Thumbs up R407C composition

I am working on a 407c system that has lost some of its charge.I can't tell the percentage that was lost. I would like to find out if the composition (chemistry) of the remaining LIQUID in the system has changed. If I remove ONLY the LIQUID (not vapour) from the system, would this liquid be 100% R407C.
Reply With Quote
  #2  
Old 31-01-2002, 07:50 PM
Prof Sporlan's Avatar
Prof Sporlan Prof Sporlan is offline
Moderator
 
Join Date: Mar 2001
Location: St. Louis, MO
Posts: 512
Rep Power: 9
Prof Sporlan is on a distinguished road
Quote:
If I remove ONLY the LIQUID (not vapour) from the system, would this liquid be 100% R407C.
If the composition of R-407C (R-32/R-125/R-134a, 23/25/52 percent by weight) has changed in the system, it will also change for the liquid R-407C in the system.

Normally, liquid or vapor leaks do not cause sufficient fractionation to be a concern. Leaks at the evaporator and condenser coil (where refrigerant is in its two-phase region) can be more of a problem.

Verifying the pressure-temperature relationship of the refrigerant blend would be in order if one suspects composition has changed significantly.
__________________
[b]Prof Sporlan[/b]
Reply With Quote
Sponsored links
  #3  
Old 01-02-2002, 01:21 AM
herefishy's Avatar
herefishy herefishy is offline
VIP Poster
 
Join Date: Jan 2002
Location: Austin, Texas
Posts: 718
Rep Power: 8
herefishy is on a distinguished road
Correct me if I'm wrong, Prof.,

But having the conversation regarding fractionization with a refrigerant mfgr rep., it was stated that the conditions under which actual fractionization could actually occur would have to be entirely "static" (for lack of a better word), in relation to constant temperature and/or agititation in order for a measureable amount of fractionization to occur.

As such, these conditions are rarely found in field service. being that equipment is typically in service and operating at the time that such occurances (leakage) occurs.

I concern myself with such matters when addressing refrigerant leaks on systems containing blends when re-activating systems which may have been "moth-balled", or inactive for some time.

In the end, I was left with the impression that the affects of fractionization are not that significant in the realm of practical, or everyday refrigeration/leak reaair of equipment "in service". That furthermore the refrigerant industry has lessened somewhat it's emphasis on the fractionization issue in the realm of "everyday service/repair.
Reply With Quote
  #4  
Old 01-02-2002, 03:36 AM
Prof Sporlan's Avatar
Prof Sporlan Prof Sporlan is offline
Moderator
 
Join Date: Mar 2001
Location: St. Louis, MO
Posts: 512
Rep Power: 9
Prof Sporlan is on a distinguished road
Quote:
But having the conversation regarding fractionization with a refrigerant mfgr rep., it was stated that the conditions under which actual fractionization could actually occur would have to be entirely "static"
The Prof can generally buy into this argument, but with the possible exception of a two-phase flow leak. A refrigerant blend flowing thru the evaporator will being evaporating at a low temperature, and continue to evaporate at higher temperature until it reaches saturated vapor (the dew point). The difference in these temperatures is the refrigerant temperature glide in the evaporator, and the reason it occurs is the more volatile components of the refrigerant blend boil off first. So if a leak exists at the inlet of the evaporator, one might expect the more volatile components to leak out, assuming refrigerant vapor and not liquid is leaking out.

But from a practical standpoint, the Prof doubts that your average refrigerant leak in an operating system could cause sufficient fractionation to cause problems.
__________________
[b]Prof Sporlan[/b]
Reply With Quote
  #5  
Old 01-02-2002, 09:59 AM
Derek's Avatar
Derek Derek is offline
regular poster
 
Join Date: Apr 2001
Location: Southern England
Age: 52
Posts: 124
Rep Power: 9
Derek is on a distinguished road
R407C goes west

ISTR that ASHRAE data gives somthing like +/-2% tolerance on fluid properties so you have to loose a lot before you were left with R134a(?) perfromance.

Theres a number of papers showing R407C performance drops off with time and my only deduction is fractional loss.

Pressures and temperatures should be a reasonable guideline but having a sample tested is only valid at the time you took it and probably not worth the time of money.

If your loosing cooling perfromance and there's no other explaination then recover and recycle (if you have the facility or supplier access).


Derek
__________________
Derek
Reply With Quote
Sponsored links
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
R407C to R404a MaDiNfO Air Conditioning 10 30-07-2006 09:34 AM
P/h chart for R407c Coolie Technical Speculations 2 22-02-2006 09:33 PM
Toshiba R407c Reversing Valves Brian_UK Air Conditioning 2 03-09-2005 11:22 PM
R22 vs R407C.....................again!! Abe Air Conditioning 5 24-07-2003 12:21 AM
R407C vs R22 Abe Refrigerants 3 14-04-2002 05:35 PM


All times are GMT +1. The time now is 11:59 AM.

 

Powered by vBulletin® Version 3.7.4
Copyright ©2000 - 2009, Jelsoft Enterprises Ltd.
This forum and its pages must not be copied or reprinted without the written consent of Refrigeration Engineer.com.
This forum is a free and open discussion board.
Refrigeration-Engineer.com, the administrators and Moderators of this site are not responsible for content posted here.Ad Management by RedTyger