30-09-2009, 03:54 AM #1
Re: Dropped in it and trying t get it sorted
G'Day,
Yes I have gauges but not exactly sure where to connect them. The chiller plate gets about 90% frosted over before shutting down. The liquid in that one is distilled water. I spoke to the freezer man and he says he put 2.5 meters of the 0.026 in that one. Sounds a bit long to me from what the discussion has been here for the freezers.
-
30-09-2009, 04:55 AM #2
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Dropped in it and trying t get it sorted
It is not same thing as with freezers. You have diferent capacity at higher temperature (90 w) and you need less superheat. 0,026 of 2.5 lenght is too much restriction.
I would change that capillary back to 0.031 of 1.6m length if compressor is same model as with freezers.
What was length of old capillary?