    Re: Liquid receiver on a reverse cycle VRV system

    Quote Originally Posted by Tayters View Post
    Also the outdoor unit may record SST and SCT but if subcooling to fan coils is different then for a fixed EEV opening more or less rerigerant will be needed for the same amount of cooling. Some have a thermistor mid coil also for this reason.
    That makes sense.

    All the bolt-on EXV controllers I've seen take the temp and pressure at the outlet of the coil (as per convention) to determine superheat. Could you reliably determine superheat by simply measuring both ends of the coil? (with suitable qualifications about limited application to unrestrictive coils with low pressure drops)


    Quote Originally Posted by Tayters View Post
    Hope that helps.
    Heaps. Cheers for that Andy.

  2. #2
    Join Date
    Feb 2012
    Location
    Bolivia
    Posts
    270
    Rep Power
    14

    Re: Liquid receiver on a reverse cycle VRV system

    Quote Originally Posted by BradC View Post
    That makes sense.

    All the bolt-on EXV controllers I've seen take the temp and pressure at the outlet of the coil (as per convention) to determine superheat. Could you reliably determine superheat by simply measuring both ends of the coil? (with suitable qualifications about limited application to unrestrictive coils with low pressure drops)
    Heaps. Cheers for that Andy.
    Yes, in general for azeotropes (or near): you can measure superheat more reliably with 2 temperature sensors than temperature/pressure unless you compensate for the different time constants the transducers have.

    Usually system pressure time constant + pressure transducer time constant are shorter than temperature TC, but you also have to consider the time it takes to look up saturation tables for the controller.

    For non azeotropes you must calibrate/compensate.

    Quote Originally Posted by BradC View Post
    (with suitable qualifications about limited application to unrestrictive coils with low pressure drops)
    All designs should keep pressure drop in the coils low for all types of refrigerants or you have to measure the coil’s pressure differential too, and compensate.

    --- o ---

    You must follow the controller’s manufacturer manual as to where, how and number of sensors must be installed, for it's control logic success depends on it.

  3. #3
    Join Date
    Oct 2010
    Location
    Australia
    Posts
    88
    Rep Power
    15

    Re: Liquid receiver on a reverse cycle VRV system

    Quote Originally Posted by aramis View Post
    You must follow the controller’s manufacturer manual as to where, how and number of sensors must be installed, for it's control logic success depends on it.
    Which is all well and good if the controller *has* a manufacturer.