Results 1 to 40 of 40

Hybrid View

  1. #1
    SGTChee's Avatar
    SGTChee Guest

    Re: Carrier Transicold Container Problem

    ok I looked at it somemore, for one there is 543Volts coming in, and 9 amps on each leg, the quench valve is frosting over and there is a major temp difference on the filter dryer. the unit is getting power from the generator that hooks up to it on top. when the unit goes into cool mode the temp dose not go lower than 73 degrees F. All pre-trip codes pass except (auto2 mode) under P8-1 this comes up as a fail.

  2. #2
    Join Date
    Oct 2008
    Location
    bursa / turkey
    Age
    47
    Posts
    219
    Rep Power
    0

    Re: Carrier Transicold Container Problem

    Quote Originally Posted by SGTChee View Post
    ok I looked at it somemore, for one there is 543Volts coming in, and 9 amps on each leg, the quench valve is frosting over and there is a major temp difference on the filter dryer. the unit is getting power from the generator that hooks up to it on top. when the unit goes into cool mode the temp dose not go lower than 73 degrees F. All pre-trip codes pass except (auto2 mode) under P8-1 this comes up as a fail.
    hi sgtchee

    have you check refrigeration level??

    al15 is loss of cool..reefr units haven t got good performans..

    i think refrigaration level is no good..

    also txv is not good workşng?*you have to check its..is there to much ice on the suction pipe??If there is too much ice on cuction pipe txv is not good working

    im waiting ur reply..

    see you

    reefer mechanic..

  3. #3
    SGTChee's Avatar
    SGTChee Guest

    Re: Carrier Transicold Container Problem

    once i get the some gauges to check it out, what would be the low and high scales read? could i just recover the whole refrigerant out with the robinair? the book says 10.8 lbs but the label on the compresser says 8.6 lbs and i missing something?

  4. #4
    Join Date
    Dec 2005
    Location
    Upper left hand corner of the USA
    Age
    64
    Posts
    203
    Rep Power
    19

    Re: Carrier Transicold Container Problem

    Quote Originally Posted by SGTChee View Post
    and there is a major temp difference on the filter dryer.
    Ding, ding, ding, ding.

  5. #5
    Join Date
    May 2008
    Location
    New Zealand
    Posts
    35
    Rep Power
    0

    Re: Carrier Transicold Container Problem

    the filter dryer is blocked try changing that first before anything else

Similar Threads

  1. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  2. Carrier Transicold problem
    By tsvetomir in forum Transport
    Replies: 17
    Last Post: 16-08-2010, 02:59 AM
  3. Carrier chiller basic board problem
    By noushad123 in forum Trouble Shooting
    Replies: 25
    Last Post: 17-06-2010, 06:55 AM
  4. Furance problem
    By ALONEI in forum Trouble Shooting
    Replies: 10
    Last Post: 14-05-2008, 11:32 AM
  5. York Chiller Excessive Purges Problem
    By imranmd in forum Commercial
    Replies: 5
    Last Post: 07-03-2008, 05:13 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •