20-07-2008, 09:56 PM #1
Re: Mass Flow Rate with Big Condenser
Originally Posted by David2008
You must be kidding? Up means up and down means down. (sorry, couldn't resist)
The difference is what you call a liquid seal. If you drain downwards the liquid may not stay in the condenser to achieve any subcooling.
If you provide a liquid seal, the liquid has a place to collect so that it can subcool.
Condenser manufacturers handle this differently in their designs.If all else fails, ask for help.
-
20-07-2008, 10:06 PM #2
-
20-07-2008, 11:47 PM #3
Re: Mass Flow Rate with Big Condenser
A bigger condenser could have all of the following positive effects on a refrigeration system because it would have a lower condensing temperature.
1. A better refrigeration effect
2. A lower mass flow rate
3. A lower volume flow rate
4. A higher COP
5. A lower condenser heat of rejection
6. A lower condenser temp difference
7. A lower condenser split
8. A lower KW/ton
9. higher efficiency and a happy compressor and it's components
-
21-07-2008, 03:03 PM #4
-
21-07-2008, 03:39 PM #5
Re: Mass Flow Rate with Big Condenser
Originally Posted by GXMPLX
If the equipment is balanced at 60Hz, the same should be expected at 50Hz with the only exception being the rated duty should be compensated for to achieve the desired results while operating at 50 Hz.Last edited by US Iceman; 21-07-2008 at 03:39 PM. Reason: fixed quote
If all else fails, ask for help.
-
21-07-2008, 03:56 PM #6
Re: Mass Flow Rate with Big Condenser
Originally Posted by Peter_1
Refrigeration systems do NOT have to have high discharge pressures to work.
The only time you should see higher discharge pressures on air-cooled condensers (or evaporative condensers) is in the summer time (or during the hottest temperatures of you location).If all else fails, ask for help.
-
21-07-2008, 04:01 PM #7
Re: Mass Flow Rate with Big Condenser
Originally Posted by jwasir
From my experience... the smallest condensers are used so that the installing contractor can have the lowest price.If all else fails, ask for help.
-
21-07-2008, 08:37 PM #8
Re: Mass Flow Rate with Big Condenser
Not necessarily. You get TEV instability if the valve tries to operate below a curve called MSS (Minimum Stable Superheat) that graphs capacity versus valve superheat. By increasing subcooling you are moving this curve to higher superheat and will produce instability more often with TEVs that have fast acting charges.
TEV stability problems are the ones I find less understood in these posts, not an easy subject that needs some drawings and I'll post something on this when I'm ready.
Though the equipment remains in balance due to the fact that TEV works fine at 20% off nominal capacity, the compressor capacity is 20%less.
The evaporator and condenser are different because it depends if the manufacturer changed blade´s attack angle to compensate for lower RPMs or not.
The problem arises when you have low thermal loads the system becomes completely unstable and out of balance. The TEV is oversized and perform VERY poorly if thermal load drops 20% to 30% below the 50Hz value! Except for balanced port valves or absorber charges, that can control well as low as 20% off their rated capacity.
This is worse in some equipment that already had the TEV oversized for the 60Hz capacity (It was correctly chosen but a little oversized).
-
21-07-2008, 08:24 PM #9
-
21-07-2008, 08:49 PM #10
Re: Mass Flow Rate with Big Condenser
Cost is a BIG disadvantage.
No! Some compressor are optimized for high condensing other for low condensing, if you use the wrong compressor with a large condenser you will get less COP.
Consider that with this line of thought all condensers should be water cooled! Go ask Chemi_cool if this is possible!
Every application has some optimizing to be done. Little larger condensers ok, too large will cause problems and probably lower system COP.
-
21-07-2008, 08:11 AM #11
Indeed, that's the correct expression, liquid seal
We had - perhaps 20 years ago - some condensing units running (Copeland with hermetic piston DCRQ's running), evaporating at 5°C.
The compressor could handle this perfectly but the condensers were ways too small. So we installed in line a second condenser and this decreased HP almost nothing. Only if we placed one in parallel, then it resulted in a serious HP decrease.
In line, what we made was a huge subcooler which didn't increase the condenser area, so HP remained almost unchanged.Last edited by Peter_1; 21-07-2008 at 02:04 PM.
Similar Threads
-
Some information on the aplication of suction gas/liquid line heat exchangers
By SteinarN in forum FundamentalsReplies: 5Last Post: 14-09-2009, 07:33 AM -
high volume flow rate
By cakabo28 in forum Technical DiscussionsReplies: 5Last Post: 04-10-2007, 03:41 AM -
Shell/Tube flow rate?
By reggie in forum FundamentalsReplies: 4Last Post: 17-11-2002, 05:41 PM -
capillary tubes and mass flow when fed with liquid/gas
By DaBit in forum FundamentalsReplies: 15Last Post: 24-10-2002, 06:52 PM