    how to remove air from R22 refrigeration system



    Who know the practical way of removing air from R22 system? Now I recycle the refrigrant and recharge it. I think it's not effecient.

    thanks

    LC


    I hear...I forget;I see...I remember;I do...I understand

  2. #2
    Join Date
    Jul 2011
    Location
    usa
    Posts
    29
    Rep Power
    0

    Re: how to remove air from R22 refrigeration system

    Can't you recover to a tank, check the r22 temperature pressure chart for non-condensables, let the tank sit for a few days and you can bleed the air off the top.

    It's not a quick answer though, and not really practical in the field.

  3. #3
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: how to remove air from R22 refrigeration system

    Lc, if air has entered the system, then the LP safety cut-out was not set correct.
    Of how many weight of refrigerant we're speaking?
    The methods for incondensable removal varies with the weight.
    Method used in NH3 system: cool down the liquid to -33°C and open a valve on the cooled receiver. All what escapes is air.
    For R22, cool it down to -41°C.

    How we remove it?
    Empty recovery bottle = 20 kg
    We recover all the refrigerant, let's say 60 kg total (20 kg bottle + 40 kg R22)
    Vacuum the system
    Refill in only-liquid state 39 kg and the remaining is all the air and 1 kg of R22.

    @clearchris: your method isn't allowed - theoretically - in the EU.
    Last edited by Peter_1; 26-07-2011 at 09:26 PM.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  4. #4
    Join Date
    Jul 2011
    Location
    usa
    Posts
    29
    Rep Power
    0

    Re: how to remove air from R22 refrigeration system

    Regarding the first method, that won't bleed off *all* the non-condensables, will it? There is still a volume of air space in the tank, at least 20% over here.

  5. #5
    mofrobaggins's Avatar
    mofrobaggins Guest

    Re: how to remove air from R22 refrigeration system

    the best way to remove air is to reclaim all the gas in the system and take to an authorized handler to dispose of it (because u suspect it for contamination) for you and then to start again put on vac pull it down to 200 microns and recharge with r 22 but whoever what is the system used for and and running pressures etc for all u know u may even have an inefficient compressor

  6. #6
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: how to remove air from R22 refrigeration system

    Mofrobaggins, expensive for your customer if you remove all the refrigerant. We use the method sometimes in supermarkets. Air can't contaminate a refrigerant, it only can remain as an incondensable on the top of it.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  7. #7
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: how to remove air from R22 refrigeration system

    Quote Originally Posted by Peter_1 View Post
    Lc, if air has entered the system, then the LP safety cut-out was not set correct.
    Of how many weight of refrigerant we're speaking?
    The methods for incondensable removal varies with the weight.
    Method used in NH3 system: cool down the liquid to -33°C and open a valve on the cooled receiver. All what escapes is air.
    For R22, cool it down to -41°C.

    How we remove it?
    Empty recovery bottle = 20 kg
    We recover all the refrigerant, let's say 60 kg total (20 kg bottle + 40 kg R22)
    Vacuum the system
    Refill in only-liquid state 39 kg and the remaining is all the air and 1 kg of R22.

    @clearchris: your method isn't allowed - theoretically - in the EU.
    Useful tip their Peter.
    Grizzly

  8. #8
    Join Date
    Nov 2009
    Location
    Minsk, Belarus
    Age
    39
    Posts
    171
    Rep Power
    15

    Re: how to remove air from R22 refrigeration system

    In such cases we unify two bottles: one empty, one with refrigerant and air. Bottle with refrigerant and air remove on warm place, empty bottle leave on cold room (-18 C for example). After 24 hours refrigerant migrate from warm bottle to cold empty bottle, air and refrigerant in gas phase would be in warm bottle.
    In some places will have to think ...

  9. #9
    Join Date
    May 2009
    Location
    manchester
    Age
    54
    Posts
    14
    Rep Power
    0

    Re: how to remove air from R22 refrigeration system

    in my understanding without all the bumf and cost is reclame of top of condenser or discharge if no nrv, air usally sits on top of condenser and this can be found with cool condenser at top and hot twords bottom

  10. #10
    gman082's Avatar
    gman082 Guest

    Re: how to remove air from R22 refrigeration system

    Quote Originally Posted by Lc_shi View Post
    Who know the practical way of removing air from R22 system? Now I recycle the refrigrant and recharge it. I think it's not effecient.

    thanks
    LC
    Hi LC,
    you're right, it's un-economical to keep reclaiming and recharging refrigerant, for you and your client.
    As I understand, if there's air getting into your clients sealed refrigeration system, I'd say start looking for a leak.

    @clearchris: Neither can I recomend this practise, our job should be to minimalise refrigerant expelled to the ozone.

    Quote Originally Posted by Peter_1 View Post
    ... Air can't contaminate a refrigerant, it only can remain as an incondensable on the top of it.
    @Peter_1: True, air is made up of lots different parts, that may remain uncondensible and un-noticed, but the moisture carried in the air can affect the hydroscopic oils and cause problems.

    Hope this helps!

    -Gr.

  11. #11
    Join Date
    Dec 2009
    Location
    Spain
    Age
    45
    Posts
    235
    Rep Power
    15

    Re: how to remove air from R22 refrigeration system

    Quote Originally Posted by gman082 View Post
    @Peter_1: True, air is made up of lots different parts, that may remain uncondensible and un-noticed, but the moisture carried in the air can affect the hydroscopic oils and cause problems.

    Hope this helps!

    -Gr.
    Normally R22 uses MO which is less hygroscopic than POE. Anyway, once you have removed the uncondensables, as Peter_1 smartly suggested, you can then recycle the gas, and remove oils and moisture.

    Regards,

    Nando.

  12. #12
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    52
    Posts
    2,554
    Rep Power
    24

    Re: how to remove air from R22 refrigeration system

    Quote Originally Posted by Peter_1 View Post
    Lc, if air has entered the system, then the LP safety cut-out was not set correct.
    And this reminds me about the deprecated habit of german supermarkets (BILLA, REWE) especially with TEKO equipment to use R134a in freezer cabinets. Only because R134a has a lower TEWI than R404a.

  13. #13
    gman082's Avatar
    gman082 Guest

    Re: how to remove air from R22 refrigeration system

    I almost forgot, (credit where credit's due, they say)... I agree with Mofobaggins (post #5), contamination is the word on the street kids. I'd suggest a dry nitro pressure test too, just to be sure I got the leak.

    Quote Originally Posted by Peter_1 View Post
    Mofrobaggins, expensive for your customer if you remove all the refrigerant.
    It maybe an expensive exercise, but I find clients warm to the idea of having a fresh, clean charge of refrigerant with a guarantee.


    Quote Originally Posted by Fri3Oil System View Post
    Normally R22 uses MO which is less hygroscopic than POE. Anyway, once you have removed the uncondensables, as Peter_1 smartly suggested, you can then recycle the gas, and remove oils and moisture.

    Regards,

    Nando.
    Hi Nando,
    now I not arguing with you, I'm whole-heartedly agreeing instead; You say less hydroscopic, very true, but is still hydroscopic all the same. Furthermore, your acid test kit will only tell you acid is present in the oil, not the quantity.

  14. #14
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: how to remove air from R22 refrigeration system

    Gman082, if you recover the liquid without the 'gas-mixture' above the liquid through a burnout filter - in case you suspect acid in it - then you will have pure R22. Sometimes more pure then the R22 in new bottles because they don't clean each bottle when it's coming back in the refilling stations.
    We've done it so many times with 100% good results that nobody can convince me from the opposite.
    Then, what's better for the environment, me reclaiming it or your giving it back to destroy?
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  15. #15
    gman082's Avatar
    gman082 Guest

    Re: how to remove air from R22 refrigeration system

    Quote Originally Posted by Peter_1 View Post
    Gman082, if you recover the liquid without the 'gas-mixture' above the liquid through a burnout filter - in case you suspect acid in it - then you will have pure R22. Sometimes more pure then the R22 in new bottles because they don't clean each bottle when it's coming back in the refilling stations.
    We've done it so many times with 100% good results that nobody can convince me from the opposite.
    Then, what's better for the environment, me reclaiming it or your giving it back to destroy?

    Peter,
    I understand your reasoning, thanks.
    I have one last question if you'd be kind; When your recovering liquid from a unit that has a suspected leak and an unknown refrigerant charge, how do you know how much refrigerant to take out, so you avoid recovering any vapour?

    -Gr.

  16. #16
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: how to remove air from R22 refrigeration system

    Quote Originally Posted by Peter_1 View Post
    How we remove it?
    Empty recovery bottle = 20 kg
    We recover all the refrigerant, let's say 60 kg total (20 kg bottle + 40 kg R22)
    Vacuum the system
    Refill in only-liquid state 39 kg and the remaining is all the air and 1 kg of R22.
    I have to add to my 3th post, we recover everything, liquid, gas and also the non-condensables.
    We then recover only +/-95% from the recovered 'mixture' - in liquid phase - and let the remaining liquid with the gas and the non-condensables still on top of this mixture in the recovery bottle.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  17. #17
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    52
    Posts
    2,554
    Rep Power
    24

    Re: how to remove air from R22 refrigeration system

    Just a thought: if one recovers refrigerant and installs a liquid receiver, through-type, in between the condensing unit and the bottle, incondensables should float in the receiver? Is there a risk of exceeding the safety pressure?

  18. #18
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: how to remove air from R22 refrigeration system

    When you start, when there's no liquid yet in the, non-condensables will flow through it.
    If you have vacuumed a cylinder where the recovered R22 will flow to, then even with a liquid seal in the receiver, the liquid will flow so fast to the bottle that it will empty.
    High pressure NNN: in many occasions, we see that our recovery station, cutting out at 26 bar actually cuts out on it's safety pressure. We end up many times with cylinders R40c or R404a at 25 bar when we come back the next morning.
    We therefore installed a safety HP between the mains of our recovery station, cutting out at 23 bar.
    And...also a LP cut out just above atmospheric pressure.
    Most recovery go to 500 mbar absolute or lower (=vacuum)
    EN378 states that you have to recover till 300 mbar absolute before opening the system. Typically, a rule invented by peoples not working in the field with their hands but only behind their desks.
    Why? If you have a leak in the system - often the reason for a recovery - your recovery unit will continue to recover through the leak, sucking in air resulting in an increase of pressure of the recovery cylinder.
    Therefore, the 300 mbara rule is for me not a good rule.
    Last edited by Peter_1; 09-10-2011 at 01:05 PM.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  19. #19
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: how to remove air from R22 refrigeration system

    But we use a vertical receiver if we need to charge a lot of oil in a compressor/system.
    Filling up the receiver via a funnel via the rotalock, 4 l at once. Screwing back the rotalock, vacuum out the air via the intake service connection. Pressurize then the receiver with HP refrigerant when system is already running or with the gas from a cylinder if system is at vacuum and pushing out the oil via the receiver outlet. We fill in this way 20 l in +/- 20 minutes.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  20. #20
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: how to remove air from R22 refrigeration system

    I am used to work whit two filter/dryers on my recovery station. one when i am recovering and a other one when i am refilling the unit. That way i am always sure to have clean refrig in mi installations.
    The cost of the filters is negligible to the cost of say 25 kg of refrig.

    One rule of thumb do, never take so much refrig out of the bottle so the station go's in vacuum.
    Ice

  21. #21
    Join Date
    Dec 2009
    Location
    Spain
    Age
    45
    Posts
    235
    Rep Power
    15

    Re: how to remove air from R22 refrigeration system

    Quote Originally Posted by gman082 View Post
    Hi Nando,
    now I not arguing with you, I'm whole-heartedly agreeing instead; You say less hydroscopic, very true, but is still hydroscopic all the same. Furthermore, your acid test kit will only tell you acid is present in the oil, not the quantity.
    My acid test? Which acid test?

  22. #22
    Join Date
    Nov 2003
    Location
    holland europe
    Age
    65
    Posts
    78
    Rep Power
    21

    Re: how to remove air from R22 refrigeration system

    **** all illegal answers!!
    the only way in a running installation is to use a purger on the receiver or condenser.
    It cools the gas very low so all R22 will condense and flow back.
    the air will be purged by a very small hole.
    look for grasso purger.
    you can use it on many systems as the only connection is one pipe.
    and when it runs for a month all air will be out.

    all other methods are illegal.
    computer shooter
    paul deelen
    +31653300739