    Feb 2011
    Russia
    Question Copeland China recipr.compr. Is it a bypass pipe?
    Hello eberybody!
    Does anyone know what this bypass /or safety pipe is with the valve?
    Re: Copeland China recipr.compr. Is it a bypass pipe?
    NEugeny,
    Check page 12 internal relief valve.
    Does it look similar?
    http://www2.renkulde.no/mkdokume.nsf/C8646D22130D5CA9C1256D90002D58C1/$FILE/EN_D060302_AGL_SHDiscus.pdf
    Feb 2011
    Russia
    Thank you.
    On one unit during operation this pipe is hot, on the second one it is cold.
    Where the pipe is hot, there is a strong vibration.
    Feb 2011
    Russia
    Update:
    I dismantled this node, there is nothing inside the pipe.
    It connects the cavity of the suction in the head and the crankcase.
    During operation, the temperature of the tube is about + 50 ° C
    Feb 2011
    Russia
    We will consider that this is such a specific oil separator. ;-)
    Quote Originally Posted by NEugeny View Post
    NEugeny,
    Any chance of exact model number so can search for answers?
    Feb 2011
    Russia
    this is made in china
    Mar 2005
    u.a.e
    68
    169
    Possibly this is a hot gas by pass to work compressor at low loads (unload) you can verify with monitoring gauge pressure and pipe temperature.