    Re: Strange TXV setup

    Quote Originally Posted by Chef View Post
    Exactly - its a system that works (with dumb luck as you mentioned earlier) and there are little or no signs of why it works but wrongly. Everything looks right except the SH at the compressor and that is so delicate with charge.

    There is no blockage as system was flushed with flushing liquid several times and tested for flow with a manometer system.

    DesA points out that the bulb should be insulated (agreed) but it still wont make any difference as it never gets colder than the TXV and Mad Fridgie reckons the #4 could still provide enough flow at minimum turn down - could be onto something there.

    Chef
    Adding charge drops the SH (drops the suction line temp). So...

    Insulate the bulb and add charge. The suction line temp will drop until the bulb temp is below the TXV temp and will thus regain its charge. If the SC is then excessive, there is a restriction.

    A restriction could be an undersized or kinked liquid line, plugged TXV inlet screen, restrictive HX, etc..

  2. #2
    Join Date
    Jun 2007
    Location
    At sea
    Posts
    367
    Rep Power
    17

    Re: Strange TXV setup

    Quote Originally Posted by Gary View Post
    Insulate the bulb and add charge. The suction line temp will drop until the bulb temp is below the TXV temp and will thus regain its charge.
    Except if his Madness is right (usually is) the #4 is too big and works only with migration so if the bulb is allowed to regain control it might not be able to turn down enough.

    So put in a smaller orifice and wont wont work properly till the bulb eventually gains control if it ever does.

    Not sure I like that scheme of things

    Chef

  3. #3
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Strange TXV setup

    Quote Originally Posted by Chef View Post
    Except if his Madness is right (usually is) the #4 is too big and works only with migration so if the bulb is allowed to regain control it might not be able to turn down enough.

    So put in a smaller orifice and wont wont work properly till the bulb eventually gains control if it ever does.

    Not sure I like that scheme of things

    Chef
    Once the bulb is in control... if the TXV hunts, the orifice is oversized.

Similar Threads

  1. Can't suss strange paramaters on Denco downflow unit
    By Coolie in forum Air Conditioning
    Replies: 20
    Last Post: 26-07-2010, 03:20 PM
  2. The Basic Setup
    By ice_cold in forum Fundamentals
    Replies: 5
    Last Post: 17-12-2009, 09:34 AM
  3. Fujitsu strange Whistling noise
    By gwilliamson in forum Air Conditioning
    Replies: 17
    Last Post: 26-03-2008, 09:48 PM
  4. Hermetic strange sound.
    By fridg in forum Technical Speculations
    Replies: 16
    Last Post: 02-03-2008, 07:08 PM
  5. strange inverter problem
    By rbartlett in forum Air Conditioning
    Replies: 11
    Last Post: 19-05-2006, 08:31 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •