    Re: Case of Chocolate biscuits to whoever can help me!!

    @joe-ice
    Signatures in our posts does not have anything with actual posts. It represent our global attitude. I am sure that Peter_1 as teacher (and moderator here ), has some good reasoning for showing that statement as his signature.


    To the subect:

    Circuit 1

    Te=-5,6°C (air in 16,9°C air out 14,6°C)
    Tc=46,5°C (air in 36°C air oit 43,3°C)
    Tsh=14,2K
    Evaporator:
    TD=22,5K
    dt=2,3K (not much heat collected)
    Approach=20,2K (starving)

    Condenser:
    TD=10,5K
    dt=7,3K
    Approach=3,2K (not much heat to reject)

    Circuit 2

    Te=-10,5°C (air in 11,1°C air out 6,9°C)
    Tc=54,8°C (air in 27,2°C air out 39,3°C)
    Tsh=14,9K
    Evaporator:
    TD=21,5K
    dt=4,2K
    Approach=17,3K

    Condenser:
    TD=27,6K
    dt=12,1K
    Approach=15,5 K

    Approach of condenser in circuit 2 is too high (15,5K) and approach of evaporator is also to high (17,3K).

    Something is probably wrong with that refrigerant inside that unit, or vacuum is not sufficient (or not done at all) prior to refrigerant charging and possible noncondensables are occupying condenser volume or unit is heavily overcharged (my bet is here) with filter dryer dirty or some other obstruction in liquid line region.


    Superheat in both circuits is similar (around 15K), but without knowing for real subcooling before TXV, I cannot make any further judgment.

    Condenser issues in both circuits should be examined before further evaluation.

    Based on given numbers, to me, circuit 1 is working with better numbers but with starving evaporator and recirculating condenser air than circuit 2 with less starving evaporator but with condenser which cannot reject heat efficiently.

    Also, as compressor is R404A model, possibly is that TXV is also R404A model and somebody has decided just to switch refrigerant without changing TXV. We need to clarify that also.

    Is this new equipment just installed or used one from some other project and someone has decided to use it with R134a instead of R404A?

    We need more background of these units since:
    The average heat transfer coefficient of R404A is estimated to be 26 to 30% higher than that of R134a for the same saturation temperature.
    http://www.tandfonline.com/doi/abs/1...0#.Ug81iIKHqxQ

    If equipment is designed to work with R404A, than with use of R134A instead of it, you have 30% less capacity then designed, just by using wrong refrigerant. Therefore, you should provide here all equipment specifications and data to troubleshoot that.
    Last edited by nike123; 17-08-2013 at 09:46 AM.

  3. #3
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Case of Chocolate biscuits to whoever can help me!!

    but joe have u seen some of the posts on here! haha
    thats why newbies always start off- hello im new please be gentle-!!!!!

    apart from the pricks floggin mobiles/ipads!
    go to your settings and u can create a signature-

    Quote Originally Posted by joe-ice View Post
    How is that ? On a sidenote peter 1 you posted a very short wording so i ended up reading the crap you wrote after it instead . Why do you feel the need to have a funny statement after your name .?. If i was first time posting on this site i would find it most offensive .

  4. #4
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Case of Chocolate biscuits to whoever can help me!!

    1st thing to clarify- can u define "a case of biscuits"- ie dimensions,weight, ratio of air/biccy- as we've all opened a bag of crisps for the scented air that escapes leavin a few crisps in an oversized bag!
    also a data sheet,nutritional values only state per 100grm- in this case im guessing over 2kg- typical weight of them red boxes of biccys everyone gets at christmas and doesnt eat!

    ps im allergic to every biccy except jaffa cakes,choc chip,hazelnut cookies,jammy dodgers!

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •