    Re: york screw chiller

    Hi thankyou install. Rusbuka and moideen i havent checked the ct resistance but the display reads different from clamp meter the clamp meter readings are higher and i dont know how to calibrate it

  2. #2
    moideen's Avatar
    moideen is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2008
    Location
    u.a.e
    Age
    49
    Posts
    412
    Rep Power
    23

    Re: york screw chiller

    Quote Originally Posted by GHAZ View Post
    Hi thankyou install. Rusbuka and moideen i havent checked the ct resistance but the display reads different from clamp meter the clamp meter readings are higher and i dont know how to calibrate it
    check the ct resistance, it is between 40-45. if there is any error,i thing the replacement of ct is the option,not calibration.