A/C Close Control with Copeland Scrolls.

My colleague asked me a question which I could not answer.
I said I would ask the guys on the forum, they may know?

Basically when you need to replace a scroll comp.
Where 1 has failed ( Phase down to earth ).
Can you just change the one.
When they are on the same base plate and linked with a horizontal oil line between them?
How do you determine what the oil levels in each compressor is?
Has anyone just changed one?
And did they add any oil.
In fact, how would you add oil to a sealed system?
Sorry to be so thick.
But it's not my area of expertise!
Cheers Grizzly
Reply With Quote
  #2  
Old 02-12-2009, 08:22 PM
Brian_UK's Avatar
Brian_UK Brian_UK is offline
Moderator
Site Moderator : and general nice guy
 
Join Date: Mar 2001
Location: Dorset
Age: 62
Posts: 7,500
Rep Power: 19
Brian_UK has a spectacular aura aboutBrian_UK has a spectacular aura aboutBrian_UK has a spectacular aura about
Re: A/C Close Control with Copeland Scrolls.

I would assume that there is some means of access to the system, Schraeder, back-seat valve, so just pump the oil in.

Or if under vacuum, suck it in.

Checking levels,?? When the oil line is cut would it be possible to get a flex tube into the oil sump to drain out the remaining before a refill?
__________________
Brian
PERCUSSIVE MAINTENANCE. The fine art of whacking the crap out of a piece of kit to get it to work again.
You should always give 100% at work...
12% Monday; 23% Tuesday; 40% Wednesday; 20% Thursday; 5% Friday
Reply With Quote
Sponsored links
  #3  
Old 02-12-2009, 08:33 PM
Goober's Avatar
Goober Goober is online now
regular poster
 
Join Date: Aug 2008
Location: Auckland
Age: 41
Posts: 77
Rep Power: 3
Goober is on a distinguished road
Re: A/C Close Control with Copeland Scrolls.

So.....if I understand right...you have two scroll compressors piped in tandem? common suction? and an oil equalizing line between the two? On an AC unit? correct?

I've just done such an exercise on a two scroll compressor Package AC unit. Wasn't close control though.

I changed one compressor, you have to assume that the oil is level in both compressors, due to the equalizing line. The only way to really change the oil in both comps is to remove both comps and tip them on there side and drain the oil from the suction stub, then either measure the oil removed and replace with same or go to the specs for that compressor and see what the oil charge is. Then prior to welding up the suction stub pour in the oil, or......if you've welded the suction stub or if the compressor can't be removed cut the oil equalizing line and drain oil that way then charge oil in through suction gauge port...Hope this helps
Reply With Quote
  #4  
Old 02-12-2009, 09:04 PM
chemi-cool's Avatar
chemi-cool chemi-cool is online now
Moderator
Site Moderator : and general nice guy
 
Join Date: Sep 2003
Location: ISRAEL
Age: 58
Posts: 2,615
Rep Power: 9
chemi-cool will become famous soon enough
Re: A/C Close Control with Copeland Scrolls.

Had to do it once on laser machine water chiller.

As Goober explained, took out both compressors, draind all the oil, put the good one and a new one back, add the missing oil and back to work.

On every compressor name plate you can also see the amount and type of oil.

http://www.hvacrinfo.com/cope_ae_bulletins/TAE1320.PDF
__________________
"All things are possible until they are proved impossible - and even the
impossible may only be so, as of now."
Reply With Quote
  #5  
Old 02-12-2009, 10:03 PM
monkey spanners's Avatar
monkey spanners monkey spanners is online now
VIP Poster
 
Join Date: Aug 2006
Location: england
Age: 36
Posts: 1,649
Rep Power: 7
monkey spanners will become famous soon enoughmonkey spanners will become famous soon enough
Re: A/C Close Control with Copeland Scrolls.

Just an idea, not actually tried, remove oil level plug from new compressor and measure how much come out. Remove duff compressor which would allow oil level to drop to oil level plug level in the two good comps. Fit new comp. Put in three times amount of oil removed from new compressor, plus a bit for the pipe.

There is a special Emkarate oil for these.
Reply With Quote
  #6  
Old 02-12-2009, 10:32 PM
Grizzly's Avatar
Grizzly Grizzly is online now
VIP Poster
I am starting to push the Mods: of RE
 
Join Date: Sep 2007
Location: Somerset
Age: 56
Posts: 1,932
Rep Power: 5
Grizzly will become famous soon enoughGrizzly will become famous soon enough
Re: A/C Close Control with Copeland Scrolls.

