Need advice on a Daikin unit. Installed in a larder room which contains a 45 cubic foot chest type freezer and a hot water geyser. Room gets quite warm therefore. Room is completely enclosed with no fresh air , almost like a cold room. The only cooling is from a 9000 btu air conditionining unit.
Back pressure is reading 50 Psi running on R22. Temp within room is around 25C
Room measures 12 feet X 10 8 feet wide. 10 feet high Compressor on freezer unit is 3/4 Hp.
Air Con is working its heart out. Is the air con sized right? Would a air exhaust fan to expel the heat generated from the chest freezer help? Or a bigger sized air conditioning unit
All components on air conditioner check out right
Reply With Quote
  #2  
Old 26-05-2001, 11:49 PM
Brian_UK's Avatar
Brian_UK Brian_UK is online now
Moderator
Site Moderator : and general nice guy
 
Join Date: Mar 2001
Location: Dorset
Age: 61
Posts: 6,318
Rep Power: 16
Brian_UK will become famous soon enoughBrian_UK will become famous soon enough
Quote:
Originally posted by Abe
snip- and a hot water geyser. Room is completely enclosed with no fresh air ...
Would a air exhaust -snip
Abe, is this 'geyser gas powered? if it is then were is the combustion air coming from and why are you working in such a dangerous place?

Yes, any ventilation will normally help dissipate heat.

It does appear that the A/C is undersized if it will not achieve a lower temperature but holding 25°C isn't too bad for the equipment listed.

Mind you I expect if you set the temp. control at 25 the temperature would start sitting around 26
__________________
Brian
PERCUSSIVE MAINTENANCE. The fine art of whacking the crap out of a piece of kit to get it to work again.
ʎɐqǝ uo pɹɐoqʎǝʞ ɐ ʎnq ı ǝɯıʇ ʇsɐן ǝɥʇ sı sıɥʇ.
"You know "that look" women get when they want sex? Me neither." --Steve Martin
Reply With Quote
Sponsored links
  #3  
Old 28-05-2001, 06:56 PM
Abe's Avatar
Abe Abe is online now
Moderator
Site Moderator : and general nice guy
 
Join Date: Apr 2001
Location: UK
Posts: 2,089
Rep Power: 11
Abe is on a distinguished road

Thanks Brian,
The geyser is electric powered, 230 volts. Location is South Africa where they dont have gas, geyser is a big beast 200 gallons capacity.
Ive put to the customer that air con is undersized.


Reply With Quote
  #4  
Old 29-05-2001, 12:30 AM
Gary's Avatar
Gary Gary is online now
VIP Poster
 
Join Date: Apr 2001
Location: New Port Richey, Florida - USA
Age: 64
Posts: 3,525
Rep Power: 12
Gary will become famous soon enough
Did the room, in the past, maintain the desired temperature? If so, what has been added since then?

What is the desired room temp?

What is the kW usage for the geyser?

If you install an exhaust fan, the room will be in a negative pressure. You should bring in fresh air to make up for the exhausted air. That fresh air will add some load, however. It would be better, cooling-wise, to duct the fresh air and exhaust directly to and from the freezer condenser.
__________________
Author of TECH Method troubleshooting books
Reply With Quote
  #5  
Old 29-05-2001, 12:51 PM
subzero*psia's Avatar
subzero*psia subzero*psia is offline
Veteran Poster
 
Join Date: Feb 2001
Location: USA
Age: 48
Posts: 266
Rep Power: 9
subzero*psia is on a distinguished road
Smile

What is the wattage the freezer condensing unit runs at? What is the load on the freezer, what product is it and what is the temperature of the product when it goes into the freezer, also how many pounds of of product and how often is it loaded?

Geyser... I am afraid you have me there, I don't know what it is by that term?

If the freezer is a 200 volt unit and runs at 7 amperes then your condenser alone is putting out roughly 4500 btu/hr. And that doesn't account for the btu's being removed from the product either... nor does it account for people that may be in the room nor lighting. And on top of that you have this "geyser" unit? I realize this post is coming in late, but can you give us any more information and if you did upsize the system (sounds like a good idea), what size system did you go to?

