Thumbs up Sight glass location

Recently there was a discussion(arguement) among our techs as to the correct location of the liquid line sight glass.Some say it should be before,some say after, others say it does not matter if its before or after the drier. I would like know what other techs think on this subject.
Reply With Quote
  #2  
Old 22-09-2001, 02:57 PM
Prof Sporlan's Avatar
Prof Sporlan Prof Sporlan is offline
Moderator
 
Join Date: Mar 2001
Location: St. Louis, MO
Posts: 512
Rep Power: 9
Prof Sporlan is on a distinguished road
Installing sight glass downstream of the liquid line filter-drier:

Pro: one can see the condition of the refrigerant as it enters the expansion device. If the expansion device is starving, checking for the presence of flash gas ahead of it is normally one of the first things to consider.

Con: if the sight glass shows flash gas, one does not know if it is the result of a low refrigerant charge, or a restricted filter-drier.

Installing tight glass upstream of the liquid line filter-drier:

Pro: if flash gas is present in the sight glass, it will not be the result of a restricted filter-drier. One can have a high confidence level that the system has a low refrigerant charge.

Con: one cannot see the condition of the refrigerant as it enters the expansion device. If the evaporator is starving, and the sight glass is clear, one can only speculate the filter-drier is restricted. One can sometimes detect a restricted filter-drier by measuring a temperature drop across it. But this technique is often not reliable. Significant pressure drop can occur across a liquid line filter-drier at low delta T.

Of course, the Prof has a solution the above debate: install two sight glasses.... one upstream and one downstream of the filter-drier....

Assuming one didn't want to go thru the trouble and expense of installing two sight glasses, the Prof opts for placing it downstream of the filter-drier. If a system is not properly cooling, it is important for the technician to determine if the expansion device is operating properly. And that can be more easily accomplished by knowing the condition of the refrigerant entering it.
__________________
[b]Prof Sporlan[/b]

Last edited by Prof Sporlan; 22-09-2001 at 02:59 PM..
Reply With Quote
Sponsored links
  #3  
Old 23-09-2001, 07:03 PM
Jai's Avatar
Jai Jai is offline
rookie poster
 
Join Date: May 2001
Location: Trinidad,West Indies
Posts: 16
Rep Power: 0
Jai is on a distinguished road
Thumbs up sight glass location

Hey Prof's, thanks for the response. I am going to share this info with the rest of the techs. Hope it doesn't start another "debate"
Reply With Quote
  #4  
Old 11-12-2001, 11:01 PM
BritCit_Juve's Avatar
BritCit_Juve BritCit_Juve is offline
regular poster
 
Join Date: Dec 2001
Location: UK
Posts: 136
Rep Power: 8
BritCit_Juve is on a distinguished road
All the replys are good ones but I would be aware that they only relate to large airhandlers. On mini splits expect to see bubbles in the sight glass otherwise the system is probably overcharged.

Me I would probably purt the site glass before the filter drier but I think we can all agree before or after they are both valid.
Reply With Quote
  #5  
Old 18-04-2002, 11:16 PM
J.D's Avatar
J.D J.D is offline
improving poster
 
Join Date: Apr 2002
Location: Nova Scotia, Canada
Age: 40
Posts: 21
Rep Power: 0
J.D is on a distinguished road
I always install the sight glass downstream of the
filter drier. I like to see the condition of the liquid going to the TXV. If there is flash gas present and a plugged drier is the cause, you will usually be able to detect a noticable temperature
drop from the inlet to the outlet.
Reply With Quote
  #6  
Old 21-04-2002, 09:35 PM
pirestani's Avatar
pirestani pirestani is offline
improving poster
 
Join Date: Mar 2002
Location: Tehran
Age: 40
Posts: 28
Rep Power: 0
pirestani is on a distinguished road
Your discussion was very usefull .
But I want to know if it is necessary installing a flat sight glass at the middle of receivers body .and what level of liquid is satisfied in it (at normal operation)?
thanks.
s.pirs
__________________
S.P
Reply With Quote
  #7  
Old 23-05-2002, 09:26 PM
superheat's Avatar
superheat superheat is offline
regular poster
 
Join Date: May 2002
Location: TN
Posts: 127
Rep Power: 8
superheat is on a distinguished road
I say a sightglass has one real use: as a moisture indicator. You should know the moisture content after the drier. Plus what the prof said able the valve getting a solid column of liquid.
Reply With Quote
  #8  
Old 23-05-2002, 09:42 PM
Andy's Avatar
Andy Andy is online now
Moderator
Site Moderator : and general nice guy
 
Join Date: Jun 2001
Location: N.Ireland
Age: 36
Posts: 1,608
Rep Power: 10
Andy is on a distinguished road
Hi,Pirestanti, I think you are asking about the liquid level in a liquid receiver. The glass shows a level from 10% to 80% aproximately. Define normal operation, if you are feeding one source (valve or vessel) or muliple. On a receiver feeding one device the level will drop at peak loading(due to a shortage or an inadequate receiver size) or when the evaporator is at it's lowest temperature. A range of levels is permissible for normal operation.
Regards. Andy.
__________________
If you can't fix it leave it that no one else will
Reply With Quote
Sponsored links
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
liquid line sight glass mystery austech Technical Discussions 19 18-07-2006 08:16 PM
Sight glass , Flashing ? kfjoe Fundamentals 15 14-02-2004 05:41 AM
Sight Glass Located Abe Trouble Shooting 3 22-01-2002 02:22 AM
Sight Glass, Abe Trouble Shooting 4 03-08-2001 08:36 PM


All times are GMT +1. The time now is 05:17 PM.

 

Powered by vBulletin® Version 3.7.4
Copyright ©2000 - 2009, Jelsoft Enterprises Ltd.
This forum and its pages must not be copied or reprinted without the written consent of Refrigeration Engineer.com.
This forum is a free and open discussion board.
Refrigeration-Engineer.com, the administrators and Moderators of this site are not responsible for content posted here.Ad Management by RedTyger