Thanks so far guys I will come back asap with more info!
Grizzly
Reply With Quote
  #7  
Old 02-12-2009, 11:02 PM
lowcool's Avatar
lowcool lowcool is offline
VIP Poster
 
Join Date: Feb 2008
Location: adelaide sth.oz
Posts: 917
Rep Power: 3
lowcool is on a distinguished road
Re: A/C Close Control with Copeland Scrolls.

i would even go as far as putting a sightglass in the balance line if possible.oil colour can be an indicator to acid in the system
__________________
mmm to beer or not to beer...........lets drink breakfast
Reply With Quote
  #8  
Old 02-12-2009, 11:17 PM
El Padre's Avatar
El Padre El Padre is offline
Senior Poster
 
Join Date: Oct 2007
Location: Britain
Posts: 185
Rep Power: 3
El Padre is on a distinguished road
Re: A/C Close Control with Copeland Scrolls.

Faced the same dilemma before on VRV systems, have always only replaced the faulty compressor and then monitored closely oil return and temperature, and I always check the quantity of oil in the faulty compressor, I think that adding oil can only be done if you know how much is in the entire system, which is unlikely. You will have to pump the oil in as you won't be able to isolate it and use a vac pump, I have always avoided tipping a scroll compressor on its side as I was told that the spring can become unseated, is that true?

Cheers
__________________
Tutto il Mondo e un Paese
Reply With Quote
Sponsored links
  #9  
Old 08-12-2009, 08:50 PM
SkyWalker's Avatar
SkyWalker SkyWalker is offline
regular poster
 
Join Date: Nov 2006
Location: Nottingham UK
Posts: 135
Rep Power: 4
SkyWalker is on a distinguished road
Re: A/C Close Control with Copeland Scrolls.

Quote:
Originally Posted by El Padre View Post
I was told that the spring can become unseated, is that true?
what spring? i have cut a few scrolls open and never come across one, if anyone knows different im all ears!
Reply With Quote
  #10  
Old 08-12-2009, 10:30 PM
Grizzly's Avatar
Grizzly Grizzly is online now
VIP Poster
I am starting to push the Mods: of RE
 
Join Date: Sep 2007
Location: Somerset
Age: 56
Posts: 1,932
Rep Power: 5
Grizzly will become famous soon enoughGrizzly will become famous soon enough
Re: A/C Close Control with Copeland Scrolls.

A Little bit more info!
Apparently these are known as Tandem systems.
There is as I said an oil balance line between the 2 compressors.
There is also a suction pressure balance line between the 2 comps.
Makes sense really as otherwise the
oil would migrate to the compressor with the lowest suction pressure.
Anyway we are going to give the customer the choice of repair!
Basically we have been advised that these are supplied as a pair on one baseplate.
Therefore unless they are replaced as a pair.
There would be no manufacturers warranty.
So we can do the cheaper job by replacing 1 comp but!
There would be no warranty.
Personally as they have quite a few of these.
It would make sense to replace the pair and keep the spare working one this time.
And should any other comp fail
a working pair could be made up.
Grizzly
Reply With Quote
  #11  
Old 09-12-2009, 12:33 AM
al's Avatar
al al is online now
Veteran Poster
I am starting to push the Mods: of RE
 
Join Date: Mar 2001
Location: ireland
Age: 40
Posts: 425
Rep Power: 10
al is on a distinguished road
Re: A/C Close Control with Copeland Scrolls.

Steve

We would also replace both compressors, the old york rooftops came with tandems and were supplied on a single base plate, we tried individual replacement(with clean up driers etc) but kept losing compressors, cheaper to go tandem in the long run.

Al
Reply With Quote
  #12  
Old 09-12-2009, 07:41 AM
Grizzly's Avatar
Grizzly Grizzly is online now
VIP Poster
I am starting to push the Mods: of RE
 
Join Date: Sep 2007
Location: Somerset
Age: 56
Posts: 1,932
Rep Power: 5
Grizzly will become famous soon enoughGrizzly will become famous soon enough
Re: A/C Close Control with Copeland Scrolls.

Was that the Old Bristol type?
This isn't a York
Not with Copeland' on it!
It's a Denco Unit.
Cheers Al.
Steve.
Reply With Quote
Sponsored links
  #13  
Old 09-12-2009, 01:42 PM
desA's Avatar
desA desA is online now
VIP Poster
 
Join Date: Mar 2009
Location: KZN, South Africa
Age: 50
Posts: 1,674
Rep Power: 3
desA will become famous soon enough
Re: A/C Close Control with Copeland Scrolls.

As I understand these Tandem sets, the compressors are closely matched in performance.

Perhaps swapping in a new compressor could create an imbalance in the tandem set. Is this just a good sales pitch on the compressor manufacturer's part, or an operational reality?
__________________
High-temperature, high-COP heat-pumps.

