Question Mcquay water source heat pump

I have very little experience trouble shooting refrigerant flow problems on heat pumps. So let me give you guys a crack at it.
After evacuating and recharging unit, start up unit(10 min run time):
suction press:65#
head press 248#
suc temp @ inlet of water heat exchanger 46F
suc temp @ outlet of water heat exchanger 75F
suc temp @ comp ahead of reversing valve 77F
discharge line temp ahead of reversing valve 175F
discharge line temp downsteam of rev valve 175F
water temp inlet 80F
water temp outlet 75F
Seems to me suction superheat is high, discharge air temp is 90F, also seems low.
Return air @ 65-70" (*store is in very negative pressure).
This is the 2nd stage compressor in a 2 stage unit.
1st stage is inoperable, blockage in refrigerant circuit.
Got 2nd stage going to provide some heat to space and
will have to return to repair first stage.
Thanks
Bernie
M# HWH-CCH120CMFS
S# 7 7L0809110
Reply With Quote
  #2  
Old 28-01-2003, 09:36 PM
Brian_UK's Avatar
Brian_UK Brian_UK is online now
Moderator
Site Moderator : and general nice guy
 
Join Date: Mar 2001
Location: Dorset
Age: 62
Posts: 7,502
Rep Power: 19
Brian_UK has a spectacular aura aboutBrian_UK has a spectacular aura aboutBrian_UK has a spectacular aura about
Without getting into your figures too deeply to start with My first thoughts are that the air temperature may not be too bad; bear in mind that if it is a 2 stage unit then performance will drop off with only one stage running.

I always try and charge and check superheat in the cooling mode although I appreciate that may be difficult at this time of year.

With smaller heat pumps I have often found the superheat at the compressor inlet somewhat higher than I would like but when in cooling things get back to normal.

Sounds like you've had, and are having, fun on this one
__________________
Brian
PERCUSSIVE MAINTENANCE. The fine art of whacking the crap out of a piece of kit to get it to work again.
You should always give 100% at work...
12% Monday; 23% Tuesday; 40% Wednesday; 20% Thursday; 5% Friday
Reply With Quote
Sponsored links
  #3  
Old 10-02-2003, 02:53 AM
bernie's Avatar
bernie bernie is offline
regular poster
 
Join Date: Jun 2001
Location: Chicago Il
Age: 39
Posts: 90
Rep Power: 10
bernie is on a distinguished road
Thats where I went wrong. I tried to adjust charge and superheat during heat mode.
When I returned to the site the other day, I turned the stat to cool and dialed the charge in.
As long as the cooling superheat is in order, I dont really care
about the heat mode superheat.
Its blowing warm, I'm off to the next adventure.
Thanks
Bernie
Reply With Quote
Sponsored links
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
frostles heat pump Lc_shi New Technologies 27 31-03-2008 07:53 AM
Evaporator Design-Air Source Heat Pump for water heating anup Technical Discussions 7 20-03-2006 03:26 PM
water source heat pump Lc_shi New Technologies 12 29-03-2005 09:09 PM
Building a wine cabinet Rory Technical Discussions 38 13-07-2004 08:28 PM
Water Source Heat Pump aliugur Fundamentals 1 02-06-2002 03:24 PM


All times are GMT +1. The time now is 04:38 AM.

 

Powered by vBulletin® Version 3.7.4
Copyright ©2000 - 2010, Jelsoft Enterprises Ltd.
This forum and its pages must not be copied or reprinted without the written consent of Refrigeration Engineer.com.
This forum is a free and open discussion board.
Refrigeration-Engineer.com, the administrators and Moderators of this site are not responsible for content posted here.Ad Management by RedTyger