05-07-2009, 06:27 PM #4
Re: Refrigeration 101
I first check the delta-T's to confirm adequate airflow through both coils.
Then I check for high subcooling.
Then I check for low superheat.
Then I check for low subcooling.
Then I check the condenser TD to see if the high side is rejecting a heavy heat load.
If the high side is rejecting a heavy load, then the low side must be absorbing a heavy load.
Adjusting a TXV aka TEV is almost always a mistake, especially when the refrigerated space is above design temp.Last edited by Gary; 05-07-2009 at 06:34 PM.