=> adT heat-pumps ::: Advanced energy-recovery systems ===>>>
Reply With Quote
  #14  
Old 09-12-2009, 02:43 PM
TRASH101's Avatar
TRASH101 TRASH101 is offline
Veteran Poster
I am starting to push the Mods: of RE
 
Join Date: Mar 2007
Location: england
Posts: 321
Rep Power: 4
TRASH101 is on a distinguished road
Re: A/C Close Control with Copeland Scrolls.

Grizzly

I've changed a couple of copelands in tandem arrangement and haven't had any problems yet

If you change one then take out the other (its easy cause you will probabley have to cut the suction and oil balance pipes) drain the oil out of both then purge as best you can your condenser(not a prob. usually if it is higher and no traps in pipework) evap and the drier. Add it all up then subtract your new copelands fill weight then charge up to full amount with new oil.
__________________
Quidvis Recte Factum Quamvis Humile Praeclarum.

Latine dictum, sit altum videtur.

Si hoc comprehendere potes, gratias age magistro Latinae.
Reply With Quote
  #15  
Old 09-12-2009, 02:51 PM
TRASH101's Avatar
TRASH101 TRASH101 is offline
Veteran Poster
I am starting to push the Mods: of RE
 
Join Date: Mar 2007
Location: england
Posts: 321
Rep Power: 4
TRASH101 is on a distinguished road
Re: A/C Close Control with Copeland Scrolls.

Quote:
Perhaps swapping in a new compressor could create an imbalance in the tandem set. Is this just a good sales pitch on the compressor manufacturer's part, or an operational reality?
Desa

I've found no cause for concern as far as an imbalance in the set. I believe the manufacturers(Denco) just don't want people cutting and brazing the balance lines. They have supplied single comps. before for fitting in tandem systems but I think GEA have took over things now.
__________________
Quidvis Recte Factum Quamvis Humile Praeclarum.

Latine dictum, sit altum videtur.

Si hoc comprehendere potes, gratias age magistro Latinae.
Reply With Quote
  #16  
Old 09-12-2009, 03:39 PM
desA's Avatar
desA desA is online now
VIP Poster
 
Join Date: Mar 2009
Location: KZN, South Africa
Age: 50
Posts: 1,674
Rep Power: 3
desA will become famous soon enough
Re: A/C Close Control with Copeland Scrolls.

^ Thanks very much for the wise advice. Much obliged.
__________________
High-temperature, high-COP heat-pumps.

=> adT heat-pumps ::: Advanced energy-recovery systems ===>>>
Reply With Quote
Sponsored links
  #17  
Old 10-12-2009, 03:28 AM
Magoo's Avatar
Magoo Magoo is offline
VIP Poster
 
Join Date: May 2007
Location: Auckland
Age: 60
Posts: 1,144
Rep Power: 5
Magoo will become famous soon enough
Re: A/C Close Control with Copeland Scrolls.

Grizzly
Go back to school. Bob basic shyte and you suck hole this site with a huge rep power and a squillion posts. You must be an electrician with half the knowledge.
Reply With Quote
  #18  
Old 10-12-2009, 06:45 AM
Grizzly's Avatar
Grizzly Grizzly is online now
VIP Poster
I am starting to push the Mods: of RE
 
Join Date: Sep 2007
Location: Somerset
Age: 56
Posts: 1,932
Rep Power: 5
Grizzly will become famous soon enoughGrizzly will become famous soon enough
Re: A/C Close Control with Copeland Scrolls.

Quote:
Originally Posted by Magoo View Post
Grizzly
Go back to school. Bob basic shyte and you suck hole this site with a huge rep power and a squillion posts. You must be an electrician with half the knowledge.
Just shows how little you know then eh!
You sir are out of order!
But fine Have it your way!
Bye
Grizzly
Reply With Quote
  #19  
Old 10-12-2009, 01:07 PM
monkey spanners's Avatar
monkey spanners monkey spanners is online now
VIP Poster
 
Join Date: Aug 2006
Location: england
Age: 36
Posts: 1,649
Rep Power: 7
monkey spanners will become famous soon enoughmonkey spanners will become famous soon enough
Re: A/C Close Control with Copeland Scrolls.

Quote:
Originally Posted by Magoo View Post
Grizzly
Go back to school. Bob basic shyte and you suck hole this site with a huge rep power and a squillion posts. You must be an electrician with half the knowledge.

That seems a little harsh there Magoo, or is this what passes for pleasant conversation in Auckland
Reply With Quote
  #20  
Old 08-04-2010, 12:31 PM
Denco Technical's Avatar
Denco Technical Denco Technical is offline
improving poster
 
Join Date: Apr 2010
Location: Hudds
Age: 36
Posts: 32
Rep Power: 0
Denco Technical is on a distinguished road
Re: A/C Close Control with Copeland Scrolls.

Hi,

We only supply tandem sets due to the warranty issue with changing only one and having any contaminants failing the compressor, also its very hard to braze on site and we have a special jig for this purpose.

