Had a call today to an A/C unit that wasn't cooling. Talk to the guy about his unit, hear about the previous visit (from our firm) and the tech who fitted a new condenser fan.

Couldn't quite tie up new fan with no cooling but the visit was young.

Anyway, started with the condensing unit which wasn't doing anything except showing some silly voltages at some of the terminals especially the one serving the fan. The the compressor starts up but not the fan

Back to the evaporator and controls - find the controller is not always switching the condenser fan on when it should do. Remove an autochangeover module and revert to manual changeover (from heat to cool) and the units seems to work fine again.

Now we get the interrogation about was the fan motor really faulty or was it the controls? How do answer that without upsetting at least one person?
__________________
Brian
PERCUSSIVE MAINTENANCE. The fine art of whacking the crap out of a piece of kit to get it to work again.
ʎɐqǝ uo pɹɐoqʎǝʞ ɐ ʎnq ı ǝɯıʇ ʇsɐן ǝɥʇ sı sıɥʇ.
"You know "that look" women get when they want sex? Me neither." --Steve Martin
Reply With Quote
  #2  
Old 24-05-2001, 03:17 PM
Gary's Avatar
Gary Gary is online now
VIP Poster
 
Join Date: Apr 2001
Location: New Port Richey, Florida - USA
Age: 64
Posts: 3,525
Rep Power: 12
Gary will become famous soon enough
This has all of the makings of a moral dillema. Does one cover for his fellow service tech and for his employer?

Was the motor really faulty? We don't know. It is entirely possible that the faulty motor burnt out the control.

That's the story I would tell.
__________________
Author of TECH Method troubleshooting books
Reply With Quote
Sponsored links
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
York chiller system trouble shoot lawrence7435 Trouble Shooting 4 06-03-2007 07:54 PM


All times are GMT +1. The time now is 11:49 AM.

 

Powered by vBulletin® Version 3.7.4
Copyright ©2000 - 2009, Jelsoft Enterprises Ltd.
This forum and its pages must not be copied or reprinted without the written consent of Refrigeration Engineer.com.
This forum is a free and open discussion board.
Refrigeration-Engineer.com, the administrators and Moderators of this site are not responsible for content posted here.Ad Management by RedTyger