I'll give you the way to know for certain:
1. Open the outdoor unit - gain access to the compressor;
2. Install a temp sensor 150mm from the compressor exit, on the discharge line (the hot one);
3. Let the unit pull down & watch the discharge temp;
4. If temp exceeds 107-110'C, then you are pushing your unit too far.
It is possible that the manufacturer lets the compressor discharge run up a little higher on non-continuous load, but not too much higher.
Let us know how you get on.Engineering Specialist - Cuprobraze, Nocolok, CD Technology