You are welcome to purchase a single compressor but you run the risk and we don't off any warranty on a singular one.#

Thanks Rob
Denco Technical
Reply With Quote
  #21  
Old 07-07-2010, 11:34 PM
aeb200's Avatar
aeb200 aeb200 is offline
regular poster
 
Join Date: Nov 2005
Location: Southampton
Age: 32
Posts: 53
Rep Power: 5
aeb200 is on a distinguished road
Re: A/C Close Control with Copeland Scrolls.

Quote:
Originally Posted by Denco Technical View Post
Hi,

also its very hard to braze on site and we have a special jig for this purpose.
"Special Jig" -I have usually just tilt compressors on a kerb in the car park when i change these compressors.
It allows keeps oil out of balance line and allows rod to run nicely around joint.

It is a shame the isn't a special jig to get them out of the unit- the common suction line is usually higher than the lip of the fan deck- you have to turn compressors on their side to get them out!!!
Reply With Quote
  #22  
Old 26-07-2010, 03:12 PM
Denco Technical's Avatar
Denco Technical Denco Technical is offline
improving poster
 
Join Date: Apr 2010
Location: Hudds
Age: 36
Posts: 32
Rep Power: 0
Denco Technical is on a distinguished road
Re: A/C Close Control with Copeland Scrolls.

Quote:
Originally Posted by aeb200 View Post
"Special Jig" -I have usually just tilt compressors on a kerb in the car park when i change these compressors.
It allows keeps oil out of balance line and allows rod to run nicely around joint.

It is a shame the isn't a special jig to get them out of the unit- the common suction line is usually higher than the lip of the fan deck- you have to turn compressors on their side to get them out!!!
Appologies i stand corrected maybe a pavment outside is suitable enough for the job.
Reply With Quote
  #23  
Old 26-07-2010, 11:10 PM
Brian_UK's Avatar
Brian_UK Brian_UK is offline
Moderator
Site Moderator : and general nice guy
 
Join Date: Mar 2001
Location: Dorset
Age: 62
Posts: 7,500
Rep Power: 19
Brian_UK has a spectacular aura aboutBrian_UK has a spectacular aura aboutBrian_UK has a spectacular aura about
Re: A/C Close Control with Copeland Scrolls.

Quote:
Originally Posted by Denco Technical View Post
Apologies i stand corrected maybe a pavement outside is suitable enough for the job.
When on site, sometimes you have to make do with what is available.

Site staff do not have the benefit of enclosed, fully fitted workshops.
__________________
Brian
PERCUSSIVE MAINTENANCE. The fine art of whacking the crap out of a piece of kit to get it to work again.
You should always give 100% at work...
12% Monday; 23% Tuesday; 40% Wednesday; 20% Thursday; 5% Friday
Reply With Quote
  #24  
Old 03-08-2010, 03:09 AM
airlift123's Avatar
airlift123 airlift123 is offline
Registered User
Hey, I am new to : RE
 
Join Date: Nov 2009
Location: L.A. California
Posts: 2
Rep Power: 0
airlift123 is on a distinguished road
Wink Re: A/C Close Control with Copeland Scrolls.

That's odd. Here in the U.S. you would rarely come across two scrolls in tandem. In Low temp refrigeration possibly. Ammonia or R-502 systems. A compressor is allways warranted by the serial# no matter even if you only replaced one.
Reply With Quote
Sponsored links
  #25  
Old 03-08-2010, 01:07 PM
Rudi Effendi's Avatar
Rudi Effendi Rudi Effendi is offline
Registered User
Hey, I am new to : RE
 
Join Date: Apr 2010
Location: Indonesia
Posts: 1
Rep Power: 0
Rudi Effendi is on a distinguished road
Re: A/C Close Control with Copeland Scrolls.

I just add and be carefully of rotation electrical system compressor, CW or CCW?
Reply With Quote
Sponsored links
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
Denco Close Control Units Freecool Air Conditioning 12 05-05-2010 12:50 PM
Leak on Airedale Close Control, Help!! Bash1803 Air Conditioning 19 29-09-2009 09:23 AM
Airedale Close Control Service and Technical Manuals? Mozambezi Air Conditioning 3 24-02-2009 12:41 AM
Close Control Definition 2aces Air Conditioning 3 28-01-2009 11:09 PM
wall mounted close control dannycool Air Conditioning 15 25-01-2009 08:36 PM


All times are GMT +1. The time now is 08:06 PM.

 

Powered by vBulletin® Version 3.7.4
Copyright ©2000 - 2010, Jelsoft Enterprises Ltd.
This forum and its pages must not be copied or reprinted without the written consent of Refrigeration Engineer.com.
This forum is a free and open discussion board.
Refrigeration-Engineer.com, the administrators and Moderators of this site are not responsible for content posted here.Ad Management by RedTyger