    Re: condensate drainage problems

    thanks for all the responses, the traps and filters are all ok, what i find when system operating is the condensate water in the condensate pan is pulled by the suction of the supply fans to such a degree that the water is kept away from the drainage pipe almost lifted out of the tray. when an access panel is opened up stream then the water flows down the trap quite freely.

  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,667
    Rep Power
    51

    Re: condensate drainage problems

    Your trap on the drainage line should be close to the drain pan and at least 150mm deep then the drain should fall away from the trap. If you have a large static pressure on the fan the drain line may need to be larger than 20mm diameter

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: condensate drainage problems

    Quote Originally Posted by mr saw View Post
    thanks for all the responses, the traps and filters are all ok, what i find when system operating is the condensate water in the condensate pan is pulled by the suction of the supply fans to such a degree that the water is kept away from the drainage pipe almost lifted out of the tray. when an access panel is opened up stream then the water flows down the trap quite freely.
    You say that traps are OK but they don't seem to be working.

    Check the static pressure at the trap inlet and ensure that the trap is deep enough.

    Something on the inlet side of the fan is blocked to have increased the suction pressure from what, we assume, was a working drainage system.

    Blocked filter, collapsed filter, dirty coil, fire damper dropped, inlet grille damper closed etc.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Apr 2003
    Location
    london
    Posts
    26
    Rep Power
    0

    Re: condensate drainage problems

    the evaporator coil did have a carpet layer of dirt which has been clean, thinking about it the coil would really need a deep clean because internally it is still floud to a degree. thanks chaps...

  5. #5
    Join Date
    May 2006
    Location
    Sussex
    Posts
    362
    Rep Power
    21

    Re: condensate drainage problems

    The Fresh air intake louver will normally have a bird wire screen behind it, which can get clogged up after a while. Maintenance deals with filters but can miss this one.

    Might be worth a check if all else looks okay on the suction side of fan.

Similar Threads

  1. Carrier 30XA Liquid chiller Problems
    By Ed Burris in forum Commercial
    Replies: 7
    Last Post: 13-08-2010, 08:12 PM
  2. Condensate drainage regulations
    By topfridgeman in forum Technical Discussions
    Replies: 1
    Last Post: 04-03-2009, 11:12 PM
  3. Hartell Condensate Pump
    By Grizzly in forum Air Conditioning
    Replies: 8
    Last Post: 03-01-2008, 09:08 AM
  4. Replies: 10
    Last Post: 18-03-2006, 07:35 PM
  5. Oil return problems
    By Peter_1 in forum Industrial
    Replies: 37
    Last Post: 23-08-2004, 11:30 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •