    Question Re: Superheat

    Correct me if i'm wrong but does that mean for me to measure superheat at the evap i have 1 probe on the expansion side of the TEV and 1 probe at the coil exit in to the suction line, and is this with the evap fans on.

    always eager to learn from good enginners.

    regards

    Wizzer

  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,667
    Rep Power
    51

    Re: Superheat

    To measure the superheat at the evaporator (amount of heat energy added to the refigerant after phase change) you need to determine the refrigerant pressure (using gauges), look this pressure up on a refrigerant properties chart (pressure versus temperature) and then measure the pipe temperature at the same point.

    The pipe temperature will be higher than the chart value. Subtract one from the other and this will be the superheat reading.

  3. #3
    Join Date
    Dec 2004
    Location
    Australia
    Age
    52
    Posts
    519
    Rep Power
    20

    Re: Superheat

    Quote Originally Posted by wizzer
    Correct me if i'm wrong but does that mean for me to measure superheat at the evap i have 1 probe on the expansion side of the TEV and 1 probe at the coil exit in to the suction line, and is this with the evap fans on.

    always eager to learn from good enginners.

    regards

    Wizzer
    That's the two temperature method.Some people use this method.

    I prefer to use pressure temperature method as others have explained, as would most people.

  4. #4
    Join Date
    Jun 2006
    Location
    Victoria
    Age
    44
    Posts
    27
    Rep Power
    0

    Re: Superheat

    When taking your superheat temperature from the evap, your TXV superheat reading should come within the 4-7K range... If its under 4K your letting too much refrigerant into the evap, same goes if its over 7K your starving the evap.

    With subcooling temperatures at the condensor, "correct me if im wrong" the subcooling should be between 2-5K over the condensor. Any less than 2K start looking at air flow restrictions on the coil, anymore than than 5K, low refrigerant charge, over sized condensor.

    Hope this helps

    Dale

  5. #5
    Join Date
    Mar 2005
    Location
    Newcastle upon Tyne
    Age
    52
    Posts
    16
    Rep Power
    0

    Re: Superheat

    Quote Originally Posted by wizzer View Post
    Correct me if i'm wrong but does that mean for me to measure superheat at the evap i have 1 probe on the expansion side of the TEV and 1 probe at the coil exit in to the suction line, and is this with the evap fans on.

    always eager to learn from good enginners.

    regards

    Wizzer
    Yes Wizzer...you are correct. Forget about all the science behind it for now, aim for 6 degrees SH and your laughing.

Similar Threads

  1. TXV Superheat
    By Gary in forum Trouble Shooting
    Replies: 15
    Last Post: 24-04-2011, 02:51 PM
  2. Carrier 23xl chiller-Low discharge superheat alarms
    By Bradysmill in forum Trouble Shooting
    Replies: 7
    Last Post: 25-04-2010, 07:43 PM
  3. TEV superheat setting and low temperatures
    By DaBit in forum Fundamentals
    Replies: 11
    Last Post: 01-03-2010, 02:11 AM
  4. Superheat debate
    By zolar1 in forum Technical Discussions
    Replies: 5
    Last Post: 08-02-2008, 09:57 PM
  5. Superheat
    By shogun7 in forum Fundamentals
    Replies: 24
    Last Post: 23-08-2004, 05:54 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •