Results 1 to 40 of 40
17-05-2008, 01:14 AM #1
19-05-2008, 01:15 AM #2
19-05-2008, 03:40 AM #3
19-05-2008, 11:00 PM #4
Re: Carrier Transicold Container Problem
hi there. I have had this problem before as well. the first thing to check is the fuses on the front of the controller. (F1 ,F2) the alarm code tells you that one of these fuses has blown. relace fuse and start up the box. If the box is turned back on and tha alarm light is still active then go into the alarm list and make sure the alarm hasn't gone from AA status to IA21. Once it has gone IA the alarm can be cleared. If it blows again. check the control transformer voltage to the controller..... hope this helps
08-07-2008, 04:26 AM #5
its the SMV module shorting to ground underneath the quench valve. from the factory they install the module so the water that drips off the quench valve right into the wiring. hope this helps.
22-07-2009, 01:39 PM #6
Hello all, im currently out in the middle of no where in afganistan and I came across a Carrier transicold container with a alarm code AL15, so i read thru the manual and it tells me nothing of that code. the model is 60NT40-541-302. if anyone can tell me why this container is shutting off and displaying AL15 that would be great.
22-07-2009, 01:41 PM #7
sorry back again the model number is 69NT40-541-302.....a 9 instead of a 0
22-07-2009, 06:48 PM #8
ok I looked at it somemore, for one there is 543Volts coming in, and 9 amps on each leg, the quench valve is frosting over and there is a major temp difference on the filter dryer. the unit is getting power from the generator that hooks up to it on top. when the unit goes into cool mode the temp dose not go lower than 73 degrees F. All pre-trip codes pass except (auto2 mode) under P8-1 this comes up as a fail.
Carrier Transicold problem
By tsvetomir in forum TransportReplies: 17Last Post: 16-08-2010, 02:59 AM -
Carrier chiller basic board problem
By noushad123 in forum Trouble ShootingReplies: 25Last Post: 17-06-2010, 06:55 AM -
Furance problem
By ALONEI in forum Trouble ShootingReplies: 10Last Post: 14-05-2008, 11:32 AM -
York Chiller Excessive Purges Problem
By imranmd in forum CommercialReplies: 5Last Post: 07-03-2008, 05:13 AM