negative pressure ward for hospital

My company is having a job in Hong Kong, which previously had a big virus SARS, so need to convert the normal ward to a negative pressure ward.

By means of extract more air than the supply air, can anyone help me how to carry out the commissioning process, will there be CIBSE commissioning guide to follow?
__________________
vB Code is ON
Reply With Quote
  #2  
Old 02-09-2003, 09:01 PM
frank's Avatar
frank frank is online now
Moderator
Site Moderator : and general nice guy
 
Join Date: Oct 2001
Location: Nottingham UK
Age: 57
Posts: 3,314
Rep Power: 12
frank is on a distinguished road
Hi Watana

Air balancing is easy but you need the right gear to do it. Air velocities from each grille must be measured and converted into volume flow then added together to reach a total air input or extract from the space.

If you require a positive airflow then you should be looking for at least 10% more air in than out. If you require a negative flow then it is the other way around. You can of course design for more than 10% but this is dependant on the application.

Do you know how to convert velocity into volume flow?
Reply With Quote
Sponsored links
  #3  
Old 04-09-2003, 09:10 PM
Brian_UK's Avatar
Brian_UK Brian_UK is online now
Moderator
Site Moderator : and general nice guy
 
Join Date: Mar 2001
Location: Dorset
Age: 61
Posts: 6,318
Rep Power: 16
Brian_UK will become famous soon enoughBrian_UK will become famous soon enough
Watana, CIBSE Code A should cover your commissioning process but would suggest that the design consultant should specify the commissioning requirements.

Maintaining differential pressures across rooms does require some careful design and commissioning.

Considering the medical aspect put as much responsibility onto the designer as you possibly can.

Good luck with it.
__________________
Brian
PERCUSSIVE MAINTENANCE. The fine art of whacking the crap out of a piece of kit to get it to work again.
ʎɐqǝ uo pɹɐoqʎǝʞ ɐ ʎnq ı ǝɯıʇ ʇsɐן ǝɥʇ sı sıɥʇ.
"You know "that look" women get when they want sex? Me neither." --Steve Martin
Reply With Quote
  #4  
Old 14-09-2003, 03:56 AM
watana's Avatar
watana watana is offline
improving poster
 
Join Date: Jul 2001
Location: hong kong
Age: 51
Posts: 27
Rep Power: 0
watana is on a distinguished road
thank you for your assistance.

I know how to convert the velocity to air flow volume by multiply the velocity by area of grille.
__________________
vB Code is ON
Reply With Quote
  #5  
Old 12-03-2005, 05:31 PM
watana's Avatar
watana watana is offline
improving poster
 
Join Date: Jul 2001
Location: hong kong
Age: 51
Posts: 27
Rep Power: 0
watana is on a distinguished road
Re: negative pressure ward for hospital

at last, I have finally finished 2 separate jobs of negative pressure ward, some with an ante room & main bedroom.We need 10 Pa differential between ward & corridor.

My working experience is you must do a first class workmanship air duct and test the leakage of air duct, according to DW144, it is better to test the air duct with the air duct branch duct attached, seal up with plastic bags. both supply & exhaust need to be tested. Minor leakage will not maintain the differential pressure, and the sealing of the wall openig & gaps between ward need very special attention, minor leakage will not get the ideal negative pressure, also our government spend a lot of money to those wards
__________________
vB Code is ON
Reply With Quote
  #6  
Old 13-03-2005, 11:44 PM
Brian_UK's Avatar
Brian_UK Brian_UK is online now
Moderator
Site Moderator : and general nice guy
 
Join Date: Mar 2001
Location: Dorset
Age: 61
Posts: 6,318
Rep Power: 16
Brian_UK will become famous soon enoughBrian_UK will become famous soon enough
Thumbs up Re: negative pressure ward for hospital

Well done Watana, yes leak testing of the ductwork is most important when you are attempting pressure differentials across rooms.

Also, thank you for giving us an update on this thread.
__________________
Brian
PERCUSSIVE MAINTENANCE. The fine art of whacking the crap out of a piece of kit to get it to work again.
ʎɐqǝ uo pɹɐoqʎǝʞ ɐ ʎnq ı ǝɯıʇ ʇsɐן ǝɥʇ sı sıɥʇ.
"You know "that look" women get when they want sex? Me neither." --Steve Martin
Reply With Quote
Sponsored links
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
Liquid Overfeed Systems US Iceman NH3 151 08-03-2007 06:34 AM
Building a wine cabinet Rory Technical Discussions 38 13-07-2004 08:28 PM
Liquid Pressure Amplification WebRam Refrigeration Articles 7 06-06-2004 02:37 AM
TEV capacity related to pressure drop DaBit CPU Overclockers 8 06-12-2002 06:11 PM
oil pressure problems on air dryer edge Trouble Shooting 1 16-07-2002 02:10 PM


All times are GMT +1. The time now is 09:33 AM.

 

Powered by vBulletin® Version 3.7.4
Copyright ©2000 - 2009, Jelsoft Enterprises Ltd.
This forum and its pages must not be copied or reprinted without the written consent of Refrigeration Engineer.com.
This forum is a free and open discussion board.
Refrigeration-Engineer.com, the administrators and Moderators of this site are not responsible for content posted here.Ad Management by RedTyger