Well, before I went there I started thinking about a system I worked on some time ago... a LONG time ago. I remembered a similar occurance... it was low on charge. So I loaded my R22 and went.
When I got there sure enough the contactor wouldn't pull in no matter what... BUT in the call for heat mode I could hold the contactor in and after about 10 seconds the pressure had built up enough to close the LPC and energize the contactor coil and hold the contacts closed. So I added refrigerant. It wasn't drastically low just enough to not close the LPC.
The service valve on the low side showed sign around the snap ring stop (back-seated position). I added tracer and asked my friend to check it every day or two at the locations I suspected. But I also noticed the reversing valve is stuck in the heat mode... his receiver is badly rusted and he is only feeding part of the outdoor condensing unit... frost build-up in bands around the coil. The unit is nine years old and his neighbors said the folks that owned it before him had lots of service calls on it, ONE JUST BEFORE HE BOUGHT THE PLACE.
I suggested he buy a new outdoor unit and line set, I will install it for him... I can see this unit nickle and diming him to death. AND since he is a friend... no mark-up on the system. He agreed (of course) so I will be making another visit probably this coming weekend now.
QUESTION.... the frost bands on the outdoor unit... it appeared that this circuit was restricted. I chased it back to the distributor, it was the only circuit of the three that was frosted. The other two were cool but not frosted... whats your opinion? I am no expert on heat-pumps... I love refrigeration but I admit I am lacking on the AC and HeatPump side.