water chiller

I am trying to establish the benefits, if any, of using a chilled water coil in a ahu as opposed to a dx coil.

There are obvious benefits if the coil is some distance from the chiller, i.e. no refrigerant in the building, but I am trying to understand why someone would install a chiller with remote condenser, with the ahu approx 2 metres away. From our first inspection it seemed like a lot of extra work with the recirc pumps, tanks etc, when they could have installed a straight dx coil in the ahu.

It appears to be a fairly old installation ( open drive dunham bush compressor), was this how things were done way back when.

Am I missing the obvious explanation?

David
Reply With Quote
  #2  
Old 08-10-2001, 10:53 PM
Brian_UK's Avatar
Brian_UK Brian_UK is online now
Moderator
Site Moderator : and general nice guy
 
Join Date: Mar 2001
Location: Dorset
Age: 61
Posts: 6,321
Rep Power: 16
Brian_UK will become famous soon enoughBrian_UK will become famous soon enough
I'm not sure about the age thing but I suppose it could have been someone trying to use up some existing, or old stock, equipment
__________________
Brian
PERCUSSIVE MAINTENANCE. The fine art of whacking the crap out of a piece of kit to get it to work again.
ʎɐqǝ uo pɹɐoqʎǝʞ ɐ ʎnq ı ǝɯıʇ ʇsɐן ǝɥʇ sı sıɥʇ.
"You know "that look" women get when they want sex? Me neither." --Steve Martin
Reply With Quote
Sponsored links
  #3  
Old 11-12-2001, 10:49 PM
BritCit_Juve's Avatar
BritCit_Juve BritCit_Juve is offline
regular poster
 
Join Date: Dec 2001
Location: UK
Posts: 136
Rep Power: 8
BritCit_Juve is on a distinguished road
Dont knock chilled water for an airconditioning system. At the end of the day chilled water is a very efficient secondary refrigerant, especially if a variable speed pump or modulating valve is fitted. Although DX is easy to install it is harder to correctly size a retrofit evaporator.
Chilled water systems were at one time a principle method of cooling and is primarily used in large projects be they newbuild or renovations. I think just lately it has been growing in popularity again, thanks to environmental concerns.
It has been doing what VRV/VRF systems try to do for years and has the advantage that if it springs a leak within the building then the leak is soon found.
It may be possible that this coil is operating on a full fresh air system where the load changes so a modulating valve will be fitted to adjust the cooling to maintain an air off temperature.
Reply With Quote
  #4  
Old 12-12-2001, 04:17 AM
Mike Hopkins's Avatar
Mike Hopkins Mike Hopkins is offline
regular poster
 
Join Date: Oct 2001
Location: Georgia, USA
Posts: 58
Rep Power: 9
Mike Hopkins is on a distinguished road
My thoughts would be along the line of what BritCit_Juve has said.
Is this some type of process that requires close control of discharge air temp? Chilled water with a modulating valve would fit that bill well, whereas DX would require extra controls and use of hot gas or elaborate staging, unloading abilities and real good design engineer with closely matched equipment. Design engineer
can be a little sloppy with chilled water design as long as they don't underestimate load or maybe pulldown factor. Also sometimes they do that if say they are thinking to add more Ahu's
to chilled water loop and so size for anticipated increase in load.
Hard to do with DX without adding another whole system. Redundancy can be another factor. If the system is critical, a mobile chiller could be brought in and hooked up in a hurry as
opposed to DX where repairs could take too long waiting for parts, etc. Sounds like they weren't thinking like that from the age of the system though.

Mike Hopkins
Reply With Quote
Sponsored links
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
Fact or Fiction david.findlay Fundamentals 40 09-03-2009 07:19 PM
Water Chiller Control David PS Air Conditioning 4 29-08-2006 11:14 PM
Mcquay PES Flooded Water Cooled Screw Chiller Brian Technical Speculations 4 05-07-2006 09:43 PM
water chiller andrewuk Technical Speculations 9 17-10-2005 09:28 PM
Hoshizaki Ice Maker Abe Legal-Business-Marketing 16 06-07-2004 05:41 PM


All times are GMT +1. The time now is 08:23 PM.

 

Powered by vBulletin® Version 3.7.4
Copyright ©2000 - 2009, Jelsoft Enterprises Ltd.
This forum and its pages must not be copied or reprinted without the written consent of Refrigeration Engineer.com.
This forum is a free and open discussion board.
Refrigeration-Engineer.com, the administrators and Moderators of this site are not responsible for content posted here.Ad Management by RedTyger