    Re: Refrigeration 101

    I first check the delta-T's to confirm adequate airflow through both coils.

    Then I check for high subcooling.

    Then I check for low superheat.

    Then I check for low subcooling.

    Then I check the condenser TD to see if the high side is rejecting a heavy heat load.

    If the high side is rejecting a heavy load, then the low side must be absorbing a heavy load.

    Adjusting a TXV aka TEV is almost always a mistake, especially when the refrigerated space is above design temp.
    Last edited by Gary; 05-07-2009 at 06:34 PM.