Quote:
Originally posted by BritCit_Juve
I just thought you might be getting lonely in here. Changing wires isn't technical thats why there are so many electricians about.
|
Whoa there BCJ, you'll be upsetting the natives
Mind you, I caught myself out the other day by listening to the account of an ac fault and not checking it
completely myself.
A unit had been installed (2nd hand from client) and worked fine, then it had to be moved after which it didn't work. The report said that it HAD worked in the new position but didn't now.
Following what service info I had the fault appeared to be in the outdoor control board. Due to the age of the unit I recommended that the indoor board was replaced as well. So I replaced the outdoor board, same fault code shown but different signal voltages from the last test. So maybe something was going right.
Anyway, swapped the indoor board and still the damn thing wouldn't work
Rechecked all the cabling again and found that the installer had wired in a condensate pump putting the neutral into the interconnecting signal wire. So that's were my volts dissappeared too.
Problem solved, unit working, crept away very quietly