learn that the maximum length was increased to 70m for 407c.

No explanation has been forthcoming from Daikin and I can't really work out why this should be without technical backup.
Reply With Quote
  #6  
Old 06-03-2002, 09:35 PM
Andy's Avatar
Andy Andy is online now
Moderator
Site Moderator : and general nice guy
 
Join Date: Jun 2001
Location: N.Ireland
Age: 36
Posts: 1,608
Rep Power: 10
Andy is on a distinguished road
Hi, i don't do much split work, but I was at the wholesalers one day and the Tech/sales guy was showing a new range he was selling. After looking through the leaflet I spotted the increaed pipe lengths before you have to add refrigerant, I asked why and he said simply that's what people want. The customer (us) have asked for something and they have responded.
He may have been spoofing, but it sounded good.
Regards. Andy.
Reply With Quote
  #7  
Old 16-03-2002, 07:06 AM
Gibson's Avatar
Gibson Gibson is offline
regular poster
 
Join Date: Dec 2001
Location: Canada
Age: 55
Posts: 53
Rep Power: 8
Gibson is on a distinguished road
If you follow good piping practices you can just ignore what the manufacturers say about maximum lengths... Do your homework on the pipe sizing and consider the refrigerant and oil charges and you can cool Britain from Canada!
Reply With Quote
  #8  
Old 24-03-2002, 08:51 PM
Jasper's Avatar
Jasper Jasper is offline
regular poster
 
Join Date: Dec 2001
Location: nottingham
Age: 47
Posts: 95
Rep Power: 8
Jasper is on a distinguished road
Hi Gibson
Sorry i'm so late with this question BUT how can you say that it dos'nt matter about pipe length, when a compressor is only able to pump it's rated amount of refrigerant .
Reply With Quote
Sponsored links
  #9  
Old 24-03-2002, 09:31 PM
Gary's Avatar
Gary Gary is online now
VIP Poster
 
Join Date: Apr 2001
Location: New Port Richey, Florida - USA
Age: 64
Posts: 3,525
Rep Power: 12
Gary will become famous soon enough
In a stabilized, closed loop, series system, the mass refrigerant flow is identical at all points.

In other words, if the compressor is pumping X pounds of refrigerant per minute, then the rate of flow at every point in the system is X pounds per minute.

The problem with cooling Britain from Canada would be friction. Friction anywhere slows the flow everywhere, resulting in the compressor reducing it's flow to match.

On the other hand, angled fittings are of much more concern than straight pipe length, each providing the friction equivalent of many feet of straight pipe. This is the equivalent length of the fittings.

Increasing the equivalent length by 20 meters isn't going to add a lot of friction. The effect on the system will be minimal, and can be compensated for by slightly reducing the friction at the choke point, i.e. metering device. In a TEV system, this would happen automatically.

As regards the rest of Gibson's post, I agree wholeheartedly.
__________________
Author of TECH Method troubleshooting books

Last edited by Gary; 24-03-2002 at 09:35 PM..
Reply With Quote
  #10  
Old 24-03-2002, 09:44 PM
Jasper's Avatar
Jasper Jasper is offline
regular poster
 
Join Date: Dec 2001
Location: nottingham
Age: 47
Posts: 95
Rep Power: 8
Jasper is on a distinguished road
If that's true Gary why do manufacturers give a maximum pipe length
Reply With Quote
  #11  
Old 24-03-2002, 10:17 PM
Gary's Avatar
Gary Gary is online now
VIP Poster
 
Join Date: Apr 2001
Location: New Port Richey, Florida - USA
Age: 64
Posts: 3,525
Rep Power: 12
Gary will become famous soon enough
Quote:
If that's true Gary why do manufacturers give a maximum pipe length
Because they are selling a one size fits all product, containing refrigerant and oil charges, metering device, pipe sizes, etc. which must perform reasonably at both minimum and maximum pipe lengths. Compensatory changes can be made, but they aren't counting on your ability to make those changes.

A few meters of pipe length can be added to their maximum by simply redefining "perform reasonably", and/or maybe adding a few ounces of this or that.

There are a lot worse things that can happen to a system than a little extra friction. You might find it difficult to measure a difference in performance caused by 20 meters of extra piping, although you may need to add a little refrigerant to fill the extra liquid line.
__________________
Author of TECH Method troubleshooting books
Reply With Quote
  #12  
Old 24-03-2002, 10:39 PM
Jasper's Avatar
Jasper Jasper is offline
regular poster
 
Join Date: Dec 2001
Location: nottingham
Age: 47
Posts: 95
Rep Power: 8
Jasper is on a distinguished road
OK Gary i see your point
but does that mean that even with a pipe run that is longer than the manufacturers maximum they will still honour the warrenty on the equipment.
Reply With Quote
Sponsored links
  #13  
Old 24-03-2002, 11:55 PM
Gary's Avatar
Gary Gary is online now
VIP Poster
 
Join Date: Apr 2001
Location: New Port Richey, Florida - USA
Age: 64
Posts: 3,525
Rep Power: 12
Gary will become famous soon enough
I suspect so, and I don't see why not, but you would have to ask them to know for sure. Personally, I wouldn't tell them. What are they going to do...come out and measure?
__________________
Author of TECH Method troubleshooting books
Reply With Quote
  #14  
Old 23-03-2006, 11:30 AM
puddleboy3's Avatar
puddleboy3 puddleboy3 is offline
regular poster
 
Join Date: Mar 2006
Location: Glasgow, Scotland
Posts: 167
Rep Power: 4
puddleboy3 is on a distinguished road
Wink Re: Eqivelant Pipe Length

Bored at work and trawling through old threads found this one and thought i would bring it up to date! Had a problem with a split type system i wont mention any brands. Unit installed was new model with new pipe limits *problems* *problems* Lets just say i didnt work so the message here is always stick within the Equivelant or actual piping limits to cover yourself and yes they will come out and measure the pipe work

Last edited by puddleboy3; 23-03-2006 at 11:33 AM..
Reply With Quote
  #15  
Old 23-03-2006, 04:06 PM
NoNickName's Avatar
NoNickName NoNickName is online now
VIP Poster
 
Join Date: Mar 2006
Location: Merate (LC) - Italy
Age: 38
Posts: 1,456
Rep Power: 5
NoNickName is on a distinguished road
Re: Eqivelant Pipe Length

As a manufacturer of big DX close control with generously sized liquid receivers, I can only recommended a maximum of 15 meters of equivalent pipe length. Beyond that, a pipe layout design is required with appropriate refrigerant piping accessories.
Too long discharge pipe will result in unexpectedly high HP, while a too long liquid pipe will not do too much harm, but starvation.
The point is that oil must be added, and god knows how much, not too little or not too much, and excessive liquid migration in the condenser coil in winter time at standstill, which will result in condenser drowning and low pressure alarms while standby (in countries of harsh winters and all year long operation, like computing centres).
So beware of generous manufacturers. No one gives away anything for free.
Reply With Quote
  #16  
Old 23-03-2006, 04:26 PM
Renato RR's Avatar
Renato RR Renato RR is offline
Senior Poster
 
Join Date: Dec 2005
Location: Šibenik
Posts: 192
Rep Power: 4
Renato RR is on a distinguished road
Thumbs up Re: Eqivelant Pipe Length

Try to calculate pressure drop.Danfoss have good program for calculation.If pressure drop cose ading 3 C to condesation or 3 C to suction temperature should be ok.

Best regards,
Renato
Reply With Quote
Sponsored links
  #17  
Old 25-03-2006, 12:26 AM
mccoolair@yahoo's Avatar
mccoolair@yahoo mccoolair@yahoo is offline
rookie poster
 
Join Date: Jan 2006
Location: Fort Worth, Texas
Age: 60
Posts: 19
Rep Power: 0
mccoolair@yahoo is on a distinguished road
Re: Eqivelant Pipe Length

Hello, I am working on a similar problem, as well. I need to calculate the amount of R-22 required to recharge several systems where someone walked-off with the line sets overnight at a supermarket. #1 system- a produce cooler (24 ft.) has a 125' line length, lineset - 1/2" liquid and 1 1/8" suction with a Heatcraft condenser (HD10502M6C) and an antique Tyler case (Y12TVBH 1041B) Mfg. pressure setings Cut in: 36 and Cut out: 14-19. I must calculate the amount of refrig. required for the bid price, and I'm not sure how to go about it. Can anybody give me a clue where to start?
Reply With Quote
  #18  
Old 25-03-2006, 04:03 AM
US Iceman's Avatar
US Iceman US Iceman is online now
Moderator
Site Moderator : and general nice guy
 
Join Date: Aug 2005
Location: USA
Age: 54
Posts: 5,286
Rep Power: 10
US Iceman will become famous soon enough
Re: Eqivelant Pipe Length

Measure the total lineal feet of each pipe. Then find the volume of each pipe. (lineal feet times pipe cross sectional area in square feet = cubic feet)

For the suction line charge multiply the suction line volume (cubic feet) times the vapor density at the suction pressure.