__________________
:D
[b]Dean[/b]
[b]Subzero*psia[/b]

[b]Extinction is simply proof of failure to adapt. [/b]
Reply With Quote
  #6  
Old 29-05-2001, 02:36 PM
WebRam's Avatar
WebRam WebRam is offline
Administrator
Boss of RE : and always up for a bribe
 
Join Date: Jan 2001
Location: Fife, Scotland.
Age: 51
Posts: 1,159
Rep Power: 20
WebRam is on a distinguished road
not often that you get caught out Dean

a "Geyser" is a hot water boiler
__________________
<img src=http://www.refrigeration-engineer.com/resignature.jpg border=0 alt= />
Reply With Quote
  #7  
Old 29-05-2001, 02:50 PM
subzero*psia's Avatar
subzero*psia subzero*psia is offline
Veteran Poster
 
Join Date: Feb 2001
Location: USA
Age: 48
Posts: 266
Rep Power: 9
subzero*psia is on a distinguished road
Smile

WOW!! In that case I can see what could possibly be a huge problem for a 9000 btu/hr air conditioner! Odd that the boiler is in an a/c room rather than a room all to itself with a fresh air supply... hmmmmm.
__________________
:D
[b]Dean[/b]
[b]Subzero*psia[/b]

[b]Extinction is simply proof of failure to adapt. [/b]
Reply With Quote
  #8  
Old 30-05-2001, 01:10 AM
Jack Lester's Avatar
Jack Lester Jack Lester is offline
improving poster
 
Join Date: May 2001
Location: Los Angeles
Posts: 23
Rep Power: 0
Jack Lester is on a distinguished road
Talking

I don't know much about Air conditioning but it would seem to me that your very undersized. A 3/4 hp compressor develops a lot of heat. Heat of compresson, work heat from the motor and heat of rejection. I don't know what a hot water geyser is but it sounds like it generates heat also. Are the walls insullated? If so with what? Is it a high use area? 25c is very warm. I would say you need to atleast double the size.If it were me I'd go to 24k BTU.. Who knows what else they might want to stick in there. Good Luck Yikes I just read down looks like all the bases have been covered.. I now know what a water geyser is...LOL
__________________
Jack
Reply With Quote
Sponsored links
  #9  
Old 05-06-2001, 10:34 PM
Abe's Avatar
Abe Abe is online now
Moderator
Site Moderator : and general nice guy
 
Join Date: Apr 2001
Location: UK
Posts: 2,089
Rep Power: 11
Abe is on a distinguished road
Sorry for my delay in responding to all the help Im getting. Im in South Africa at the moment , the owner of the site in question is the owner of the JUMBO CASH AND CARRY in Fordsburg, and a rich guy, whos gone into the trouble of installing an air con in his larder!!!
His got a mansion in Jan Smuts Ave near Wits,

Actually an air con company sold him the air con, saying it would solve his problems.
I would have gone for a cellar cooling type system instead, Theres a large chest type freezer and this huge boiler in the room, and its like a sauna in there, with no air in, or air exhaust in place.
Ive told him that the 9000 btu system is too small.

Thanks for the help Brian trying to organise a local tech to help, my cell no is 083-725-1548

By the way I met Andre at Coolfrost in Boksburg. He says Hello to you.

Im returning to UK shortly, the violance here is scaring me silly, the fear is even worse!!! of being hijacked and mugged !!!
Reply With Quote
  #10  
Old 06-06-2001, 12:52 PM
subzero*psia's Avatar
subzero*psia subzero*psia is offline
Veteran Poster
 
Join Date: Feb 2001
Location: USA
Age: 48
Posts: 266
Rep Power: 9
subzero*psia is on a distinguished road
Unhappy

Sheesh! Sounds like you guys need a war dog for a side kick to watch your back!
__________________
:D
[b]Dean[/b]
[b]Subzero*psia[/b]

[b]Extinction is simply proof of failure to adapt. [/b]
Reply With Quote
  #11  
Old 06-06-2001, 08:37 PM
Abe's Avatar
Abe Abe is online now
Moderator
Site Moderator : and general nice guy
 
Join Date: Apr 2001
Location: UK
Posts: 2,089
Rep Power: 11
Abe is on a distinguished road
Hello Brian,
I gave you the wrong cell number, its 083-725-1543
Im flying out tomorrow evening, Thursday, to Birm and on to Leicester
My number in UK is 0116-2627540
Ill return to SA end of June
Ill read up your report properly when I get home
Im actually in Vereeniging tonight, near the River Square Shopping Complex
Ill try and see Andre tomorrow before I leave
He says he knows you well
Talking about hijacking, Two guys try to rob me in Pretoria yesterday.



