toshiba rav 460 indoor coil freezing up

i am having problems with a tosh rav460.The customer reported poor performance in cooling mode.On arrival i found one side of the coil completely iced up blocking air flow the check codes where showing 01 08 and 01 09.The suction valve on the outdoor unit and 3/4 of the compressor was also iced up as there was no air flow through the indoor coil and liquid was making its way back to the compressor.I removed the drain bung turned the unit over to heating to clear the ice and drain away the water. I set the unit back to cooling at 21 deg C and watched the unit cycle on and off normally about six times.I also checked that the TA probe was cutting off the compressor by dipping it in ice water and cutting back in by holding it in my hand it ran ok.I also checked that the drain and pump was functioning normally. I recovered all the refrigerant (R22) and recharged it to the factory spec of 3.8 kg so i do not think it is a gas shortage or overcharge problem the pressures were 230psi / 50psi the ambient about 25 deg c. 2 days later it has come back in same fault could this be a intermitant fault on the indoor pcb. sugestions gladly received. thankyou.
Reply With Quote
  #2  
Old 07-05-2003, 07:58 PM
frank's Avatar
frank frank is online now
Moderator
Site Moderator : and general nice guy
 
Join Date: Oct 2001
Location: Nottingham UK
Age: 57
Posts: 3,314
Rep Power: 12
frank is on a distinguished road
Check that the controller has not been put into "test" which will override the stat and give the symtoms you describe. Just found exactly the samre problem with a Tosh wall unit. This only applies to the pencil type controller.

Frank
Reply With Quote
Sponsored links
  #3  
Old 08-05-2003, 01:13 AM
herefishy's Avatar
herefishy herefishy is offline
VIP Poster
 
Join Date: Jan 2002
Location: Austin, Texas
Posts: 718
Rep Power: 8
herefishy is on a distinguished road
50psi? .... 26degF S.S.T.? Is this an air conditioner... not familiar with Tosh R460....
Reply With Quote
  #4  
Old 08-05-2003, 07:47 PM
frank's Avatar
frank frank is online now
Moderator
Site Moderator : and general nice guy
 
Join Date: Oct 2001
Location: Nottingham UK
Age: 57
Posts: 3,314
Rep Power: 12
frank is on a distinguished road
fridgefixer

The first part of the fault code refers to the number of starts the compressors has requested based on the hexidecimal format. The second part, i.e. 08 or 09 refers to the fault.

08 refers to the "reverse change temp" - you need to check the operation of the 4 way valve or the TC senser (Coil sensor)

09 refers to 2 different things

1 - No change in the indoor unit temps - compressor not pumping/klixon tripped/crossed wiring

2 - Frost condition - Gas Charge/Pipe blockage/Indoor air flow/TC sensor/cross wiring

Looking at this problem from a distance I would suggest that the TC (coil sensor) is at fault

Frank
Reply With Quote
  #5  
Old 10-05-2003, 11:30 PM
Argus's Avatar
Argus Argus is online now
Moderator
Site Moderator : and general nice guy
 
Join Date: Aug 2001
Location: UK
Posts: 1,044
Rep Power: 10
Argus is on a distinguished road
Frank is absolutely right. From the fact that you have 2 coils, I deduce that it is a cassette. This an old unit, since Tosh stopped making R22 kit some years ago in favour of HFC's.

The problem, if it recurs intermitently, is probably caused by overcondensing - ie the unit operates at low ambient temperatures in cooling.

The 09 code signifies a period of time where the coil sensor (TC) does not sense a change in temperature. Once the coil picks up frost, the problem persists.

Very often this fault is caused by over condensing, especiallly at the pressures you mention (50 psi, which will give an evaporating temperature on R22 about - 3 or 4. The TC sensor goes into fault mode below -2, ( if my memory serves me correctly). The ambient temperature rarely goes above 25 deg in the summer, in the UK, never mind in May!

Check that you have an adequate form of condenser fan speed controller, as a low internal loads at intermediate seasons and low outside ambient can give these symptoms.

Tosh incorporated a fan speed control in the outdoor unit from about the mid 90's. A 460 may be prior to that.

You can check the sensors very easily by looking at their centre value, which is 10k ohm at 25 deg - as the temperature goes up, the resistance falls, but it is not linear. Tosh should be able to provide a temp / resistance gradient.
Reply With Quote
Sponsored links
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
Quick freezing of fresh products maxim971 Technical Speculations 12 18-09-2009 11:06 PM
Toshiba Digital Inverter range? Slim R410a Air Conditioning 14 24-04-2007 08:01 PM
Freezing problem MajinDave Trouble Shooting 10 15-07-2006 12:01 AM
Looking for air temp sensors for Toshiba GR334 fridge (have part number) Cluster Domestic 1 19-02-2006 01:08 AM


All times are GMT +1. The time now is 02:23 AM.

 

Powered by vBulletin® Version 3.7.4
Copyright ©2000 - 2009, Jelsoft Enterprises Ltd.
This forum and its pages must not be copied or reprinted without the written consent of Refrigeration Engineer.com.
This forum is a free and open discussion board.
Refrigeration-Engineer.com, the administrators and Moderators of this site are not responsible for content posted here.Ad Management by RedTyger