Single pole contactor & crankcase heater

Helping out a friend (by GOD, if I'm working on your air conditioner - you're a good friend), I pondered the use of the single pole contactor (with the common bar on the other line). I just learned that the purpose of that congiguration is to complete the circuit through the crankcase heater which is wired across the (open) contact of the contactor, and "disable" the crankcase heater when the contacts are closed.

What amount of heat gain (or increased load) do you anticipate with the crankcase heater energized during compressor operation, in such a case as a two pole contactor be applied, and the heater connected to the line side of the contactor (always energized). ooops!
Reply With Quote
  #2  
Old 10-05-2003, 08:49 PM
frank's Avatar
frank frank is online now
Moderator
Site Moderator : and general nice guy
 
Join Date: Oct 2001
Location: Nottingham UK
Age: 57
Posts: 3,314
Rep Power: 12
frank is on a distinguished road
Crankcase heaters are normally around 40 to 60 watts so not much of a heat gain.

We had a compressor go down a couple of months ago and reported it under warranty. The manufacturer admitted that it was a design fault as the crankcase heater was under sized and allowed the oil to be carried out of the crankcase which causing the failure. Seems like you have to be careful with these things.
Reply With Quote
Sponsored links
  #3  
Old 10-05-2003, 09:18 PM
Gary's Avatar
Gary Gary is online now
VIP Poster
 
Join Date: Apr 2001
Location: New Port Richey, Florida - USA
Age: 64
Posts: 3,525
Rep Power: 12
Gary will become famous soon enough
Quote:
We had a compressor go down a couple of months ago and reported it under warranty. The manufacturer admitted that it was a design fault as the crankcase heater was under sized and allowed the oil to be carried out of the crankcase which causing the failure. Seems like you have to be careful with these things.
I'm betting the coil was above the compressor and/or the unit was started in cool weather.
__________________
Author of TECH Method troubleshooting books
Reply With Quote
  #4  
Old 11-05-2003, 10:54 AM
frank's Avatar
frank frank is online now
Moderator
Site Moderator : and general nice guy
 
Join Date: Oct 2001
Location: Nottingham UK
Age: 57
Posts: 3,314
Rep Power: 12
frank is on a distinguished road
It was a "plug" type heater Gary which fits into a small aperture in the base of the compressor. The unit in question was a Daikin VRV Plus system which comprises of 3 outdoor condensing units (6 compressors).

This link will show more http://global.daikin.com/global/our_...rv/p_vrv.html.

The system is a 24hp unit, 3 pipe heat recovery with one inverter driven compressor and 5 on/off units. The unit that failed was compressor No. 6 - the last to be called so you can see that it stood there for most of the time at rest just collecting liquid.

Apparently, upgrading to a 60W heater from a 40W heater has done the trick.

Last edited by frank; 11-05-2003 at 08:06 PM..
Reply With Quote
  #5  
Old 31-03-2009, 02:03 PM
Sridhar1312's Avatar
Sridhar1312 Sridhar1312 is offline
regular poster
 
Join Date: Jan 2008
Location: India
Age: 55
Posts: 131
Rep Power: 2
Sridhar1312 is on a distinguished road
Re: Single pole contactor & crankcase heater

Some of the scroll compressors I have seen are without crank case heaters can any one tell me Why?
Reply With Quote
  #6  
Old 31-03-2009, 11:46 PM
monkey spanners's Avatar
monkey spanners monkey spanners is online now
VIP Poster
 
Join Date: Aug 2006
Location: england
Age: 35
Posts: 967
Rep Power: 4
monkey spanners is on a distinguished road
Re: Single pole contactor & crankcase heater

Some systems pass a small current through the motor windings when the compressor is off, just enough to keep it warm, so don't need a crankcase heater, some are on pumpdown, and some should have one fitted and don't....
Reply With Quote
  #7  
Old 01-04-2009, 08:37 AM
NoNickName's Avatar
NoNickName NoNickName is online now
VIP Poster
 
Join Date: Mar 2006
Location: Merate (LC) - Italy
Age: 38
Posts: 1,455
Rep Power: 5
NoNickName is on a distinguished road
Re: Single pole contactor & crankcase heater

Crankcase heaters are to be considered as "COMPULSORY" . Monkey spanners: I don't know where you heard about that story of current leakage, but it makes me smile, also because motors are not in the oil, and it's not the motor who has got to be warm, but the oil is!
Additionally, heaters can burn when kept ON while compressor is operating, because heaters could be overheated and burn out. That's why they always have to be interfaced with a NC contact of the compressor contactor.
Reply With Quote
  #8  
Old 01-04-2009, 08:38 AM
NoNickName's Avatar
NoNickName NoNickName is online now
VIP Poster
 
Join Date: Mar 2006
Location: Merate (LC) - Italy
Age: 38
Posts: 1,455
Rep Power: 5
NoNickName is on a distinguished road
Re: Single pole contactor & crankcase heater

Quote:
Originally Posted by Sridhar1312 View Post
Some of the scroll compressors I have seen are without crank case heaters can any one tell me Why?
Because the installer forgot to buy the heater or just wanted to speculate for few bucks.
Reply With Quote
Sponsored links
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump


All times are GMT +1. The time now is 01:42 PM.

 

Powered by vBulletin® Version 3.7.4
Copyright ©2000 - 2009, Jelsoft Enterprises Ltd.
This forum and its pages must not be copied or reprinted without the written consent of Refrigeration Engineer.com.
This forum is a free and open discussion board.
Refrigeration-Engineer.com, the administrators and Moderators of this site are not responsible for content posted here.Ad Management by RedTyger