    Re: Strange TXV setup

    Quote Originally Posted by Gary View Post
    Hmmm... two more plates and a HX were added, with presumably the same liquid line. An undersized liquid line would not be out of the question.
    Now you will have to explain this one, 3/8" line - same compressor, suction controlled flow rate - what can possibly get outside of the parameters acceptable for this line by adding plates.

    Speculations about many things are maybe OK but it does not get us any closer to understanding how the system worked as it was.

    I am still convinced it was a critically charged orifice system not under txv control and have yet to see any compelling evidence otherwise. No blockages, no kinks, no hunting, line sizes OK and orientation of filter drier OK - though that is also a scratch the head item - what has it really got to do with the issue at hand?

    Chef

  2. #2
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Strange TXV setup

    Quote Originally Posted by Chef View Post
    Now you will have to explain this one, 3/8" line - same compressor, suction controlled flow rate - what can possibly get outside of the parameters acceptable for this line by adding plates.

    Speculations about many things are maybe OK but it does not get us any closer to understanding how the system worked as it was.

    I am still convinced it was a critically charged orifice system not under txv control and have yet to see any compelling evidence otherwise. No blockages, no kinks, no hunting, line sizes OK and orientation of filter drier OK - though that is also a scratch the head item - what has it really got to do with the issue at hand?

    Chef
    The TXV bulb charge is sensing freezer temp or it is sensing chiller temp. Either way it is not at its minimum flow position. It is running wide open with an orifice that is at least adequate if not oversized.

    If there was solid liquid at the orifice the system would be flooded. Therefore, there is solid liquid at the sightglass but not at the orifice... ergo there is a restriction in between. Adding refrigerant drops the suction temp because it is overcoming the restriction.
    Last edited by Gary; 21-03-2010 at 02:28 PM.

Similar Threads

  1. Can't suss strange paramaters on Denco downflow unit
    By Coolie in forum Air Conditioning
    Replies: 20
    Last Post: 26-07-2010, 03:20 PM
  2. The Basic Setup
    By ice_cold in forum Fundamentals
    Replies: 5
    Last Post: 17-12-2009, 09:34 AM
  3. Fujitsu strange Whistling noise
    By gwilliamson in forum Air Conditioning
    Replies: 17
    Last Post: 26-03-2008, 09:48 PM
  4. Hermetic strange sound.
    By fridg in forum Technical Speculations
    Replies: 16
    Last Post: 02-03-2008, 07:08 PM
  5. strange inverter problem
    By rbartlett in forum Air Conditioning
    Replies: 11
    Last Post: 19-05-2006, 08:31 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •