22-07-2009, 06:48 PM #1
Re: Carrier Transicold Container Problem
ok I looked at it somemore, for one there is 543Volts coming in, and 9 amps on each leg, the quench valve is frosting over and there is a major temp difference on the filter dryer. the unit is getting power from the generator that hooks up to it on top. when the unit goes into cool mode the temp dose not go lower than 73 degrees F. All pre-trip codes pass except (auto2 mode) under P8-1 this comes up as a fail.
-
22-07-2009, 09:30 PM #2
Re: Carrier Transicold Container Problem
hi sgtchee
have you check refrigeration level??
al15 is loss of cool..reefr units haven t got good performans..
i think refrigaration level is no good..
also txv is not good workşng?*you have to check its..is there to much ice on the suction pipe??If there is too much ice on cuction pipe txv is not good working
im waiting ur reply..
see you
reefer mechanic..
-
23-07-2009, 08:05 AM #3
Re: Carrier Transicold Container Problem
once i get the some gauges to check it out, what would be the low and high scales read? could i just recover the whole refrigerant out with the robinair? the book says 10.8 lbs but the label on the compresser says 8.6 lbs and i missing something?
-
23-07-2009, 02:40 AM #4
-
17-08-2009, 12:04 AM #5
Re: Carrier Transicold Container Problem
the filter dryer is blocked try changing that first before anything else
Similar Threads
-
MICROPROCESSOR DIAGNOSTICS/Differnces beteween TK/CTC
By REEFER-TEK in forum TransportReplies: 12Last Post: 27-03-2011, 04:12 AM -
Carrier Transicold problem
By tsvetomir in forum TransportReplies: 17Last Post: 16-08-2010, 02:59 AM -
Carrier chiller basic board problem
By noushad123 in forum Trouble ShootingReplies: 25Last Post: 17-06-2010, 06:55 AM -
Furance problem
By ALONEI in forum Trouble ShootingReplies: 10Last Post: 14-05-2008, 11:32 AM -
York Chiller Excessive Purges Problem
By imranmd in forum CommercialReplies: 5Last Post: 07-03-2008, 05:13 AM