What would be the normal low side and high side pressures on a R22 air conditioning system with the folowing parameters

Ambient 30 Degrees Celcius
Remote Controller set at -16C

Reply With Quote
  #2  
Old 25-05-2001, 10:31 PM
Gary's Avatar
Gary Gary is online now
VIP Poster
 
Join Date: Apr 2001
Location: New Port Richey, Florida - USA
Age: 64
Posts: 3,525
Rep Power: 12
Gary will become famous soon enough
Pressures are only meaningful when converted to saturation temperature, and even then they represent only a small part of the refrigeration or A/C picture.

If you want to understand what's going on in a system, you need the following:

High side saturation temp.
Condenser air in temp.
Condenser air out temp.
Liquid line temp at receiver outlet.
Liquid line temp at TXV inlet.
Low side saturation temp.
Evaporator air in temp.
Evaporator air out temp.
Suction line temp near compressor inlet.
Suction line temp at TXV sensing bulb.

All of these variables affect pressures.

__________________
Author of TECH Method troubleshooting books
Reply With Quote
Sponsored links
  #3  
Old 26-05-2001, 11:33 PM
Brian_UK's Avatar
Brian_UK Brian_UK is online now
Moderator
Site Moderator : and general nice guy
 
Join Date: Mar 2001
Location: Dorset
Age: 61
Posts: 6,321
Rep Power: 16
Brian_UK will become famous soon enoughBrian_UK will become famous soon enough
As Gary correctly said there is a lot a information required before you can state what is correct for a given system.

However, think on this - you are only trying to cool air not freeze it so what 'range' of low side pressures would you expect?

Also, most important - - it doesn't matter a rat's ar*e what temperature the remote controller is set at
__________________
Brian
PERCUSSIVE MAINTENANCE. The fine art of whacking the crap out of a piece of kit to get it to work again.
ʎɐqǝ uo pɹɐoqʎǝʞ ɐ ʎnq ı ǝɯıʇ ʇsɐן ǝɥʇ sı sıɥʇ.
"You know "that look" women get when they want sex? Me neither." --Steve Martin
Reply With Quote
  #4  
Old 01-06-2001, 02:15 PM
Jack Lester's Avatar
Jack Lester Jack Lester is offline
improving poster
 
Join Date: May 2001
Location: Los Angeles
Posts: 23
Rep Power: 0
Jack Lester is on a distinguished road
Wink

Perhaps I missunderstand your aplication but here are some thoughts Abe. I asume your remote control is controlling the temp of the area to be cooled. -16c to me is a freezer which equates to 3.2F in the states. I usually figure a 10F degree TD thru the coil or the coil is 10 degress colder then the air. This means the coil would be -6.8F or -18.5C. look at the TP chart and see what preasure this is and check your gauges. Should be fairly close. If not check your superheat thru the coil. Of course there is preasure loss depending on piping but you can come close.
__________________
Jack
Reply With Quote
  #5  
Old 05-06-2001, 10:20 PM
Abe's Avatar
Abe Abe is offline
Moderator
Site Moderator : and general nice guy
 
Join Date: Apr 2001
Location: UK
Posts: 2,089
Rep Power: 11
Abe is on a distinguished road
Thank you Jack for your reply, stat is set at 16 c and not minus 16
I have info now to go on so thanks a lot
As they say you learn a little every day


[Edited by Abe on 05-06-2001 at 10:37 PM]
Reply With Quote
Sponsored links
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
System design: first cost or operating cost? US Iceman NH3 35 13-12-2006 12:51 PM
Operating Theatres nick_nst@aapt.n Air Conditioning 6 05-06-2006 12:19 PM
CARE refigerants by BOC dogma Refrigerants 6 03-02-2006 08:30 AM
Liquid Pressure Amplification WebRam Refrigeration Articles 7 06-06-2004 02:37 AM
System Design Pressures herefishy Fundamentals 11 27-01-2004 01:31 PM


All times are GMT +1. The time now is 07:03 AM.

 

Powered by vBulletin® Version 3.7.4
Copyright ©2000 - 2009, Jelsoft Enterprises Ltd.
This forum and its pages must not be copied or reprinted without the written consent of Refrigeration Engineer.com.
This forum is a free and open discussion board.
Refrigeration-Engineer.com, the administrators and Moderators of this site are not responsible for content posted here.Ad Management by RedTyger