Reply With Quote
  #12  
Old 12-03-2006, 02:59 AM
nick_nst@aapt.n's Avatar
nick_nst@aapt.n nick_nst@aapt.n is offline
rookie poster
Hey, I am new to : RE
 
Join Date: Mar 2006
Location: australia
Posts: 10
Rep Power: 0
nick_nst@aapt.n is on a distinguished road
Re: Is the air con too small

Hi Aiyub
Looking at the back pressure you've measured and the room temperature it looks like the system is either running low back pressures from either short of refrigerant or the filter or coil is blocked.You should have about 68 psi back pressure at this room temp.
Suggest looking for leaks or the filter or the system was never fully charged.Fully charge system and the cooling capacity of the unit should increase.
The suction line at the compressor should be sweating back at the compressor when operating correctly.

Nick
Reply With Quote
Sponsored links
  #13  
Old 12-03-2006, 12:25 PM
Sir Josiah Sodd's Avatar
Sir Josiah Sodd Sir Josiah Sodd is offline
regular poster
 
Join Date: Jul 2005
Location: UK
Posts: 60
Rep Power: 5
Sir Josiah Sodd is on a distinguished road
Re: Is the air con too small

Quote:
Originally Posted by nick_nst@aapt.n
Hi Aiyub

Suggest looking for leaks or the filter or the system was never fully charged.Fully charge system and the cooling capacity of the unit should increase.
Nice to see you, Nick, and keep posting, but this thread is over 5 years old......!
__________________
.
Sodd's the name...... Law's the game.
Established 1791 - still going strong.
Reply With Quote
  #14  
Old 12-03-2006, 12:47 PM
Abe's Avatar
Abe Abe is online now
Moderator
Site Moderator : and general nice guy
 
Join Date: Apr 2001
Location: UK
Posts: 2,089
Rep Power: 11
Abe is on a distinguished road
Re: Is the air con too small

Yes...........but it brought back memories.

I was in Johannesburg, near University of Witwatersrand
The house belonged to the big boss of Jumbo Cash and Carry....

I left soon after that, so Im not sure what happened......but this guy was so rich he even air conditioned his pantry!!
__________________
Opinions, statements and facts expressed do not constitute legal advice and are general in nature.
Seek appropriate professional assistance for definitive advice.
Reply With Quote
  #15  
Old 12-03-2006, 03:21 PM
nick_nst@aapt.n's Avatar
nick_nst@aapt.n nick_nst@aapt.n is offline
rookie poster
Hey, I am new to : RE
 
Join Date: Mar 2006
Location: australia
Posts: 10
Rep Power: 0
nick_nst@aapt.n is on a distinguished road
Re: Is the air con too small

Well then.It's probably fully out of refrigerant by now.
Nick
Reply With Quote
Sponsored links
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
crazy 3rd-world idea: aircon from small fridge lsemprini Fundamentals 72 29-05-2008 01:10 AM
Small Searle Cooler Abe Commercial 9 27-01-2006 07:07 AM
Building a small refrigerator rollerblade12 Fundamentals 4 13-01-2004 05:02 PM
How many small strands needed to equal pipe pressure drop? DaBit Fundamentals 17 25-08-2003 09:56 PM
R134a small chiller Robearbam Refrigerants 1 24-01-2003 06:15 AM


All times are GMT +1. The time now is 03:03 AM.

 

Powered by vBulletin® Version 3.7.4
Copyright ©2000 - 2009, Jelsoft Enterprises Ltd.
This forum and its pages must not be copied or reprinted without the written consent of Refrigeration Engineer.com.
This forum is a free and open discussion board.
Refrigeration-Engineer.com, the administrators and Moderators of this site are not responsible for content posted here.Ad Management by RedTyger