Fan Static Pressure

How to classified the term "Total Static Pressure", "External Static Pressure" & "Velocity Pressure" and how to use to calculate the air duct pressure drop, air grille, weatherproof louvre, air filters pressure drop.

What is a differential pressure meter.how to install to read the differential between the room.
__________________
vB Code is ON
Reply With Quote
  #2  
Old 04-10-2003, 06:38 AM
bhrobin's Avatar
bhrobin bhrobin is offline
rookie poster
 
Join Date: Apr 2001
Location: Topeka, Kansas
Age: 62
Posts: 16
Rep Power: 0
bhrobin is on a distinguished road
Perhaps I can help just a bit. Grilles, louvers and filters normally are given an individual "pressure drop" by their respective manufacturers. For example: a given filter might be rated by its manufacturer for 0.2" W.C. pressure drop at 300 feet per minute air velocity. The same will be true for louvers, etc. A fan or air hanlder manufacturer will rate the blower at a variety of "external static pressures" to deliver a given air flow rate. This will be in the form of a table or graph.
When you assemble all the data from the manufacturers about their respective devices, add them all together. Then calculate the additional static pressure drop from ducts, etc. to get the total air pressure drop seen by the air handler or fan.
I use a Dwyer "Magnehelic" gauge to read differential pressure. It has fittings for two hoses. One will go to the room and the other to the outside or another room or space. The differential pressure is then read directly on the gauge.
__________________
Bruce H. Robinson
bhrobin@anchor-robinson.com
company page: www.anchor-robinson.com
personal page: www.anchor-robinson.com/bruce01.html
Reply With Quote
Sponsored links
  #3  
Old 04-10-2003, 04:24 PM
watana's Avatar
watana watana is offline
improving poster
 
Join Date: Jul 2001
Location: hong kong
Age: 51
Posts: 27
Rep Power: 0
watana is on a distinguished road
thank you, Bruce

I will try the calculation, as my project is near completion.
__________________
vB Code is ON
Reply With Quote
  #4  
Old 05-10-2003, 06:43 AM
RogGoetsch's Avatar
RogGoetsch RogGoetsch is offline
Senior Poster
 
Join Date: Mar 2002
Location: San Francisco Bay Area
Posts: 182
Rep Power: 8
RogGoetsch is on a distinguished road
Not sure what you need to know if the project is near completion, but the terms you inquired about can be expained as follows:

In any fluid stream, there are two pressures present. The velocity pressure is the pressure exerted by the flowing mass in the direction of flow but it can't be measured alone. The second pressure is the static pressure which acts in all directions, and is the pressure that is exerted by the fluid on the walls of the duct or pipe.

The measurements need to be taken in a long enough section of tube or duct so that the flow stream is smooth, not turbulent.

If a sensing tube is placed in the stream parallel to the flow with an opening facing upstream, this probe will register the total pressure of the system, both velocity pressure and static pressure.

If another probe is inserted at right angles to the flow, this will register only the static pressure.

If the two probes are connected to a device (a manometer) so that the pressures oppose one another, the effect is to subtract the static pressure from the total pressure picked up by the first probe and the resultant reading gives the velocity pressure.
Reply With Quote
Sponsored links
Reply


Currently Active Users Viewing This Thread: 3 (0 members and 3 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
Building a wine cabinet Rory Technical Discussions 38 13-07-2004 08:28 PM
Liquid Pressure Amplification WebRam Refrigeration Articles 7 06-06-2004 02:37 AM
TEV capacity related to pressure drop DaBit CPU Overclockers 8 06-12-2002 06:11 PM
oil pressure problems on air dryer edge Trouble Shooting 1 16-07-2002 02:10 PM
Venturi effect at fan intake TAB TECH Air Conditioning 3 15-07-2002 02:57 AM


All times are GMT +1. The time now is 06:04 AM.

 

Powered by vBulletin® Version 3.7.4
Copyright ©2000 - 2009, Jelsoft Enterprises Ltd.
This forum and its pages must not be copied or reprinted without the written consent of Refrigeration Engineer.com.
This forum is a free and open discussion board.
Refrigeration-Engineer.com, the administrators and Moderators of this site are not responsible for content posted here.Ad Management by RedTyger