    Question Regassing question [amateur]
    Hi,
    I've got an 18000btu split a/c unit (Bergdorf) I bought a few years ago. I self-installed it in my portakabin office, and it worked beautifully for about 12 months, then slowly and noticeably got less & less effective over the next 6-8 months. Diagnosis - I didn't do the connection pipes up firmly enough, and the gas leaked out over time. It sat on the wall for the next 4-5 years, a few months back I decommissioned the cabin but kept the A/C unit.
    Obviously, it needs new gas (R134 I think, but will confirm before I get any obviously). I'm also assuming I need to add some oil, but here come the questions....
    1) How much oil? Roughly? Is it likely to have lost much as the leak was so slow?
    2) How much gas? I can get 5kg of R134A for £35 locally, I'm guessing that would last me a lifetime even if I didn't cure the leak...
    3) I'd like to re-use the piping. It's been indoors most of its life, and the only times it's been disturbed are when I've disturbed it, so it shouldn't be too distorted/fractured or work hardened. Plus it's going back into an indoor setting (the outside unit is under cover), so it should last years, right?
    This is a self-install again by me (a capable amateur but not an a/c expert by any stretch), the building is basically a large shed, it's not for commercial or domestic use, so I don't need to follow codes, so long as I don't do anything stupidly dangerous.
    Of course, if it would only cost, say £50ish to have someone come onsite & gas/oil/recommission it for me, then that's the route I'd take. Unfortunately I'm on a shoestring budget though, otherwise I'd be tempted to just buy another one.
    Many thanks in advance for any advice.
    Cheers!
    Ade.
  2. #2
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,097
    Rep Power
    33
    Re: Regassing question [amateur]
    Where are you in the UK,that may get you some response?
  3. #3
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,479
    Rep Power
    45
    Quote Originally Posted by AdeV View Post
    Welcome to the real world.
    You have set your location as UK. Here we are not allowed to carry out any work on any refrigeration circuits unless we are suitably qualified and registered. Sorry.
    Quote Originally Posted by GOV.CO.UK
    Only trained technicians can carry out work on equipment containing F gases, including:
    • installation
    • testing for leaks
    • general maintenance
    • disposal or decommissioning when you no longer need the product
    For more information have a look HERE
  4. #4
    Join Date
    Jun 2017
    Location
    UK
    Age
    50
    Posts
    10
    Rep Power
    0
    Hi, thanks for the replies.
    I'm in Birkenhead, right on the end of the Wirral peninsular. Miles away from anyone...
    Re codes/qualifications/registrations etc.... well, I won't tell if you won't
    Seriously - I'm just after some advice. I'll have a go at re-gassing it myself, if it's not incredibly difficult, but without the proper training etc. I obviously don't know the volumes, pressures, and so on. Come to think of it, I don't even know _what_ oil to use (Mobil 1 is not suitable, I assume!). At the end of the day, if I destroy my own AC unit, then I can just shrug and buy another one when the budget allows. I just need to not set it on fire...
    Cheers!
    Ade.
  5. #5
    Join Date
    Jun 2017
    Location
    UK
    Age
    50
    Posts
    10
    Rep Power
    0
    PS: I do spend quite a lot of time in China. We can pretend the A/C unit is there if that helps nudge nudge wink wink etc...
  6. #6
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,097
    Rep Power
    33
    Sorry most people here don't do nudge wink,we are professionals that abide by all! the rules and regulations,cowboys are great in the wild west but my friends on here are all abiding by rules that's what professionals do,if I was you I would just save up and buy a new unit,or put more Windows into your cabin.
  7. #7
    hookster's Avatar
    hookster is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2007
    Location
    Hampshire
    Posts
    439
    Rep Power
    31
    Hi,
    Cheers!
    Ade.
    "PLUG AND PLAY" AC capable amateur / I didn't do the connection pipes up firmly enough, and the gas leaked out!
    Very funny read (going to get moaned at by the drama police but you would do it anyway so here goes!)
    The oil leakage would not have been large enough to worry about just ignore it.
    It will have 1.1 - 1.8 Kg of refrigerant (will be marked on the data plate on outdoor unit)
    You can reuse the pipe if there is no leak
    I hope you are not growing something you should not be????
    Until refrigerant and AC products are stopped being sold without the need for certification this will be a continuing saga!
    It is not just online stores selling AC but all the manufacturers of AC in the UK, cutting the professionals out as they chase unit sales!
    I love the smell of Ammonia in the morning!
  8. #8
    Join Date
    Jun 2017
    Location
    UK
    Age
    50
    Posts
    10
    Rep Power
    0
    Many thanks all. I appreciate everyone here is a professional (so am I... in my chosen profession).
    Hookster, many thanks. No... it's not for growing things, it's for keeping my fevered brow cool in summer, and warming my frigid workshop in winter. AS to not doing the pipes up tight enough.... er, yeah (embarrassed smiley), I didn't know they needed to be murder-tight! I do now....
  9. #9
    Join Date
    Sep 2010
    Location
    Dorset
    Age
    76
    Posts
    209
    Rep Power
    16
    ......... AS to not doing the pipes up tight enough.... er, yeah (embarrassed smiley), I didn't know they needed to be murder-tight! I do now....
    Not 'murder-tight' but correct tight.
    Welcome to the ozone hole generating group.
  10. #10
    Join Date
    Jun 2017
    Location
    UK
    Age
    50
    Posts
    10
    Rep Power
    0
    Quote Originally Posted by FaultCode View Post
    R134a has an ozone depletion rating of zero. My A/C is not so old it uses R12!
    See, I'm not a totally clueless idiot.
  11. #11
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51
    In all my years in the trade I've never seen an a/c unit on r12...or r134a come to think of it
  12. #12
    Join Date
    Sep 2010
    Location
    Dorset
    Age
    76
    Posts
    209
    Rep Power
    16
    Quote Originally Posted by frank View Post
    ^^Agreed^^
  13. #13
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,045
    Rep Power
    35
    £35 for 5kg is cheaper than we get it for a the wholesaler so you are doing well there, or perhaps I'm being rogered.
    Health and safety first..........unless I'm in a hurry.
  14. #14
    Join Date
    Jun 2017
    Location
    UK
    Age
    50
    Posts
    10
    Rep Power
    0
    www.gas-uk.co.uk near St Helens, Merseyside. R134A is £35kg for a 5kg bottle (there will be a bottle deposit too, but obviously that's refundable on return of the cylinder). R410A is the same price but the smallest size is 10kg. (so £70). Looks like I only need around 670gms, I can get a piddly little 800g bottle via eBay for around £35 (from Germany? Why no UK suppliers I wonder?) - expensive way to buy it, but OK for a one-off. Then I need to make/buy a filler adapter. Happy days. Good excuse to get on the lathe
  15. #15
    Join Date
    Jun 2017
    Location
    UK
    Age
    50
    Posts
    10
    Rep Power
    0
    I have an old Ford Granada in the shed, that uses (used) R12. I presume it's all gone off to eat some ozone by now, when I get a very large Round Tuit, I'll replace the A/C system with something that uses a more modern gas.
  16. #16
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,097
    Rep Power
    33
    That's cheap! Looked on the website provided it appears misleading,but they are getting a call from my son who is still involved in the industry,sadly me due to health issues I am not feet up now awaiting my operation,but wow some refrigerant prices are scary God help you guys out there trying to make money!
  17. #17
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,537
    Rep Power
    36
    If you look closely on the site before you can order it you
    have to submit your F-gas certificate and declare who is the
    qualified person who will be using it.
    See
    https://www.gas-uk.co.uk/help/f-gas
    It is against the law in the EU to sell refrigerants to unqualified
    personnel and they face prosecution if they flout the law.
    Rob
  18. #18
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,537
    Rep Power
    36
    You will find that any site on ebay that sells refrigerant is quickly
    shut down and therefore they all require proof of qualification before
    they will take your order.
    If you find a site that actually does sell the stuff both you and they
    are breaking the law and if found both are open to prosecution.
    So your question "Why no UK suppliers" is answered with It is against
    the law!
    Rob
  19. #19
    Join Date
    Jun 2017
    Location
    UK
    Age
    50
    Posts
    10
    Rep Power
    0
    Quote Originally Posted by Rob White View Post
    I hadn't spotted that, no; but then I hadn't looked closely either. Good to know.
    Genuine question then: Why is the only R410A on eBay for sale from Germany? I though the Germans were even more sticklers for EU rules than we are/were?
    One last question then: Do you need certificates/qualifications to work on vehicle A/C systems; and if so, are they the same certificates/qualifications as you would need to work on fixed A/C systems? Basically... can I get someone who normally does car AC to "do a foreigner*" and regas my split system without breaking any laws?
    Cheers,
    Ade.
    * Obviously any monies paid would be declared for tax etc.
  20. #20
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,537
    Rep Power
    36
    They are good in Germany, look closer at the site and check the small
    print I bet there will be a clause that states a certificate is required.
    I honestly would be surprised if they would ship it to you without proof.
    Cheers,
    Ade.
    I'm sure you could find somebody to do a foreigner they could work
    in any discipline of the fridge industry. If they were prepared to do the
    work and if they were satisfied the system was gas tight, then no laws
    would be broken.
    Obviously all VAT and duties would be declared and paid
    Car AC used to be exempt but was brought under similar requirements
    to those for static refrigeration equipment.
    Since 2014 all mobile fridge, freezer or AC (MAC) is covered by a legal
    requirement for refrigerant qualifications. It is not exactly the same
    as normal static equipment but they are now clamping down on their
    use and who can work on them.
    Regards
    Rob
  21. #21
    Join Date
    Jun 2017
    Location
    UK
    Age
    50
    Posts
    10
    Rep Power
    0
    Again, many thanks for all the replies, much appreciated.
    I've discovered a kink at one end of the pipes from my unit, so they need either replacing, or cutting back & flaring.
    I can't find a suitable board to post an official request on; but if anyone fancies the job of re-gassing & recommissioning the unit for me, please feel free to PM me. I do realise that everyone's going to be snowed under (pardon the phrase) right now, of course. Maybe I'll ask again in October when you're all scratting around for work.....
    Cheers!
    Ade.
  22. #22
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,537
    Rep Power
    36
    Put your location in your profile and
    somebody who works in your area
    might be able to assist.
    Regards
    Rob
  23. #23
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,479
    Rep Power
    45
    HI'm in Birkenhead, right on the end of the Wirral peninsular.
    Cheers
    Ade.
    1234567890
  24. #24
    Join Date
    Jun 2017
    Location
    UK
    Age
    50
    Posts
    10
    Rep Power
    0
    Hmm, I thought I had, oops.
    I'm in Birkenhead, postcode CH41 1DT.
    Still looking for anyone who can assist...
    Cheers!
    Ade.
Posting Permissions
  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts