Hi guys, I'm new to this forum but I think it's a very informative site. I would like to get some feedback on the reliability and problems of scroll compressors.Recently we have lost 4 scroll compressors due to what seems to be a lack of lubrication.These compressors were from different systems with no apparent "system" problems.
Reply With Quote
  #2  
Old 11-05-2001, 12:56 AM
acman's Avatar
acman acman is offline
improving poster
 
Join Date: Apr 2001
Posts: 20
Rep Power: 0
acman is on a distinguished road
Cool

Check rotation.Read amps.If 3 phase,reverse phases.
Reply With Quote
Sponsored links
  #3  
Old 11-05-2001, 02:06 AM
Jai's Avatar
Jai Jai is offline
rookie poster
 
Join Date: May 2001
Location: Trinidad,West Indies
Posts: 16
Rep Power: 0
Jai is on a distinguished road
Thumbs up Scroll problems

These systems were commissioned about 9 months ago and 2 out of 4 compressors failed after 5 months.The system is a York package Liquid chiller with 2 independant refrigerant circuits of 2 compressors each.When the system was started-up,the voltage,rotation,superheat,oil level,pressures etc. were verified.Also a voltage monitor with phase reversal protection was installed.What I found odd is that I had to add 2 gallons of oil to the system and the oil level remained low.Seems as the compressors were pumping the oil out. I am presently working on 2 York Scroll systems and it seems as the compressors are pumping the oil out.I have already added 3 gallons of oil to these systems and the oil level is still low. I have never had this problem with recips. unless its a system problem. I'm trying to find out if other techs. out there are having the same problem.
Reply With Quote
  #4  
Old 11-05-2001, 02:19 AM
Prof Sporlan's Avatar
Prof Sporlan Prof Sporlan is offline
Moderator
 
Join Date: Mar 2001
Location: St. Louis, MO
Posts: 512
Rep Power: 9
Prof Sporlan is on a distinguished road
Keep in mind that the oil you are adding to the system isn't disappearing..... the oil is likely residing in the chiller. An appropriate question to ask at this point is why the oil isn't returning back to the compressor.
__________________
[b]Prof Sporlan[/b]
Reply With Quote
  #5  
Old 12-05-2001, 01:02 AM
Gary's Avatar
Gary Gary is online now
VIP Poster
 
Join Date: Apr 2001
Location: New Port Richey, Florida - USA
Age: 64
Posts: 3,525
Rep Power: 12
Gary will become famous soon enough
I agree, Prof. It isn't that the oil is pumping out of the compressor. The problem is that it isn't returning. Adding oil to a system is almost always a mistake.
__________________
Author of TECH Method troubleshooting books
Reply With Quote
  #6  
Old 12-05-2001, 03:19 AM
Jai's Avatar
Jai Jai is offline
rookie poster
 
Join Date: May 2001
Location: Trinidad,West Indies
Posts: 16
Rep Power: 0
Jai is on a distinguished road
Thumbs up

Gary I agree with you and Prof. Sporlan where the oil can be leaving and not returning.What does not seem to make sense is the fact that this is a package chiller so there is no "external" piping to cause oil return problems. Also the load in the evaporator is not lower than normal.(the g.p.m. is running slightly higher than design). Is there a tendency for Scroll compressors to circulate more oil through the system than Recips.
Reply With Quote
  #7  
Old 12-05-2001, 03:47 AM
Gary's Avatar
Gary Gary is online now
VIP Poster
 
Join Date: Apr 2001
Location: New Port Richey, Florida - USA
Age: 64
Posts: 3,525
Rep Power: 12
Gary will become famous soon enough
I know of no particular tendency for scroll compressors to circulate more oil, and the fact that you keep adding more and it doesn't come back should tell you something.

Designed by the manufacturer doesn't necessarily translate to perfect design, although they tend to learn from their mistakes. Perhaps you are witnessing some of their mistakes.

I would want to look very closely at the suction line sizing/sloping/trapping, as well as the chiller barrel flow pattern. Ask yourself, "Where is the low spot that is trapping the oil, while the refrigerant flows above it".

As the Prof points out, it hasn't disappeared, it is hiding somewhere.
__________________
Author of TECH Method troubleshooting books
Reply With Quote
  #8  
Old 13-05-2001, 10:15 PM
Brian_UK's Avatar
Brian_UK Brian_UK is online now
Moderator
Site Moderator : and general nice guy
 
Join Date: Mar 2001
Location: Dorset
Age: 61
Posts: 6,318
Rep Power: 16
Brian_UK will become famous soon enoughBrian_UK will become famous soon enough
Quote:
Originally posted by Jai
this is a package chiller so there is no "external" piping to cause oil return problems
We had to change out a compressor on a Daikin packaged chiller during last summer. One team started and I had to finish the final connection and get it running again.

