Chemical wash on condenser of chilleers
Hi,
Anyone has experience on chemical wash on condenser of chiller please advise.
I would like to know the points to be aware of and precautions need to know etc.
The chiller concerned is Ebara with plates design.
Thanks
-
27-05-2015, 12:29 PM #2
Re: Chemical wash on condenser of chilleers
Weak solution of sulfamic acid at a temperature around 50 deg C helps to clear the scales. This should be following by circulation of caustic solution.
-
29-05-2015, 12:24 PM #3
Re: Chemical wash on condenser of chilleers
Hi Sandybapat, Is it for Air-cooled or water cooled chiller ? Thanks !
-
Re: Chemical wash on condenser of chilleers
this stuff is pretty efficient if it's on the water side
http://wssproducts.wilhelmsen.com/ma...escalex-25-kg/
http://wssproducts.wilhelmsen.com/ma...g-liquid-25-l/
Both of these require you to circulate the mixture on the heat exchanger.
We find it very effective on plate heat exchangers, but remember to circulate the mixture counter to normal flow
According to the product guy I spoke to a few years back, it's not a marine pollutant and can be flushed to sea after use.
for a closed system follow the neutralizing instructions, for a system open to the sea, just run the condenser pump for 5 hours to remove all residue-Cheers-
Tycho
-