Frank is absolutely right. From the fact that you have 2 coils, I deduce that it is a cassette. This an old unit, since Tosh stopped making R22 kit some years ago in favour of HFC's.
The problem, if it recurs intermitently, is probably caused by overcondensing - ie the unit operates at low ambient temperatures in cooling.
The 09 code signifies a period of time where the coil sensor (TC) does not sense a change in temperature. Once the coil picks up frost, the problem persists.
Very often this fault is caused by over condensing, especiallly at the pressures you mention (50 psi, which will give an evaporating temperature on R22 about - 3 or 4. The TC sensor goes into fault mode below -2, ( if my memory serves me correctly). The ambient temperature rarely goes above 25 deg in the summer, in the UK, never mind in May!
Check that you have an adequate form of condenser fan speed controller, as a low internal loads at intermediate seasons and low outside ambient can give these symptoms.
Tosh incorporated a fan speed control in the outdoor unit from about the mid 90's. A 460 may be prior to that.
You can check the sensors very easily by looking at their centre value, which is 10k ohm at 25 deg - as the temperature goes up, the resistance falls, but it is not linear. Tosh should be able to provide a temp / resistance gradient.
|