    andy1957's Avatar
    andy1957 Guest
    fujitsu fault codes
    Hi, I have a AOYR 12 LC system flasing twice on the timer led, any ideas
    Split Croatia
    6,151
    Re: fujitsu fault codes
    Outdoor unit does not have timer led.
    Your error code means that indoor unit doesn't receive communication signal from outdoor unit.
    andy1957's Avatar
    andy1957 Guest
    The timer led on the indoor unit is flashing twice. Chears
    Split Croatia
    6,151
    Quote Originally Posted by andy1957 View Post
    Yes, but you gave us model number of outdoor unit.
    May 2010
    Russia
    168
    andy1957
    1. Check cabel conection indoor<->outdoor units
    2. Check fuse 20A on outdoor unit
    andy1957's Avatar
    andy1957 Guest
    found out that the fault is the out door board after talking with fujitsu tec dept. IE checked voltage on term 3 on the outdoor board the n tested it on the indoor board, both readings the same. \\\\going to remove the old system and fit a mitsi heavy inverter as i have had no trouble with them. Thanks to all