I got this service call the other day. It was a 2ton keeprite ultraquiet residential a/c system. The complaint was that the A/C doesnt shut off and runs continiously. On my inspection the pressure were a litttle low, and condenser unit was very dirty. So i topped up the refrigerant and cleaned the condenser coil.
The pressure on low side was 70psi and High Side 160Psi. with R22 refrigerant and temperature outside was about 88F. I dont know why the high side pressure is too low? Any idea as to why the high side pressure lines feel cold and has low pressure?
-
13-08-2007, 10:57 PM #2
Re: High Side Pressure is ...
Did you do a leak test before 'topping up'?
Is the compressor pumping correctly?Brian - Newton Abbot, Devon, UK
Retired March 2015
-
13-08-2007, 11:47 PM #3
Re: High Side Pressure is ...
If we take a step back.....
Did you connect your gauges to the service ports on the outside side of the outdoor unit?
Were both pipes lagged?(sorry never worked on these units)
If the answer to both these questions is YES, then you measured an intermediate pressure and not a true HP.
-
14-08-2007, 02:59 AM #4
Re: High Side Pressure is ...
It sounds the system has leakage, both the low-side and high-side pressure are low. It can also deduced from the low values of the condensing and evaporating temperatures 80.71F and 30F although the condenser was fouled and the ambient temperature is above the condensing temperature. So it is better to check the leakage matter firstly?.
-
14-08-2007, 09:21 AM #5
Re: High Side Pressure is ...
Hi, could be a leaking reversing valve, 70psi could be high depending o room temp.
-
14-08-2007, 12:53 PM #6
Re: High Side Pressure is ...
i would recomend that you check if the compressor pumping efficiently, and verify that there are no leaks.
Similar Threads
-
Compressor loading, cooling, and range of operation.
By Air duster in forum FundamentalsReplies: 10Last Post: 02-04-2008, 08:39 AM -
fun quiz
By Brian23 in forum New to REReplies: 6Last Post: 02-10-2007, 10:18 PM -
High head pressure no duty
By LRAC in forum CommercialReplies: 15Last Post: 23-07-2007, 12:12 AM -
High pressure reading before and after condenser coil
By Cofreth in forum RefrigerantsReplies: 6Last Post: 18-11-2005, 04:30 PM