Bad Contactor

A friend of mine has asked me to come look at his heat pump.

He says it runs in A/C mode but doesn't blow cool air. I am thinking he may not be noticing it as the ambient is already cool and he may not be "sensing" a low temperature difference.

He puts the unit into heat mode from a "no-call" position, into the call for heat and it won't run. He went outside observed the contactor not pulling in, so he manually closed it... it ran for a few moments then out.

At first I thought it may be the low pressure control, but if so it shouldn't let the contactor energize period. It may be low on charge but obviously not low enough to open the LPC. I haven't been out to the site so I am not sure of anything... just going on his word.

Any ideas?
__________________
:D
[b]Dean[/b]
[b]Subzero*psia[/b]

[b]Extinction is simply proof of failure to adapt. [/b]
Reply With Quote
  #2  
Old 06-11-2001, 01:38 PM
subzero*psia's Avatar
subzero*psia subzero*psia is offline
Veteran Poster
 
Join Date: Feb 2001
Location: USA
Age: 48
Posts: 266
Rep Power: 9
subzero*psia is on a distinguished road
Correction... the contactor "tries" to pull in but is very slow.
__________________
:D
[b]Dean[/b]
[b]Subzero*psia[/b]

[b]Extinction is simply proof of failure to adapt. [/b]
Reply With Quote
Sponsored links
  #3  
Old 06-11-2001, 06:28 PM
Brian_UK's Avatar
Brian_UK Brian_UK is online now
Moderator
Site Moderator : and general nice guy
 
Join Date: Mar 2001
Location: Dorset
Age: 61
Posts: 6,321
Rep Power: 16
Brian_UK will become famous soon enoughBrian_UK will become famous soon enough
Quote:
Originally posted by subzero*psia
Correction... the contactor "tries" to pull in but is very slow.
Sounds a bit like a control voltage problem.....
__________________
Brian
PERCUSSIVE MAINTENANCE. The fine art of whacking the crap out of a piece of kit to get it to work again.
ʎɐqǝ uo pɹɐoqʎǝʞ ɐ ʎnq ı ǝɯıʇ ʇsɐן ǝɥʇ sı sıɥʇ.
"You know "that look" women get when they want sex? Me neither." --Steve Martin
Reply With Quote
  #4  
Old 07-11-2001, 11:42 PM
subzero*psia's Avatar
subzero*psia subzero*psia is offline
Veteran Poster
 
Join Date: Feb 2001
Location: USA
Age: 48
Posts: 266
Rep Power: 9
subzero*psia is on a distinguished road
Talking

NOW he is telling me that it DOESN'T pull in when he tries the A/C... I think it is just a weak contactor coil. It is a 24V contactor so possibly the transformer... have to see I guess.

I should know better... doesn't matter if it is a friend or not... they never tell you the same thing twice and mix it all up anyway.

I DIDN'T WANT TO GO, it is a ways away! LOL!! But it is a friend so.... I am going on my day off.
__________________
:D
[b]Dean[/b]
[b]Subzero*psia[/b]

[b]Extinction is simply proof of failure to adapt. [/b]
Reply With Quote
  #5  
Old 08-11-2001, 09:31 PM
Brian_UK's Avatar
Brian_UK Brian_UK is online now
Moderator
Site Moderator : and general nice guy
 
Join Date: Mar 2001
Location: Dorset
Age: 61
Posts: 6,321
Rep Power: 16
Brian_UK will become famous soon enoughBrian_UK will become famous soon enough
Quote:
Originally posted by subzero*psia
.. I am going on my day off.
It WAS your day off Dean
__________________
Brian
PERCUSSIVE MAINTENANCE. The fine art of whacking the crap out of a piece of kit to get it to work again.
ʎɐqǝ uo pɹɐoqʎǝʞ ɐ ʎnq ı ǝɯıʇ ʇsɐן ǝɥʇ sı sıɥʇ.
"You know "that look" women get when they want sex? Me neither." --Steve Martin
Reply With Quote
  #6  
Old 12-11-2001, 01:44 PM
subzero*psia's Avatar
subzero*psia subzero*psia is offline
Veteran Poster
 
Join Date: Feb 2001
Location: USA
Age: 48
Posts: 266
Rep Power: 9
subzero*psia is on a distinguished road
Well, before I went there I started thinking about a system I worked on some time ago... a LONG time ago. I remembered a similar occurance... it was low on charge. So I loaded my R22 and went.

When I got there sure enough the contactor wouldn't pull in no matter what... BUT in the call for heat mode I could hold the contactor in and after about 10 seconds the pressure had built up enough to close the LPC and energize the contactor coil and hold the contacts closed. So I added refrigerant. It wasn't drastically low just enough to not close the LPC.

