Just winding up this thread again.....Well, I finally got a look at this low humidity room on Friday and gained a bit more knowledge.
The system was designed and built as a skid system by Harris Environmental Systems of Andover, MA and uses two Copeland 35hp compressor packs. I have not been able to find out what caused the earlier compressor failures but my initial thoughts could be that they were due to oiling problems.
I still have to trace information on some of the kit fitted but am always looking for advice or comments from others.
The pack comprises Copeland N3DH-3500-TSD compressor with an AC & R S-1901 oil separator, remote air cooled condenser with a Sporlan ORI-10-65/225 (liquid) head pressure valve working in conjunction with a Sporlan ORD-4/20 (hot gas) head pressure valve to maintain pressure in the lquid receiver.
The evaporators have SVE-2-L1 valves with ORIT EPRs, the high pressure line to the ORIT is taken after the solenoid valve serving the hot gas bypass system used for capacity control. There is also a liquid quenching system to control the suction temperature.
We also have two Refrigeration Research 3704V suction accumulators with the quench system TEV(SVE-2-L1) sensing bulb located after the first accumulator.
First impressions are that there may be a problem with the oil separator on one system in particular. The oil returns from the separator via a hand valve, Sporlan C053S filter, sightglass and solenoid valve directly to the compressor crankcase.
When off the oil level in the crankcase is very nearly at the full sightglass level. With the compressor running there is froth on top of the oil and extreme agitation of the oil itself. The oil return sightglass is constantly running with what appears to be high temperature gas carrying oil with it. It does not look like oil with gas in it! My thinking is that the separator is not collecting oil and returning it but is open all the time.
If I shut off the hand valve then the crankcase oil level begins to drop and the agitation action reduces. I did not run this test for long as time was limited and I did not want to lose oil into the system late on a Friday
My first question of the accumulated minds out there is - does anyone have experience of the AC&R oil separator? Should it hold back the oil until released or just blow it back where it came from?