Question IMI Air con units

OK any of you guys worked with IMI units

Have one that indoor unit runs not showing any faults, but outdoor doesn't kick in.

Close the contactor for the compressor & it runs.

Thermostat on indoor??

Capacitors on outdoor??

Board Knackerd??

Thoughts anyone.......
Reply With Quote
  #2  
Old 17-06-2003, 08:09 AM
Mark's Avatar
Mark Mark is online now
Moderator
Site Moderator : and general nice guy
 
Join Date: Jun 2002
Location: UK
Age: 34
Posts: 572
Rep Power: 8
Mark is on a distinguished road
Wink imi air con unit

do you have a model no.it would help with fault finding .ie heatpump,impact,image e,mechanical,electronic,electromechanical
mark
Reply With Quote
Sponsored links
  #3  
Old 17-06-2003, 06:36 PM
Andy's Avatar
Andy Andy is online now
Moderator
Site Moderator : and general nice guy
 
Join Date: Jun 2001
Location: N.Ireland
Age: 36
Posts: 1,608
Rep Power: 10
Andy is on a distinguished road
Hi Stuart,
internal Klixon out on the compressor
Regards. Andy
Reply With Quote
  #4  
Old 18-06-2003, 10:28 PM
Brian_UK's Avatar
Brian_UK Brian_UK is online now
Moderator
Site Moderator : and general nice guy
 
Join Date: Mar 2001
Location: Dorset
Age: 61
Posts: 6,318
Rep Power: 16
Brian_UK will become famous soon enoughBrian_UK will become famous soon enough
Stuart, without knowing the model number we are all guessing, but....
sometimes the head pressure control pipe sensor can go down which throws up a failure.

If you have another unit nearby, try a swap.

But yes, it could well be a board down, not unknown with IMI.
__________________
Brian
PERCUSSIVE MAINTENANCE. The fine art of whacking the crap out of a piece of kit to get it to work again.
ʎɐqǝ uo pɹɐoqʎǝʞ ɐ ʎnq ı ǝɯıʇ ʇsɐן ǝɥʇ sı sıɥʇ.
"You know "that look" women get when they want sex? Me neither." --Steve Martin
Reply With Quote
  #5  
Old 18-06-2003, 11:05 PM
Karl Hofmann's Avatar
Karl Hofmann Karl Hofmann is offline
VIP Poster
 
Join Date: Jan 2003
Location: Crewe, United Kingdom
Age: 44
Posts: 710
Rep Power: 7
Karl Hofmann is on a distinguished road
Hofmanns rule of thumb:- Always start by checking for the simple faults first and work your way up to the expensive stuff but always explain to the customer that it COULD be something major and expensive, this way if it is expensive they're already primed for the bad news, if it is a simple and cheap repair then you become a hero and your name is passed on.
__________________
Karl
Reply With Quote
  #6  
Old 19-06-2003, 09:16 AM
FreezerGeezer's Avatar
FreezerGeezer FreezerGeezer is online now
Veteran Poster
 
Join Date: Aug 2001
Location: Gold Coast, Australia
Posts: 255
Rep Power: 9
FreezerGeezer is on a distinguished road
Our splits were very simple, so I don't know if this will help, but:

Check that you have a cooling signal from your thermostat to your control board (I'm assuming the main control board is on the indoor unit).
If that is okay, and you're getting a signal for cooling back to the main board, then check that there is a signal out from the control board to the condenser. Ours send a 24V feed to the condenser, to activate the compressor contactor, and the condenser fan.
If there is no signal, then either:
The relay is knackered - replace the board.
There is a condensate overflow safety, or the condensate pump is wired in series with the compressor feed, and has failed. Either of which will stop a signal reaching the condenser.
If there is a signal out, then (on our units) it would have to be the H.P. or L.P. switch holding it off, since you say that the compressor will run if you hold in the contactor.

No doubt you've already done all this, and it's something more complicated. Sorry if I'm teaching anyone to suck eggs.

Karl, I like that philosophy!
Reply With Quote
  #7  
Old 19-06-2003, 10:18 AM
FreezerGeezer's Avatar
FreezerGeezer FreezerGeezer is online now
Veteran Poster
 
Join Date: Aug 2001
Location: Gold Coast, Australia
Posts: 255
Rep Power: 9
FreezerGeezer is on a distinguished road
Our splits were very simple, so I don't know if this will help, but:

Check that you have a cooling signal from your thermostat to your control board (I'm assuming the main control board is on the indoor unit).
If that is okay, and you're getting a signal for cooling back to the main board, then check that there is a signal out from the control board to the condenser. Ours send a 24V feed to the condenser, to activate the compressor contactor, and the condenser fan.
If there is no signal, then either:
The relay is knackered - replace the board.
There is a condensate overflow safety, or the condensate pump is wired in series with the compressor feed, and has failed. Either of which will stop a signal reaching the condenser.
If there is a signal out, then (on our units) it would have to be the H.P. or L.P. switch holding it off, since you say that the compressor will run if you hold in the contactor.

No doubt you've already done all this, and it's something more complicated. Sorry if I'm teaching anyone to suck eggs.