The service valve on the low side showed sign around the snap ring stop (back-seated position). I added tracer and asked my friend to check it every day or two at the locations I suspected. But I also noticed the reversing valve is stuck in the heat mode... his receiver is badly rusted and he is only feeding part of the outdoor condensing unit... frost build-up in bands around the coil. The unit is nine years old and his neighbors said the folks that owned it before him had lots of service calls on it, ONE JUST BEFORE HE BOUGHT THE PLACE.

I suggested he buy a new outdoor unit and line set, I will install it for him... I can see this unit nickle and diming him to death. AND since he is a friend... no mark-up on the system. He agreed (of course) so I will be making another visit probably this coming weekend now.

QUESTION.... the frost bands on the outdoor unit... it appeared that this circuit was restricted. I chased it back to the distributor, it was the only circuit of the three that was frosted. The other two were cool but not frosted... whats your opinion? I am no expert on heat-pumps... I love refrigeration but I admit I am lacking on the AC and HeatPump side.
__________________
:D
[b]Dean[/b]
[b]Subzero*psia[/b]

[b]Extinction is simply proof of failure to adapt. [/b]
Reply With Quote
  #7  
Old 13-11-2001, 12:01 AM
Brian_UK's Avatar
Brian_UK Brian_UK is online now
Moderator
Site Moderator : and general nice guy
 
Join Date: Mar 2001
Location: Dorset
Age: 61
Posts: 6,321
Rep Power: 16
Brian_UK will become famous soon enoughBrian_UK will become famous soon enough
Quote:
Originally posted by subzero*psia
QUESTION.... the frost bands on the outdoor unit... it appeared that this circuit was restricted......
Yes, we've had systems where there have been restrictions due to check valves sticking, cap-lines (distributor) blocking. Some of these blockages have never been clearly resolved. They may have been fixed but....

The feeling sometimes is that sticky fingers have been working on the units in the past, the oil has broken down and is beginning to clog the narrow pipes.

Mind you, it could just be that the gas charge is still low.?.
__________________
Brian
PERCUSSIVE MAINTENANCE. The fine art of whacking the crap out of a piece of kit to get it to work again.
ʎɐqǝ uo pɹɐoqʎǝʞ ɐ ʎnq ı ǝɯıʇ ʇsɐן ǝɥʇ sı sıɥʇ.
"You know "that look" women get when they want sex? Me neither." --Steve Martin
Reply With Quote
  #8  
Old 27-11-2001, 08:50 PM
frank's Avatar
frank frank is online now
Moderator
Site Moderator : and general nice guy
 
Join Date: Oct 2001
Location: Nottingham UK
Age: 57
Posts: 3,316
Rep Power: 12
frank is on a distinguished road
I recently came across this very same problem on a Daikin low wall unit. The installation engineer came back and said that on commissioning he could not get the suction pressure up above 35psig. When I looked closely at the system the indoor coil was only frosting on the lower third of the evaporator and one line out of the distributor was frosting.

When we stripped the coil out and de-brazed the dist'r we found the 2 out of the 3 feeder pipes into the evaporator were blocked, apparantlly by some over zealous factory worker in Belgium! A new one was fitted and the system continues to run like a dream!

Moral of the story is - don't trust it just because it is new!

Frank
Reply With Quote
Sponsored links
  #9  
Old 27-11-2001, 11:56 PM
Brian_UK's Avatar
Brian_UK Brian_UK is online now
Moderator
Site Moderator : and general nice guy
 
Join Date: Mar 2001
Location: Dorset
Age: 61
Posts: 6,321
Rep Power: 16
Brian_UK will become famous soon enoughBrian_UK will become famous soon enough
Quote:
Originally posted by frank
Moral of the story is - don't trust it just because it is new!
Oh so true and welcome to the forum Frank
__________________
Brian
PERCUSSIVE MAINTENANCE. The fine art of whacking the crap out of a piece of kit to get it to work again.
ʎɐqǝ uo pɹɐoqʎǝʞ ɐ ʎnq ı ǝɯıʇ ʇsɐן ǝɥʇ sı sıɥʇ.
"You know "that look" women get when they want sex? Me neither." --Steve Martin
Reply With Quote
Sponsored links
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
Why a capacitor on contactor coil wambat Electrical 18 15-05-2009 03:18 AM
Single pole contactor & crankcase heater herefishy Air Conditioning 7 01-04-2009 08:38 AM
Trane RTAD125 Problems Latte Trouble Shooting 9 14-12-2006 08:25 PM
Single phase contactor Andy T Commercial 9 23-10-2006 01:45 PM
Ascon ac multi split mike live Air Conditioning 14 30-06-2006 08:52 PM


All times are GMT +1. The time now is 09:10 PM.

 

Powered by vBulletin® Version 3.7.4
Copyright ©2000 - 2009, Jelsoft Enterprises Ltd.
This forum and its pages must not be copied or reprinted without the written consent of Refrigeration Engineer.com.
This forum is a free and open discussion board.
Refrigeration-Engineer.com, the administrators and Moderators of this site are not responsible for content posted here.Ad Management by RedTyger