Cubic feet of volume times pounds per cubic foot. That will give the total refrigerant charge for the suction line. Similar process for the other piping.

For the liquid line charge multiply the liquid line volume (cubic feet) times the liquid density at condensing the pressure.

For the discharge line charge multiply the discharge line volume (cubic feet) times the vapor density at the condensing pressure.

You will need to add some charge for the receiver, since the diptube in the receiver must have a liquid seal on it before liquid can flow out.

Heatcraft should have the condenser charge in a catalog somewhere. If you are using head pressure controls to flood the condenser, you also need to find out how much this will be.

In Texas this is probably not too bad. If the system were installed in Montana, it would be a different story.

Add all of the different amounts of refrigerant and you have your total. To be safe add 20% to this amount so you have enough money allowed for minor changes.
Reply With Quote
  #19  
Old 25-03-2006, 07:14 PM
Peter_1's Avatar
Peter_1 Peter_1 is online now
Moderator
Site Moderator : and general nice guy
 
Join Date: Oct 2003
Location: Belgium
Age: 48
Posts: 4,291
Rep Power: 11
Peter_1 will become famous soon enough
Re: Eqivelant Pipe Length

NoNnickName, visted last Thursday X-Change (Flumignano) and Intherm (Gregorio di Veronella, nearby Verona)
They will start a production with oval pipes in their drycoolers.
Both factories were very clean, well organised and I was impressed of what I saw at X-Change.
Are you also a customer of Intherm?
__________________
It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
Reply With Quote
  #20  
Old 25-03-2006, 08:17 PM
NoNickName's Avatar
NoNickName NoNickName is online now
VIP Poster
 
Join Date: Mar 2006
Location: Merate (LC) - Italy
Age: 38
Posts: 1,456
Rep Power: 5
NoNickName is on a distinguished road
Re: Eqivelant Pipe Length

No, I'm not, but will take a look
Reply With Quote
  #21  
Old 25-03-2006, 10:56 PM
Peter_1's Avatar
Peter_1 Peter_1 is online now
Moderator
Site Moderator : and general nice guy
 
Join Date: Oct 2003
Location: Belgium
Age: 48
Posts: 4,291
Rep Power: 11
Peter_1 will become famous soon enough
Re: Eqivelant Pipe Length

Daniele Stolfo is the present boss, previous founder or co-founder of Thermokey.
The oval tube is in my opinion a nice 'invention'
__________________
It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
Reply With Quote
  #22  
Old 26-03-2006, 01:20 AM
wambat's Avatar
wambat wambat is offline
Veteran Poster
 
Join Date: Jun 2005
Location: California
Posts: 387
Rep Power: 5
wambat is on a distinguished road
Re: Eqivelant Pipe Length

Quote:
Originally Posted by frank
I was looking through the latest manufacturers catalogue the other day and noticed that the maximum pipework length between indoor/outdoor unit had increased from 50m for an R22 unit to 70m for an R407c unit.
Can anyone explain why this is?
The molecular weight of R-22 and 407c are nearly the same , However say at 40*F SST the cuft/lb of 407c is less then that for R-22 therefor less pressure drop so a longer suction line is possible.

Last edited by wambat; 27-03-2006 at 02:13 AM..
Reply With Quote
Sponsored links
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
Single room a/c - long pipe run? electro Air Conditioning 7 07-08-2006 09:49 PM
pipe sizeing tool Latte Tools and Calculators 5 11-12-2003 12:32 AM
How many small strands needed to equal pipe pressure drop? DaBit Fundamentals 17 25-08-2003 09:56 PM
Pipe sizes benncool Chit Chat & Service Stories 10 08-07-2003 10:58 PM


All times are GMT +1. The time now is 08:08 PM.

 

Powered by vBulletin® Version 3.7.4
Copyright ©2000 - 2009, Jelsoft Enterprises Ltd.
This forum and its pages must not be copied or reprinted without the written consent of Refrigeration Engineer.com.
This forum is a free and open discussion board.
Refrigeration-Engineer.com, the administrators and Moderators of this site are not responsible for content posted here.Ad Management by RedTyger