Karl, I like that philosophy!
Reply With Quote
  #8  
Old 22-06-2003, 01:28 PM
Stuart's Avatar
Stuart Stuart is offline
regular poster
 
Join Date: Mar 2002
Location: Sydney Australia :D
Age: 39
Posts: 47
Rep Power: 0
Stuart is on a distinguished road
All comments gratefully received

Freezer yes have tried your suggestions & I too think its a relay or thermostat prob.

For all you Techies out there.

Outdoor unit: HPUE100 3ph
Indoor unit: Image 120E (Twin Fan)

Brian- yes board change needed on outdoor I feel.
__________________
:cool: [COLOR=Red]Do the job once & do it right.[/COLOR] :cool:
Reply With Quote
Sponsored links
  #9  
Old 26-06-2003, 09:56 PM
BritCit_Juve's Avatar
BritCit_Juve BritCit_Juve is offline
regular poster
 
Join Date: Dec 2001
Location: UK
Posts: 136
Rep Power: 8
BritCit_Juve is on a distinguished road
If the unit is an Image E model then the indicator lams woul usually indicate the fault and the sounder would go.

first off though check termina 5 in the HPUE. if you have 240V there is a fault on the outdoor unit.
If you dont have any voltage then check the unit fuse. You should see around 70V normally.

On the indoor unit is the green led on? if not the unit doesn't want cooling so try resending the Cooling only signal or raise the temperature one degree. In both cases you should get a single bleep. If you get a double bleep then it doesnt like the command.

If you send a signal and get the sounder going around 16 times then you have an alarm such as
green led flash high condensate or pump fuse blown
Amber LED network fault
All three LEDs on Sensor fault indoor or outdoor
if outdoor terminal 5 would also be 240V

The E models work on a 2 wire data cable and if the outdoor unit is a heat pump both legs need to be good. If you have a green and red LED showing and 240 on terminal unit then the fault may be on the data cables. There are two ways to check em.
1 Force a fault. Remove one of the sensors off the liquid line sensor or
2 use an LED across the two data wires they should flash once every 3 seconds out and the return flash is a second later.

Note that if a unit attached to a heatpump HPUE/DHPUE/MHPUE unit will work in cooling but wont accept the heating command then the data cable is not connected correctly.
On the handset the transmission takes a finite time and it is possible for the display to over run ie display showes 16C but transmission still at 24C. just try raising the temperature to retansmit the present setting.


Lots of ramble but might help. let us know.

Never change an IMI PCB if you dont have to, unless your names Rockafella or beckham

Brit
Reply With Quote
  #10  
Old 01-07-2003, 05:38 PM
Stuart's Avatar
Stuart Stuart is offline
regular poster
 
Join Date: Mar 2002
Location: Sydney Australia :D
Age: 39
Posts: 47
Rep Power: 0
Stuart is on a distinguished road
Thanks Britcit did most of what you said already.

Just so you all know pcb was blown...Hot & discoloured in one or two areas.

No faults shown on the indoor Brit it just ran but showed no faults. But yes it was an Image E
__________________
:cool: [COLOR=Red]Do the job once & do it right.[/COLOR] :cool:
Reply With Quote
  #11  
Old 02-07-2003, 10:34 PM
Brian_UK's Avatar
Brian_UK Brian_UK is online now
Moderator
Site Moderator : and general nice guy
 
Join Date: Mar 2001
Location: Dorset
Age: 61
Posts: 6,318
Rep Power: 16
Brian_UK will become famous soon enoughBrian_UK will become famous soon enough
Glad that you have sorted it Stuart, it all sounds like pretty standard IMI stuff.

I used to get wiring faults on the contactors which I put down to that *Friday manufacture* syndrome, they just didn't crimp the terminals properly and then they would overheat and burn-out.
__________________
Brian
PERCUSSIVE MAINTENANCE. The fine art of whacking the crap out of a piece of kit to get it to work again.
ʎɐqǝ uo pɹɐoqʎǝʞ ɐ ʎnq ı ǝɯıʇ ʇsɐן ǝɥʇ sı sıɥʇ.
"You know "that look" women get when they want sex? Me neither." --Steve Martin
Reply With Quote
Sponsored links
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
What units you'll see in your country? nova Transport 17 30-08-2009 09:39 PM
Mitsibishi VRV System 8 out of 10 units work moondawn Air Conditioning 5 29-09-2005 11:02 PM
Highcool split air con units iceman007 Air Conditioning 10 31-05-2005 12:31 PM
AC units as cooling units Peter_1 Commercial 11 18-03-2005 07:42 AM
Sizeing condensing units Latte Commercial 4 25-11-2004 10:26 PM


All times are GMT +1. The time now is 10:10 AM.

 

Powered by vBulletin® Version 3.7.4
Copyright ©2000 - 2009, Jelsoft Enterprises Ltd.
This forum and its pages must not be copied or reprinted without the written consent of Refrigeration Engineer.com.
This forum is a free and open discussion board.
Refrigeration-Engineer.com, the administrators and Moderators of this site are not responsible for content posted here.Ad Management by RedTyger