If it's any guidance, I encountered a similar problem from your description many, many years ago on a beer cellar in the UK that was cooled with an old York hermetic. In my experience it is comparatively rare in refrigeration systems.
The problem was intermittent, it came and went and sure enough, it never occurred when the engineer was present.
In this instance it was LOUD- about the same intensity as a car horn. I had packed up and left the job thinking another abortive visit and I could hear it in the street. When I finally tracked it down, it was the TX valve. I concluded that the seat and needle arrangement was worn sufficiently for it to vibrate and cause a constantly pitched whine, like a single note on a church organ, though it seemed to favour a particular range of pressures in the liquid line and evaporator, because it came and went and seemed to be dependent on the valve position.
You get the same effect more frequently with water valves that tend to ‘hoot’ when the valve stem is loose against the seat.
In short if it is anywhere near the evaporator, check the TXV, though the noise can tend to travel around the system.
Good luck