Re: New system tripping on low pressure??
This is basic commissioning knowledge. If you want to get into the design then we can go there but I think that would be unnecessary considering the scope of practicalities here.
Gary asked about the bypass factor principles I mentioned - not the original poster. So the answers were not addressed to the original poster - only to Gary. The comments about this being a fresh air application possibly being asked to operate out of range were aimed at the original poster and all other posters in general.
-
05-11-2010, 10:28 PM #2
Re: New system tripping on low pressure??
Going into the design principles would be ok for me and probably be more helpful, hence my reasoning over the style and build of the coil block. I couldn't see how bypass factors could have anything to do with basic commissioning! They are elements of design not commissioning. I doubt there are many peeps on here who would have the experience of designing air coils from basics, without a pc at hand.
I wasn't having a go at anyone ... just pointing out the main thread.
Reality is an elusion created by alcohol deficiency. Quaff and enjoy. [Yorkshire, UK]
-
05-11-2010, 10:37 PM #3
Re: New system tripping on low pressure??
No worries - but commissioning engineers must get the right SHR at the right total duty. For this they must understand the relationship between ADP and BPF. This is for custom build AHU's. For catalog AHU's only external static pressure and distribution balance is of concern. Standard AHU's have fans, motors and pulleys closely selected without much tolerance. Custom build AHU's these days have motors oversized by perhaps 40% with VFD's for RPM fine tuning according to ADP, SHR and BPF.
-
05-11-2010, 10:52 PM #4
Re: New system tripping on low pressure??
Sensible Heat Ratio is preset at design given specific design parameters. Aparatus Dew Point and ByPass Factors are also predefined at design. I can't see how a commissioning Engineer is able to make any corrections to these factors when he is most like never to achieve designg conditions at all. I would find it very unusual that any one would have the luxury and satisfaction of designing an AHU system with ducting etc and for it to drop into a design performance for commissioning purposes. In a real world it never happens. There are many peeps who sit at their drwng brds believing that the world is perfectly round ...well it surely isn't and never will be. There is a great difference between design practice and the realms of commissioning and the reality of having to instal a system that wasn't thought thru properly.Reality is an elusion created by alcohol deficiency. Quaff and enjoy. [Yorkshire, UK]
-
05-11-2010, 11:08 PM #5
Re: New system tripping on low pressure??
-
05-11-2010, 11:24 PM #6
Re: New system tripping on low pressure??
-
05-11-2010, 11:30 PM #7
-
05-11-2010, 11:33 PM #8
Re: New system tripping on low pressure??
Consider it this way, Gary.
You are standing between two AHU's. One has a return of 22 and a supply of 12 while the other a return of 24 and a supply of 21.
For a given deviation in leaving air temperature from design by say 0.2K which one is further off the SHR mark? The answer comes to mind instantaneously - yes?
-
06-11-2010, 12:02 AM #9
Similar Threads
-
Superheat and Subcooling
By Chunk in forum FundamentalsReplies: 42Last Post: 15-01-2011, 01:24 AM -
Max low side pressure in R404A system
By Wilade in forum Technical DiscussionsReplies: 8Last Post: 25-08-2009, 09:23 PM -
Low Pressure tripping
By Beginner in forum Trouble ShootingReplies: 16Last Post: 18-05-2008, 05:21 PM -
Fan model for system optimization
By autt in forum System OptimizationReplies: 8Last Post: 31-03-2007, 05:34 AM -
Liquid Overfeed Systems
By US Iceman in forum NH3Replies: 151Last Post: 08-03-2007, 05:34 AM