Found a lack of gas flow due to the discharge line up to the TEV being full of oil.

Problem appeared to be bad location causing high pressure trips during hot weather....probably pumped out the oil and killed the compressor that way.
__________________
Brian
PERCUSSIVE MAINTENANCE. The fine art of whacking the crap out of a piece of kit to get it to work again.
ʎɐqǝ uo pɹɐoqʎǝʞ ɐ ʎnq ı ǝɯıʇ ʇsɐן ǝɥʇ sı sıɥʇ.
"You know "that look" women get when they want sex? Me neither." --Steve Martin
Reply With Quote
Sponsored links
  #9  
Old 26-06-2002, 03:59 AM
Preston Roy Powell's Avatar
Preston Roy Powell Preston Roy Powell is offline
rookie poster
 
Join Date: Apr 2001
Location: Tyler, Texas
Age: 39
Posts: 12
Rep Power: 0
Preston Roy Powell is on a distinguished road
Scroll losses!!

First ckeck you line size.. Then ckeck your super heat back to the compressor.

1. DId the compessor ground out!!
2. Are slugging the compressor
3. Are you starving the compressor.
__________________
Preston Roy Powell
[url]www.thinkcool.net[/url]
Reply With Quote
  #10  
Old 26-06-2002, 06:07 AM
Dan's Avatar
Dan Dan is online now
Moderator
Site Moderator : and general nice guy
 
Join Date: Feb 2001
Location: Tampa Florida
Posts: 1,087
Rep Power: 10
Dan is on a distinguished road
[quote]Found a lack of gas flow due to the discharge line up to the TEV
being full of oil. [\quote]

Last edited by Dan; 26-06-2002 at 06:14 AM..
Reply With Quote
  #11  
Old 28-06-2002, 08:36 PM
stevec's Avatar
stevec stevec is offline
rookie poster
 
Join Date: Apr 2002
Location: Samoa
Posts: 13
Rep Power: 0
stevec is on a distinguished road
One might expect some of the oils to come back to the compressor when it starts warm. Unless it is on 24 hr operation.You couls also check water flows etc.
One of the intersting points here being raised also is putting in oils when you can't see it on the ground!!! or ceiling or anywhere.
I have problems sometimes with some of our guys who believe if oil level is low it needs oil. As you all suggest step back and re focus.
Reply With Quote
  #12  
Old 08-10-2009, 08:52 PM
install monkey's Avatar
install monkey install monkey is offline
Registered User
Hey, I am new to : RE
 
Join Date: Oct 2007
Location: uk
Posts: 9
Rep Power: 0
install monkey is on a distinguished road
Re: Scroll problems

have you done acid test on each circuit ,were drier cores,contactors changed with new compressors,are the compressors short cycling,condenser coils clean,tev functioning correctly.mains problems on site???????????????
Reply With Quote
Sponsored links
  #13  
Old 08-10-2009, 09:35 PM
El Padre's Avatar
El Padre El Padre is offline
regular poster
 
Join Date: Oct 2007
Location: Britain
Posts: 110
Rep Power: 3
El Padre is on a distinguished road
Re: Scroll problems

You could try isolating one circuit to ensure compressors are running at 100% capacity which will ensure maximmum oil return, is there an oil return line from the evaporator?

Cheers
__________________
Tutto il Mondo e un Paese
Reply With Quote
  #14  
Old 08-10-2009, 10:04 PM
El Padre's Avatar
El Padre El Padre is offline
regular poster
 
Join Date: Oct 2007
Location: Britain
Posts: 110
Rep Power: 3
El Padre is on a distinguished road
Re: Scroll problems

Just a thought, is there a water flow problem on that site, did they leave flow rate measurements on the commissioning sheets? If you post the model number one of the Yorkies might be able to give you more information.

Cheers
__________________
Tutto il Mondo e un Paese
Reply With Quote
Sponsored links
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
Suction pressure problems on TS units at low ambient temps nova Transport 10 18-03-2006 08:35 PM
Problems LG don't want you to know about Andy W Air Conditioning 11 16-02-2006 05:52 PM
Oil return problems Peter_1 Industrial 37 23-08-2004 11:30 PM
Scroll Compressor dwallan Commercial 1 30-07-2001 04:18 AM


All times are GMT +1. The time now is 08:54 AM.

 

Powered by vBulletin® Version 3.7.4
Copyright ©2000 - 2009, Jelsoft Enterprises Ltd.
This forum and its pages must not be copied or reprinted without the written consent of Refrigeration Engineer.com.
This forum is a free and open discussion board.
Refrigeration-Engineer.com, the administrators and Moderators of this site are not responsible for content posted here.Ad Management by RedTyger