Re: condensate drainage problems
thanks for all the responses, the traps and filters are all ok, what i find when system operating is the condensate water in the condensate pan is pulled by the suction of the supply fans to such a degree that the water is kept away from the drainage pipe almost lifted out of the tray. when an access panel is opened up stream then the water flows down the trap quite freely.
-
30-06-2010, 09:50 PM #2
Re: condensate drainage problems
Your trap on the drainage line should be close to the drain pan and at least 150mm deep then the drain should fall away from the trap. If you have a large static pressure on the fan the drain line may need to be larger than 20mm diameter
-
30-06-2010, 10:16 PM #3
Re: condensate drainage problems
You say that traps are OK but they don't seem to be working.
Check the static pressure at the trap inlet and ensure that the trap is deep enough.
Something on the inlet side of the fan is blocked to have increased the suction pressure from what, we assume, was a working drainage system.
Blocked filter, collapsed filter, dirty coil, fire damper dropped, inlet grille damper closed etc.Brian - Newton Abbot, Devon, UK
Retired March 2015
-
02-07-2010, 10:51 PM #4
Re: condensate drainage problems
the evaporator coil did have a carpet layer of dirt which has been clean, thinking about it the coil would really need a deep clean because internally it is still floud to a degree. thanks chaps...
-
04-07-2010, 02:39 PM #5
Re: condensate drainage problems
The Fresh air intake louver will normally have a bird wire screen behind it, which can get clogged up after a while. Maintenance deals with filters but can miss this one.
Might be worth a check if all else looks okay on the suction side of fan.
Similar Threads
-
Carrier 30XA Liquid chiller Problems
By Ed Burris in forum CommercialReplies: 7Last Post: 13-08-2010, 08:12 PM -
Condensate drainage regulations
By topfridgeman in forum Technical DiscussionsReplies: 1Last Post: 04-03-2009, 11:12 PM -
Hartell Condensate Pump
By Grizzly in forum Air ConditioningReplies: 8Last Post: 03-01-2008, 09:08 AM -
Suction pressure problems on TS units at low ambient temps
By nova in forum TransportReplies: 10Last Post: 18-03-2006, 07:35 PM -
Oil return problems
By Peter_1 in forum IndustrialReplies: 37Last Post: 23-08-2004, 11:30 PM